Reading: Timers in PLC Programming – Siemens Tia Portal Tutorials
Inst Tools > Blog > PLC Tutorials > Timers in PLC Programming – Siemens Tia Portal Tutorials
The most commonly used timers in PLC programming are Pulse timers, on-delay timers, retentive on-delay timers, and off-delay timers.
Last updated: March 23, 2023 2:57 pm
Mahmoud Salama
13 Min Read
Timers are very important instructions in any PLC logic; you can hardly find any automation code that doesn’t include a timer inside. There are many types of timers you can use but in this article, we will talk about the most commonly used timers in Siemens PLC.
What are Timers in PLC?Timers in PLC ProgrammingPulse TimerON-Delay TimerOff-delay TIMERRetentive On Delay Timer (Accumulator)Example PLC Timer Program SimulationPLC Timer Programming ExamplesConclusion
Contents:
  • What are timers in PLCs?
  • Pulse Timers TP.
  • ON-Delay timers TON.
  • OFF-Delay timers TOF.
  • Retentive on delay timer TONR.
  • Example program simulation.
  • Conclusions.
Timers in PLCs are built-in function blocks FBs that are used to provide the same timing instructions as a mechanical timing relay would do.
Timers are function blocks in the sense that they will need a data instance associated with them each time you use a timer. This data instance will include all data related to the operation of the timing instruction.
Timer in PLC Programming - Types of PLC Timers - Siemens TIA Portal
Some PLCs might include more timers than these 4, but they will basically be some sort of a combination of the 4 basic timers.
You can find the 4 timers in the Siemens TIA Portal instruction tab. See picture 1.
Different types of timers in the TIA Portal
Picture 1 – Different types of timers in the TIA Portal
Pulse Timer
You can use the Pulse timer (TP) instruction to generate a pulse for a specified amount of time.
The pulse timer will set the Q output for a programmed duration when the result of the logic operation (RLO) at input IN changes from “0” to “1” (positive signal edge).
The programmed time PT begins when the instruction starts. While Output Q is set for the duration PT, the detection of a new positive signal edge at the IN input has no influence on the signal state at the Q output.
You can scan the current time value at the ET output. The timer value starts at T#0s and ends when the value of the time duration PT is reached. When the time PT has elapsed and the signal state at input IN is “0”, the ET output is reset.
Generate Pulse Timer in PLC - TP Timer Instruction - Siemens Tia
The Pulse Timer instruction can be placed within or at the end of the network. It requires a preceding logic operation.
Each call of the Pulse timer instruction must be assigned to an instance data in which the timer data is stored. See picture 2 for the timing diagram of a pulse timer.
Timing diagram of pulse timer
Picture 2 – Timing diagram of pulse timer
You use a pulse timer in your program by dragging and dropping the TP instruction into your network. See picture 3.
Pulse timer in Siemens Tia
Picture 3 – Using a pulse timer in your code
As we said before, a pulse timer is a function block FB, so when calling a pulse timer you will have to assign a data instance with the timer. As you see in the last picture.
For better understanding, we will create a simple network with the pulse timer to see how it works when running a simulation. See picture 4.
Simple plc network with a pulse timer
Picture 4 – Simple network with a pulse timer
A global data block was created and inside this DB we will define some tags for our logic. A StartTP tag is used to start the pulse timer and a PulseTimerOutput tag will be true when the pulse timer is triggered.
ON-Delay Timer
You can use the ON-Delay Timer (TON) instruction to delay the setting of the Q output by the programmed time PT. The instruction is started when the result of the logic operation (RLO) at input IN changes from “0” to “1” (positive signal edge). The programmed time PT begins when the instruction starts.
When the time PT has elapsed, the output Q will have the signal state “1”. Output Q remains set as long as the start input is still “1”. When the signal state at the start input changes from “1” to “0”, the Q output is reset.
The timer function is started again when a new positive signal edge is detected at the start input.
Timer instructions in PLC - Generate On Delay Timer (TON)
The TON instruction can be placed within or at the end of the network. It requires a preceding logic operation.
Each call of the ON-Delay timer instruction must be assigned to an instance data in which the timer data is stored. See picture 5 for the TON timing diagram.
Timing diagram of On Delay Timer
Picture 5 – Timing diagram of On Delay Timer
You use the on-delay timer in your program by dragging and dropping the TON instruction into your network. See picture 6.
On Delay Timer TON in Tia Portal
Picture 6 – Using TON in your logic
As we said before, a TON timer is a function block FB, so when calling a TON you will have to assign a data instance with the timer. As you see in the last picture.
For better understanding, we will create a simple network with the ON-Delay timer to see how it works when running a PLC simulation. See picture 7.
TON Instruction Siemens PLC
Picture 7 – Simple network with a TON Instruction
Off-delay TIMER
You can use the Off-delay Timer (TOF) instruction to delay resetting of the Q output by the programmed time PT.
The Q output is set when the result of the logic operation (RLO) at input IN changes from “1” to “0” (negative signal edge). When the signal state at input IN changes back to “1”, the programmed time PT starts.
The Output Q remains set as long as the time duration PT is running. When the PT time duration expires, the Q output is reset. If the signal state at input IN changes to “1” before the PT time duration expires, the timer is reset. The signal state at the output Q continues to be “1”.
