Reading: Wiring Diagrams of PLC and DCS Systems – DI, DO, AI, AO
Inst Tools > Blog > Control Systems > Wiring Diagrams of PLC and DCS Systems – DI, DO, AI, AO
PLC and DCS control systems Wiring Diagrams for Digital Input (DI), Digital Output (DO), Analog Input (AI), and Analog Output (AO) signals.
Last updated: November 1, 2023 2:57 pm
Jatin Katrodiya
Control Systems PLC Tutorials
6 Comments
9 Min Read
In this article, we are sharing the basic concepts of PLC and DCS control systems Wiring Diagrams for Digital Input (DI), Digital Output (DO), Analog Input (AI), and Analog Output (AO) signals.
Wiring Diagrams of PLC and DCSDigital Input (DI) SignalsDigital Output (DO) SignalsAnalog Input (AI) SignalsAnalog Output (AO) SignalsDigital Input Signals to PLC / DCSTwo-Wire Connection with Input CardTwo-Wire Connection with Line MonitoringDI Card with Single Wire ConnectionDI With Relay – Wet Contact (For Coil)What is the Interrogation Voltage?DI With Relay – Dry Contact (For Coil)Digital Output Signals from PLC / DCSTwo-wire connection with Output CardDO With Relay – Wet ContactDO With Relay – Dry ContactInterfacing with Other Control Systems (DCS/PLC/ESD)DO with Line MonitoringAnalog Input Signals to PLC / DCSTwo-wire Connection with AI CardAI Card with Single Wire ConnectionFor Interfacing with Other Control SystemsDCS AO to PLC AIPLC AO to DCS AIAnalog Output Signals
Note that these diagrams are without a Barrier or isolator, fuses, or surge protector to keep them very simple and understandable.
Also Check: PLC and SCADA Training courses
The below list shows the basic types of wiring connections available for DI, DO, AI, and AO Signals:
  • Single-wire Connection
  • Two-wire connection
  • Two-wire connection with Line Monitoring
  • DI with Relay – Wet Contact
  • DI with Relay – Dry Contact
  • DO with Relay – Wet Contact
  • DO with Relay – Dry Contact
  • Interfacing with Other Control Systems
  • DO with Line Monitoring
  • Single-wire connection
  • Three-wire connection
  • Interfacing with other control systems
Input type with respect to the system
Terminal type/connection, Shield is not shown for simplicity.
Digital Input Without Relay and Dry Contact
The two-wire connection is used to connect field instruments like limit switches, proximity switches, motor run feedback, Pump start permissive, etc.
Digital Input With Line Monitoring
When we need additional protection measures to identify the short circuit and open circuit of digital inputs then we use this configuration.
Generally, a pair of resistors are used at the terminations of field instruments or in some cases at marshaling cabinets.
This works on the principle of change in resistance. During the Open circuit, both resistors R1 & R2 are in line, so we will get some loop resistance, say “x” ohms. During a Short Circuit, resistor R1 becomes zero and we will get some other loop resistance, say “y” ohms.
The input cards are designed such that they will identify the signal status and differentiate these conditions, alert the system engineers with alarms.
Digital Input Card With Single Wire Connection
Digital Input Card with Relay and Wet Contact
This configuration is used when we need an additional power supply for the field instruments, motor control centers, etc.
Generally, in marshaling cabinets, we make the necessary wiring arrangements as per the application requirements.
We are using the additional power supply in the marshaling cabinet (or at the control room side), so we are calling this a WET Contact.
When the field instrument is in an Open state then the relay will not be energized thus DI card doesn’t have the return signal, so it will be considered as OFF state.
When the field instrument is in a closed state then the relay will be energized thus DI card has the return signal, so it will be considered as ON state.
This external relay power supply is called as interrogation voltage.
The interrogation voltage from the panel can be 24 VDC, 110 VDC, etc.
PLC Programming Tutorial for Beginners - Siemens PLC Training Course
Interrogation voltage is a term used in relation to digital inputs of PLC or DCS control systems.
When there is some activity in the digital inputs like limit switch activation, then there will be a change in input state from open to close or close to open depending on the type of contact used in the limit switch.
Now we need to interrogate (identify) the state of these contacts (open/close) using a voltage. So we send a voltage (12VDC, 24VDC, 110 VDC, etc) to the limit switch and receive the signal back when the limit switch is in the closed state.
The PLC reads these signals and takes the action as per its logic. This voltage is called as interrogation voltage.
Digital Input Dry Contact
We are NOT using any additional power supply in the marshaling cabinet (or at the control room side), so we are calling this a DRY Contact.
When the field instrument is in an Open state then the relay will not be energized thus DI card doesn’t have the return signal, so it will be considered as an OFF state.
Example: Motor Run Feedback.
The interrogation voltage from voltage can be 24 VDC, 110 VDC, etc.
Output type with respect to system terminal type/connection.
The shield is not shown for simplicity reasons.
Digital Output With Two wire Connection
This configuration is used to control digital instruments like Solenoid Valves.
We may use Barriers after the DO card for safety reasons. Barriers are not shown in the diagrams.
When the DO command is given then the respective voltage will go to the field instrument and it will be energized.
When the DO command is taken back then the respective voltage will be stopped to the field instrument and it will be De-energized.
