Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: How to do Interface Level Calculation using DP Transmitter ?
Share
Notification Show More
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Level Measurement > How to do Interface Level Calculation using DP Transmitter ?

How to do Interface Level Calculation using DP Transmitter ?

Last updated: March 27, 2020 10:05 am
Editorial Staff
Level Measurement
No Comments
Share
4 Min Read
SHARE

Interface level calculation is not complicated.

Contents
Interface Level CalculationAt 4mA Case ( Zero interface level ) :-At 20mA Case ( When tank is full with Heavy fluid)So here’s our calibration range “-50 inH2O to 0 inH2O”Case 3 ( 50% is filled with Lighter fluid and 50% is filled with heavier fluid)

If we just have our basics concepts clear it is very straight forward.

First simple pressure measurement formula

Pressure Measurement Formula

The pic above shows a Container of Height 100 Inches

And this tank contains Liquid of Specific gravity 0.9

So what is the pressure at the bottom?

Height x Specific gravity = InH2O

100 (inches) X 0.9 = 90 inH2O

This Formula is adapted from Rosemount technical Datasheet (paper no :- 00816-0100-3207)

Note :- Specific gravity :- It compares with Density of substance with that of WATER (H2O)

Hence when we multiply ,

Height (Inches) x S.G ( Comparing with Density of substance with that of WATER (H2O))

= inH2O (The unit we get as product)

This our Simple Formula that we will be using.

Interface Level Calculation

One prerequisite recommended for this system is to fill impulse lines with Heavier fill fluid.

At 4mA Case ( Zero interface level ) :-

Zero Interface Level Calculation

In this case the entire portion we are measuring will be filled with “Lighter fluid” .

So as per our formula

Pressure at HP tapping = Height X Specific gravity

Pressure at HP tapping = 100 inches X 0.5 = 50 inH2O

(One prerequisite recommended for this system is to fill LP impulse lines with Heavier fill fluid to get stable reading at 20mA )

Hence

Pressure at LP tapping = Height X Specific gravity

Pressure at LP tapping = 100 inches X 1 = 100 inH2O

Differential pressure of Transmitter = H.P – L.P

Differential pressure of Transmitter = 50 inH2O – 100 inH2O = -50 inH2O

It means at -50 inH2O transmitter will give 4mA

Hurry we are already half way !!!!!

At 20mA Case ( When tank is full with Heavy fluid)

Full Interface Level Calculation

As per our formula

Pressure at HP tapping = Height X Specific gravity

Pressure at HP tapping = 100 inches X 1 =100 inH2O

Pressure at LP tapping = Height X Specific gravity

Pressure at LP tapping = 100 inches X 1 =100 inH2O (as LP tapping is filled with Heavier fluid)

Differential pressure of Transmitter = H.P – L.P

Differential pressure of Transmitter = 100 inH2O – 100 inH2O = 0 inH2O

It means at 0 inH2O transmitter will give 20mA

So here’s our calibration range “-50 inH2O to 0 inH2O”

For Extra information, what if we need to know what would transmitter give at 50% of Interface

Case 3 ( 50% is filled with Lighter fluid and 50% is filled with heavier fluid)

Interface Level Calculation

50 % of transmitter output will be 12mA transmitter at-25inH2O (Half of total calibration range -50inH2O to 0inH2O )

Interface = { (D.P by transmitter – Lower calibration range)/Span } X Total C-C distance

Here C-C distance nothing but center to center of measuring distance, as shown in above picture.

I = { ( -25 inH2O – (-50 inH2O) ) X 50inH2O } X 100 inH2O

Interface = 50 inH2O

Cross checking

Our total distance is 100 inches of H2O

When interface is at 50% means Interface between Lighter and heavier fluid will be at 50 inH2O

Thanks for reading !

Author : Asad Shaikh

Profile : Linkedin

Articles You May Like

Types of  Cable Shields

Instrument Air System Design

Thermowell Installation Problem

Cable Screen Grounding

Selection of a Fuse

Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

DP Level Measurement Problems
Siemens Pressure Transmitter with Remote Seals Calculations
Tuning Fork Level Switch Principle
Displacer Level Sensor Working Animation
Closed tank DP Level Transmitter with wet leg elevation zero direct mount Calibration
Magnetostrictive Level Measurement
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
Leave a Comment

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

Level Instruments Design Rules
Inductively Coupled Wire Guided Float Detectors
Root Cause Analysis of Differential Pressure Level Transmitter
Zero Elevation and Zero Suppression in Level Measurement
Nuclear Interface Level Measurement Principle, Limitations, Installation and Calibration
Ultrasonic Level Switch Working Principle
Radiation Level Measurement
Guided Wave Radar Questions and Answers

Keep Learning

Displacement Level Transmitter in situ calibration

Displacer (buoyancy) Level Transmitter Principle, Limitations, Design, Installation & Calibration

FMCW Radar level transmitter Working Principle

FMCW Radar Level Transmitter Working Principle

Level Sensors MCQ

Level Sensors MCQ – Industrial Instrumentation

Dip Tape

What is Dip Tape Level Measurement?

DP Transmitter Level Measurement for Closed Tank Wet leg Method

DP Transmitter Dry Leg & Wet Leg Calculations

Bubbler Liquid Level Transmitter Calculation

Bubbler Liquid Level Transmitter Calculation

Boiler Three Element Controller Philosophy

Boiler Three Element Controller Philosophy

Non‐contact RADAR Level Transmitter Pulse

Non Contact RADAR Level Transmitter Principle, Limitations, Design, Installation and Calibration

Learn More

FactoryTalk View Studio Site Edition Pop-Up Confirm Action

How to Automatically Close Pop-up in FactoryTalk View Studio?

DP transmitter Elevated 10 Feet above the Vessel

DP transmitter Elevated 10 Feet above the Vessel

Parallel Disk Gate Valve

Classification of Gate Valves

Transducers MCQ

Transducers MCQ

HVDC transmission compared to HVAC transmission

Comparison of HVDC transmission and HVAC transmission

PLC based 4 Way Traffic Light Control System

PLC based 4 Way Traffic Light Control System

SIS PFD - Safety Instrumented System

SIS PFD – Safety Instrumented System

Electric Circuits Objective Questions

Electric Circuits Objective Questions – Set 12

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?