PLC Timer Programming for Beginners - Generate Off Delay Timer - TOF Instruction
The Off-delay timer instruction can be placed within or at the end of the network. It requires a preceding logic operation.
Each call of the “Generate off-delay” instruction must be assigned to a data instance in which the timer data is stored. See picture 8 for the TOF timing diagram
Timing diagram of TOF timer
Picture 8 – Timing diagram of TOF timer
You use the TOF in your logic by dragging and dropping the instruction into your code as you said with the TP and TON before.
We will create a simple code with a TOF timer, so we can see how it behaves when we start the PLC simulation. See picture 9.
Simple logic with a TOF timer
Picture 9 – Simple logic with a TOF timer
Keep in mind that the start signal StartOffDelay and the output OffDelayOutput are tags defined inside the global data block we just created.
The Retentive On Delay Timer (TONR) instruction is used to accumulate time values within a period set by the parameter PT. When the signal state at the IN input changes from “0” to “1” (positive signal edge), the time measurement is executed and the time PT starts.
While the time PT is running, the time values are accumulated that are recorded when the IN input has signal state “1”.
The accumulated time is written to the ET output. When the duration PT expires, the output Q will have the signal state “1”.
The Q parameter remains set to “1”, even when the signal state at the IN parameter changes from “1” to “0” (negative signal edge).
The R input resets the ET and Q outputs regardless of the signal state of the start input.
PLC Timers - Retentive Timer - Time Accumulator - TONR Instruction
The TONR instruction can be placed within or at the end of the network. It requires a preceding logic operation.
Each call of the TONR instruction must be assigned a data instance where the timer data is stored. See picture 10 for the TONR timing diagram.
Timing diagram of Retentive On Delay Timer
Picture 10 – TONR timing diagram
To use the TONR timer in your logic, you need to drag and drop the instruction in the coding area, you have to assign a data instance as we mentioned before. See picture 11.
PLC Retentive On Delay Timer (Accumulator)
Picture 11 – Adding a TONR timer to your logic
As we did with the last 3 timers, we will also create a simple logic for the TONR to see how it works in the simulation. See picture 12.
Siemens PLC TONR Instruction
Picture 12 – TONR simple logic
For the sake of simulation, we will create a simple HMI project.
In this project, we have created a separate screen for each type of timer, and on each HMI screen, you will find a representation of the timer similar to what you can see in the next picture. See picture 13.
Siemens Tia HMI screen for pulse timer
Picture 13 – HMI screen for pulse timer
Keep in mind that the screen for TONR will have an extra Button for the Reset signal. See picture 14.
WinCC HMI screen for TONR timer
Picture 14 -. HMI screen for TONR timer
After you compile the logic code we made and run the simulation for the PLC and the HMI.
Try to experiment with the logic through the HMI screens and buttons and see if the behavior of each timer matches the explanation given above.
See the next video for the program simulation.
Tia Portal - Example PLC Timer Program Simulation
Some of the example ladder logics are shared for your reference.
  • Pause the Timer PLC Ladder Logic
  • PLC Timer for Motor Direction Change
  • Extend Timer Duration Logic in PLC
  • PLC Timers Program Example Code
Conclusion
  • Timers are very important tools used with any PLC logic.
  • Different types of timers are available to match different requirements.
  • A timer instruction is a function block, so you have to assign a data instance with it.
  • A best practice when working with timers is to not make the PT time as a constant value, you should instead make this value configurable through an HMI to give the operator a wider range of control.
  • Function Blocks in PLC
  • 1oo2 Safety Logic in PLC
  • Automation Project Investment
  • Industrial Automation Solution
  • Two Hand Press Control Circuit
PLC Program for Controlling a Water Pump with 3 Power Sources
How to Communicate with Excel from Intouch SCADA?
Timer during Motor Direction Change PLC Program
Difference Between PLC and RTU?
How to Use Analog Input in Mitsubishi FX3U LOLLETTE PLC?
Shutdown Motors in Timed Operation PLC Program
Comparison of Proportional Integral Derivative Controllers (PID)
Developing PLC Logic for Water Pumping and Chemical Addition
Yokogawa DCS Tutorials – Configuration of Analog Input (Transmitter)
How to Detect Speed of Conveyor in PLC?
PLC Mixing Process with Adjustable Timer and Valve Control
PLC Timer Example: Sequential Control of Three Lights with Reset
Types of PLC
Cars Garage Counter From the Same Door PLC Logic
DC Circuit
Main differences between Sinking and Sourcing Circuits
Allen Bradley PLC Example with Sub routines
How to use Sub Routines with Allen Bradley PLC
Steps in PLC System Design
PLC attendance system design
UDT in the PLC Programming
Implement UDT in PLC Programming: User-Defined Data Type
Example of Automated Guided Vehicle with PLC
Relay-Operation
Relay Working Animation
Button 3C of the Matrix Keypad is pressed
How the Matrix Keypad works with a Micro controller?
CNC Machining vs 3D Printer
CNC Machining vs 3D Printer – What is the difference?
Electrical Machines MCQ Series 12
Zero Interface Level Calculation
How to do Interface Level Calculation using DP Transmitter ?
Butterfly Valve Failure caused Fire
Butterfly Valve Failure Caused Serious vicinity Heavy Fire
Top 300 Arduino Projects for Engineering Students
Instrument Cable
Difference Between Power Cable and Instrument Cable