Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: Weirs and Flumes Flow Measurement
Share
Notification Show More
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Flow Measurement > Weirs and Flumes Flow Measurement

Weirs and Flumes Flow Measurement

Open-channel flow meter is weir, which is nothing more than a dam obstructing passage of liquid through channel. Study Weirs and Flumes Flow Measurement.

Last updated: November 2, 2023 5:33 am
Editorial Staff
Flow Measurement
1 Comment
Share
14 Min Read
SHARE

A very different style of variable-area flow meter is used extensively to measure flow rate through open channels, such as irrigation ditches.

Contents
Open Channel Flow MeasurementWeir-type Open Channel Flow MeterParshall FlumeWeir-flume channel flow measurementUltrasonic weir flow sensorWeirs flow measurement

If an obstruction is placed within a channel, any liquid flowing through the channel must rise on the upstream side of the obstruction.

By measuring this liquid level rise, it is possible to infer the rate of liquid flow past the obstruction.

Open Channel Flow Measurement

The first form of open-channel flowmeter is the weir, which is nothing more than a dam obstructing the passage of liquid through the channel.

Three styles of weir are shown in the following illustration; rectangular, Cippoletti, and V-notch:

open-channel flow meter

A rectangular weir has a notch of a simple rectangular shape, as the name implies.

A Cippoletti weir is much like a rectangular weir, except that the vertical sides of the notch have a 4:1 slope (rise of 4, run of 1; approximately a 14-degree angle from vertical).

A V-notch weir has a triangular notch, customarily measuring either 60 or 90 degrees.

Weir-type Open Channel Flow Meter

The following photograph shows water flowing through a Cippoletti weir made of 1/4 inch steel plate:

Weirs and flumes flow measurement

At a condition of zero flow through the channel, the liquid level will be at or below the crest (lowest point on the opening) of the weir. As the liquid begins to flow through the channel, it must spill over the crest of the weir in order to get past the weir and continue downstream in the channel.

In order for this to happen, the level of the liquid upstream of the weir must rise above the weir’s crest height. This height of liquid upstream of the weir represents a hydrostatic pressure, much the same as liquid heights in piezometer tubes represent pressures in a liquid flow stream through an enclosed pipe.

The height of liquid above the crest of a weir is analogous to the pressure differential generated by an orifice plate. As liquid flow is increased even more, a greater pressure (head) will be generated upstream of the weir, forcing the liquid level to rise. This effectively increases the cross-sectional area of the weir’s “throat” as a taller stream of liquid exits the notch of the weir (Note).

Note: Orifice plates are variable-pressure, constant-area flowmeters. Rotameters are constant-pressure, variable-area flowmeters. Weirs are variable-pressure, variable-area flowmeters. As one might expect, the mathematical functions describing each of these flowmeter types are unique!

weir flow meter principle

This dependence of notch area on flow rate creates a very different relationship between flow rate and liquid height (measured above the crest) than the relationship between flow rate and differential pressure in an orifice plate:

weir flow meter formula

Where,
Q = Volumetric flow rate (cubic feet per second – CFS)
L = Width of crest (feet)
θ = V-notch angle (degrees)
H = Head (feet)

As you can see from a comparison of characteristic flow equations between these three types of weirs, the shape of the weir’s notch has a dramatic effect on the mathematical relationship between flow rate and head (liquid level upstream of the weir, measured above the crest height).

This implies that it is possible to create almost any characteristic equation we might like just by carefully shaping the weir’s notch in some custom form.

A good example of this is the so-called proportional or Sutro weir, which is designed to have a linear relationship between head and flow rate:

weir flow meter notch

Sutro weirs are not used very often, due to their inherently weak structure and tendency to clog with debris.

A rare example of a Sutro weir appears in the following photograph, discharging flow from a lake into a stream:

Sutro weir flow meter principle

The metal plates forming the weir’s shape are quite thick (about 1/2 inch) to give the weir sufficient strength.

