Reading: Minimum Oil Circuit Breaker (MOCB) No Vendor Spares & Service
Inst Tools > Blog > Root Cause Analysis (RCA) > Minimum Oil Circuit Breaker (MOCB) No Vendor Spares & Service
110 KV Minimum Oil Circuit Breaker (MOCB); No Vendor Spares & Service threaten their sudden failure and indefinite outage.
Last updated: September 28, 2022 3:02 pm
S Raghava Chari
3 Min Read
Electrical engineering root cause analysis (RCA) related to 110 KV Minimum Oil Circuit Breakers (MOCB); No Vendor Spares & Service threaten their sudden failure and indefinite outage.
ProblemThe author solves the problemBenefits Received
Article Type:Root Cause Analysis (RCA)
Category:Electrical
Equipment Type:Circuit Breakers
Author:S. Raghava Chari
Problem
The author found the Feeder-A and Feeder B Minimum Oil Circuit Breaker (MOCB) top dome level glasses (LG)  missing.
The crew reported the vendor had neither supplied the 4‑years ago ordered LGs and MOCB overhaul services.
Several follow-ups to the vendor lead to no response and went in vain.
He sketched the LG guessing from the remaining LG portions. He talked a laboratory glass parts maker into supplying these agreeing to his 100 Nos. min order though only the plant had two MOCBs only! Fortunately, the glassmaker charged ½ of what the breaker vendor quoted for the two LGs.
He found the Electricity Board using tens of the same make MOCBs. Checking with them, he found they have well-trained MOCB overhaul crews. Finding their MOCBs to having no LGs the author offered them 90 LGs and requested their overhaul help. Their crew finely Overhauled one MOCB at a time.
Benefits Received
  1. MOCB-B had handled several on-offs and MOCB-A several on-offs and numerous lightening arrester heavy fault current trips. The electricity board crew completed the long due safety need.
  2. Giving away the negligible cost LGs influenced the EB engineer to do the direly needed but not available elsewhere overhaul
  3. Assurance of a ready source for the fragile LGs and overhaul services
Author: S. Raghava Chari
  • Welding Machine Problems
  • Miscellaneous Electrical Tasks
  • 11 KV Bus A to Bus B Phase Check
  • Inability to Test Repaired HT Motors
  • Street Light Poles Corrosion Problems
An Indian Plants all turbines’ low Vacuum & Saudi Plant turbo-compressor only
Serious Constraints Prevent using an Available Turbine Flow Meter
Solving Control Valve Hunting: Instrument Troubleshooting
Phosphate Dozing System Problems
Root Cause Analysis for Plant Trip Due to Work on Incorrect Tag
Carbamate Plunger Pump Packing Problems Eliminated
How Kalrez O-rings Seal So effectively So Long?
Root Cause Analysis of Differential Pressure Level Transmitter
Miscellaneous Electrical Tasks – Repaired Reformer Tubes Weld Stress Relief
Repeat Safety Valve Popping caused Urea Plant Shutdown
Flanged Rotameter Caused Pipe Weld Cracks and Gives Wrong Readings
Critical High KiloWatt Motor Winding Burnout Threats
Control Valves Leak Tightness Restoration Pose Difficulties
Turbine Flow Meter (TFM) Field Calibration Uncommon Request
Plunger Pump Drive
Too Low Efficiency Torque Converter Elimination Attempt
11 KV Bus A to Bus B Phase Check Problem
Burst Transformers Root Cause Analysis
Root Cause Analysis – Burst Transformers and 11 kV Input Breakers
Under and Over-Capacity Control Valve
Under and Over-Capacity Control Valve Pose Poor Controllability
Compressor IP Case Discharge Temperature Gradually Increases
Compressor Anti-Surge Control near-miss incident
Rotary Drier Shell to Split Gear drive
Rotary Drier Shell to Split Gear drive eliminates too frequent drive failures
Leaky Boiler Drum Level Switch
Leaky Boiler Drum Level Switch Stops NH3 Plant Commissioning
Pump Low throughput
[RCA] Pump Low throughput Eliminated
DC Motors Objective Questions and Answers
175+ DC Motors Objective Questions and Answers
Burner Management System (BMS) Principle
What is Burner Management System (BMS)?
Home Heating
What Type of Heating is Best for Your Home?
AC Generator Operation
Types of AC Generators
Time Response Analysis
Steady-state Errors & Error Constants
Full Wave Rectifier Peak Inverse Voltage
Full Wave Bridge Rectifier Peak Inverse Voltage
Gamp 5 Compliance in Pharmaceutical Industry
What is insulation
What is insulation? How to Choose the Insulation Material?