Digital Output Card With Relay and Wet Contact
We use an additional power supply (24 VDC, 110 VDC, 230 VAC, etc) in the marshaling cabinet (at the control room side) to power the field instrument.
This configuration is generally used for hooters, beacons, high-power solenoid valves, etc.
Digital Output with Dry Contact
This configuration is generally not preferred.
Interfacing with PLC or DCS Control Systems Wiring
This configuration is widely used in industries for interfacing with third-party control systems.
The line monitoring for digital output cards is also possible but up to relay coil and/or up to field shall be confirmed by the system vendor.
PLC SCADA Full Course in 7 Hours - InTouch | Wonderware Online Training
Shields are not shown for simplicity reasons.
The 4-wire instruments require an additional power supply.
This configuration is used to connect two-wire transmitters like PT, TT, FT, LT, etc.
We may use barriers also after the AI card for safety precautions. These are not shown in the diagrams.
DCS AO to PLC AI
DCS AO to PLC AI
Both side’s Active will not work.
PLC AO to DCS AI
PLC AO to DCS AI
Both sides Active will not work
Both sides Passive will not work.
DCS Analog Output Wiring
Author: Jatin Katrodiya
Join the Discussion! Share your thoughts about the basic wiring diagrams using the comments section.
Missed any?
  • Control System Architecture
  • Industrial Control Systems
  • Difference between DCS & PLC
  • Control System Security
  • What is PLC Redundancy?
  • DCS System Basics
Architecture of Allen Bradley PLC
Wood Sawing and Blower System: PLC Control Design
What is Human Machine Interface (HMI) ?
How to Blink Lights in Ladder Logic?
Interactions With Process Control Systems Philosophy
6 Comments
  • Srinu says:
    March 10, 2020 at 1:41 pm
    DI or discrete/digital input is the type of PLC input which used to read the status of digital input devices. The Digital input device only has 2 statuses, ON or OFF. ON state mean PLC DI point received status in form of electrical power (can be 24 VDC, 120 VAC, etc.) and OFF state mean PLC DI point received no power from devices. An example of a Digital input device is a switch.
    DO or discrete/digital output is the type of PLC output which used to control digital output devices. Digital output devices only have 2 status, ON or OFF. ON command mean PLC DO point send command in form of electrical power (24 VDC, 120 VAC, etc.) and OFF command means PLC DO send no power to devices. An example of digital output devices is a relay.
    AI or analog input is the type of PLC input which used to read the value from the sensor. AI receives value from the sensor in the form of electrical current (4-20 ma) or electrical voltage (1-5 V). ADC (Analog to Digital Converter) inside PLC will convert current or voltage to a digital value in the form of 16 or 12-bit word data to further process. An example of a sensor is the temperature sensor. The temperature sensor will measure temperature and send measurement value to the AI channel in the form of current or voltage.
    AO or analog output is the type of PLC output which used to control analog devices. AO sends a command to the device in the form of electrical current (4 – 20 mA) or electrical voltage. DAC (Digital to Analog Converter) inside PLC will convert a digital value (12 bit or 16-bit word data resulted from PLC calculation) to current or voltage and send it to a controlled device through the AO channel. An example of an AO device is the control valve, PLC could control opening percentage of the control valve with send 4 – 20 mA current which represents 0 – 100% open command.
  • Vikash kumar pandey says:
    March 11, 2020 at 11:08 pm
    Nice concept
  • P Maruthi Prasad says:
    June 6, 2020 at 7:01 pm
    Excellent explanation in very simple way possible. Thank you very much for valuable information.
  • Raj Narayan says:
    July 20, 2020 at 8:22 pm
    Sir very nice information
  • h.YK says:
    November 17, 2020 at 1:05 pm
    Yes, following is missed:
    “Analog Input (AI) -Three-wire connection”
  • Milan kar says:
    April 3, 2021 at 9:42 pm
    Sir you’re great and help us to understand
Flood Warning System using Programmable Logic Controller
Ladder Logic for Stair-Case wiring using Toggle Switches
Siemens PLC Comparator Logic
Top PLC Manufacturers
Basic PLC Ladder Programming Example
Purpose of Gateways, Bridges & Routers in Networking
PID Controller Theory
Loop Calibrator to Simulate a 4-20 mA Signal
Zener Barrier Protection
Zener Diode Barrier Principle
Industrial Automation Cold and Hot Standby
Relay Parts
Difference Between NO and NC Contacts
S7 1200 PLC Program
Download Free Robotics Software
Step by Step Guidelines to Download Free Robotics Software
PLC Program to Separate Different Size Objects
Surge Protection Device
Why Baud Rate is Important in Modbus Network
Factory Acceptance Test of PLC Panel
Factory Acceptance Test (FAT) of a PLC Panel
Voltage and Current Phase Relationships in an Inductive Circuit
corroded tank
Cathodic Protection – Sacrificial Anodic and Impressed Current
Helix and Spiral Tubes - Pressure Sensor
Helix and Spiral Tubes – Pressure Sensor
How to program a running hours meter in PLC
Allen Bradley Studio 5000: Motor Running Hours PLC Program
DCS ESD Logic Overview Graphic Display
Automation System Process Functionalities
Sinking and Sourcing Devices Operation