A good construction practice seen on this Sutro weir, but recommended on all weir designs, is to bevel the downstream edge of the weir plate much like a standard orifice plate profile. The beveled edge provides a minimum-friction passageway for the liquid as it spills through the weir’s opening.

A variation on the theme of a weir is another open-channel device called a flume. If weirs may be thought of as open-channel orifice plates, then flumes may be thought of as open-channel venturi tubes:

open-channel orifice plates

Like weirs, flumes generate upstream liquid level height changes indicative of flow rate. One of the most common flume design is the Parshall flume, named after its inventor R.L. Parshall when it was developed in the year 1920.

The following formulae relate head (upstream liquid height) to flow rate for free-flowing Parshall flumes:

Q = 0.992H1.547                       3-inch wide throat Parshall flume
Q = 2.06H1.58                           6-inch wide throat Parshall flume
Q = 3.07H1.53                           9-inch wide throat Parshall flume
Q = 4LH1.53                               1-foot to 8-foot wide throat Parshall flume
Q = (3.6875L + 2.5)H1.53       10-foot to 50-foot wide throat Parshall flume

Where,
Q = Volumetric flow rate (cubic feet per second – CFS)
L = Width of flume throat (feet)
H = Head (feet)

Flumes are generally less accurate than weirs, but they do enjoy the advantage of being inherently self-cleaning. If the liquid stream being measured is drainage- or waste water, a substantial amount of solid debris may be present in the flow that could cause repeated clogging problems for weirs. In such applications, flumes are often the more practical flow element for the task (and more accurate over the long term as well, since even the finest weir will not register accurately once fouled by debris).

Once a weir or flume has been installed in an open channel to measure the flow of liquid, some method must be employed to sense upstream liquid level and translate this level measurement into a flow measurement. Perhaps the most common technology for weir/flume level sensing is ultrasonic.

Ultrasonic level sensors are completely non-contact, which means they cannot become fouled by the process liquid (or debris in the process liquid). However, they may be “fooled” by foam or debris floating on top of the liquid, as well as waves on the liquid surface.

Parshall Flume

The following photograph shows a Parshall flume measuring effluent flow from a municipal sewage treatment plant, with an ultrasonic transducer mounted above the middle of the flume to detect water level flowing through:

Parshall flume measuring flow

Once the liquid level is successfully measured, a computing device is used to translate that level measurement into a suitable flow measurement (and in some cases even integrate that flow measurement with respect to time to arrive at a value for total liquid volume passed through the element, in accordance with the calculus relationship V = ∫ Q dt + C).

A technique for providing a clean and “quiet” (still) liquid surface to measure the level of is called a stilling well. This is an open-top chamber connected to the weir/flume channel by a pipe, so the liquid level in the stilling well matches the liquid level in the channel.

Weir-flume channel flow measurement

The following illustration shows a stilling well connected to a weir/flume channel, with the direction of liquid flow in the channel being perpendicular to the page (i.e. either coming toward your eyes or going away from your eyes):

weir-flume channel flow measurement

To discourage plugging of the passageway connecting the stilling well to the channel, a small flow rate of clean water may be introduced into the well. This forms a constant purge flow into the channel, flushing out debris that might otherwise find its way into the connecting passageway to plug it up.

Note how the purge water enters the stilling well through a submerged tube, so it does not cause splashing on the water’s surface inside the well which could cause measurement problems for the ultrasonic sensor:

Ultrasonic weir flow sensor

ultrasonic weir flow sensor

A significant advantage that weirs and flumes have over other forms of flow measurement is exceptionally high rangeability: the ability to measure very wide ranges of flow with a modest pressure (height) span. Another way to state this is to say that the accuracy of a weir or flume is quite high even at low flow rates.

Earlier in this section you saw a three-image representation of liquid flow through a rectangular weir. As fluid flow rate increased, so did the height (head) of the liquid upstream of the weir:

Weirs flow measurement

weir flow measurement

The height of liquid upstream of the weir depends on the flow rate (volumetric Q or mass W) as well as the effective area of the notch through which the fluid must pass. Unlike an orifice plate, this area changes with flow rate in both weirs and flumes.

One way to envision this by comparison is to imagine a weir as acting like an elastic orifice plate, whose bore area increases with flow rate. This flow-dependent notch area exhibited by both weirs and flumes means that these devices become more sensitive to changes in flow as the flow rate becomes smaller.

A comparison of transfer function graphs for closed-pipe head elements such as orifice plates and venturi tubes versus weirs and flumes shows this striking difference in characteristics:

weirs and flumes

Looking at the orifice plate / venturi tube graph near the lower-left corner, you can see how small changes in flow result in extremely small changes in head (differential pressure), because the function has a very low slope (small dH/dQ ) at that end.

By comparison, a weir or flume produces relatively large changes in head (liquid elevation) for small changes in flow near the bottom end of the range, because the function has a very steep slope (large dH/dQ ) at that end.

The practical advantage this gives weirs and flumes is the ability to maintain high accuracy of flow measurement at very low flow rates – something a fixed-orifice element simply cannot do.

It is commonly understood in industry that traditional orifice plate flowmeters do not maintain good measurement accuracy much below a third of their full-range flow (a rangeability or turndown of 3:1), whereas weirs (especially the V-notch design) can achieve far greater turndown (up to 500:1 according to some sources).

If you liked this article, then please subscribe to our YouTube Channel for Instrumentation, Electrical, PLC, and SCADA video tutorials.

You can also follow us on Facebook and Twitter to receive daily updates.

Read Next:

  • Swirl Flow Meter Principle
  • Basics of Level Measurement
  • Flow Transmitter Square Root
  • Magnetic Flow Meter Animation
  • Limitations of Coriolis flow meter
Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Basic Working Principle of Vortex Flowmeter
Turbine Flow Meter Coefficient and Scaling Factor
What is Water Cut Meter?
Lobed Impeller Flow Meters Working Principle
Types of Vortex Flow Meter Sensors
Troubleshooting Magnetic Flow Meters Common Problems
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
1 Comment
  • Omer Fadl says:
    April 20, 2025 at 3:43 am

    Very informative topic, thank you, and keep spreading knowledge

    Reply

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

Overview of Positive Displacement Flow Meters
Thermal Dispersion Flow Switch Working Principle
Transit Time Flow Meter – Types, Advantages, Disadvantages
Dall Tube Flow Meter – Principle, Advantages, Disadvantages
Area Velocity Flow Meter Principle
Working Principle of Flow Switch with Animation
Design Considerations of Orifice Plate
Coriolis Mass Flow Meter as a Multi-Variable Transmitter

Keep Learning

Oscillating Piston Flow Meters Principle Animation

Nutating Disc Flow Meters Working Principle

Magnetic Flow Meters

Magnetic Flow Meters Installation Guidelines

Flow Meters Troubleshooting

Turbine Flow Meters Troubleshooting

Flow Measurement

Continuous Flow Measurement

V Cone Flow Meter Working Principle

V Cone Flow Meter – Principle, Advantages, Disadvantages

magnetic-flow-meter-earthing

Importance of Magnetic Flow Meters Grounding

Turbine Flow Meter Installation Procedure

Reasons to Calibrate Flowmeters

Reasons to Calibrate Different Types of Flow Meters

Learn More

Absorption Chiller Principle - HVAC System

HVAC Double Effect Absorption Chiller

Micro 870 Rockwell PLC

Rockwell Automation Allen Bradley PLC for Smaller and Medium Projects

Pilot Operated Back Pressure Regulator Valve

Pilot Operated Back Pressure Regulator Valve Test

Chromatograph Principle

Basics of Chromatograph Operation

Simulation in Machine Expert HVAC

How to do Simulation in Schneider PLC?

Performance Characteristics of Sensors and Transducers

Performance Characteristics of Sensors and Transducers

Questions on Piping and Instrumentation Diagrams

Questions on Piping and Instrumentation Diagrams

How does the IIoT work - Industrial Internet of Things

How does the IIoT work? – Industrial Internet of Things

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?