Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: What is a Logic Solver? – Safety PLC
Share
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Safety Instrumented System (SIS) > What is a Logic Solver? – Safety PLC

What is a Logic Solver? – Safety PLC

SIS Logic solver safety functions to be made independent and separated from the basic process control system (BPCS).

Last updated: September 28, 2022 3:36 pm
Sriram Krishnamurthi
Safety Instrumented System (SIS)
No Comments
Share
8 Min Read
SHARE

In Safety Instrumented System (SIS), Logic solvers are very critical to the process industry handling various hydrocarbons, Oil & Gas or Nuclear, Power plant installations, SIS Logic solvers are designed in such a way that they’re robust and have very high reliability for the safe operation of the plants.

Contents
Logic Solver BasicsRequirements for SIS Logic Solver DesignManufacturersCertificationSafety ManualCommunicationApplication ProgramIndependenceDiagnosticsSecurityDocumentation

Various International Standards such as IEC, ISA & ANSI govern the requirements of SIS Logic solver design.

Logic Solver Basics

A safety instrumented system logic solver is typically made up of redundant (double or triple) processors, power supplies, and human interfaces. The safety logic solver will process many safety instrumented functions (SIF) concurrently.

SIS Logic solvers are built with very high-speed microprocessors and perform the required logical functions/calculations within a very short time period. Usually, the processing speed lies in milliseconds.

DeltaV SIS Logic Solver
Figure: DeltaV SIS Logic Solver

In addition to that, there will be continuous monitoring of the healthiness of the processor (also known as Watchdog), in case of anyone running the processor fails to perform, secondary logic solver takes over the control, and error is reported back to the control room via annunciation system, system alarm, etc.

Requirements for SIS Logic Solver Design

Usually dedicated Logic solvers – programming device with independent Input / Output modules & wiring is installed across many plants. In a few cases as per the LOPA/PHA study outcome some DCS controllers functions as SIS logic solver.

Safety functions implemented on a certified logic solver must follow the Safety Manual for that logic solver.

Manufacturers of logic solvers from different manufacturers shall meet the requirements of IEC61508 / 61511. Every manufacturer shall register their product with approved Safety system verifying agencies and update their Safety manual.

The number of instrumented LOPA/PHA study outcome credits implemented on a single logic solver in a given LOPA scenario must not exceed the limits of the logic solver.  

Logic Solver in Safety PLC
Image Courtesy: Emerson

SIS programming must follow specifically approved programming practices and other restrictions. Safety Instrumented Functions implemented on a certified logic solver must follow the Safety Manual for that logic solver. 

Logic solvers purchased for SIS applications (Not involving burners/heaters/flame rods/ ignitors) must be certified according to IEC 61508. Logic solvers having burners for furnaces & fired heaters are to be certified according to IEC 61508, EN298 (for gas fuels), or EN230 (for liquid fuels).

SIS software, hardware, and procedures used to develop and execute the application program shall be subject to configuration management and shall be maintained under revision control.

Manufacturers

There are many reputed manufacturers in the SIS logic solver, all such manufacturers are to comply with IEC 61508 and be certified by various international agencies like TUV, Exida, etc.

Reputed manufacturers such as Schneider Electric (Triconex), Honeywell, Emerson, Yokogawa, Siemens, Omran, Allen Bradly, and ABB systems are used in the industries in various safety and critical control applications. These systems are certified and must be used in accordance with the applicable safety manual.

Certification

IEC provides all the requirements necessary to design, implement, and operate a Safety system logic solver in a safety-relevant application according to its certificate. 

The certifying authority assesses each logic solver intended for use in SIS applications.  The hardware, software, and safety manual of the logic solver are analyzed for the purpose of the application to be used. 

New logic solvers purchased for SIS applications must be certified according to IEC 61508

Emerson SIS DeltaV Cabinet
DeltaV SIS Cabinet

Safety Manual

A safety manual accompanies each certified SIS logic solver. The safety manual describes any limitations applicable for operation and maintenance.

It also addresses diagnostics, testing, programming languages, and the SIL level for which the device is capable.

Communication

The design of any SIS communication interface shall ensure that any failure of the communication interface shall not adversely affect the ability of the SIS to achieve or maintain a safe state of the process

The communication interface is robust to withstand electromagnetic interference including power surges without causing a dangerous failure of the SIS.

Hardwired communication (DO to DI). If communication is required for SIL-2 or SIL-3, then multiple communication methods must be utilized.

Application Program

SIS Logic solver – The application program of the SIS shall be in accordance with the application program safety requirements.

The application program is to be designed in such a way that all parts of the application program are executed on every application program scan. Process safety time requirements shall be considered when establishing application program scanning requirements.

Application program and data are to be designed in such a way that they can be modified as and when required, any program revision to be monitored/controlled, version management, backup, and restoration procedure.

Independence

SIS Logic solver Software for safety functions to be made independent and separated from software for basic process control (BPCS).

The SIS code must be clearly identified in the program. Typically, in industry, the SIS is physically separated from the BPCS by the use of independent logic solvers. 

Diagnostics

SIS Logic solvers shall be capable of performing ‘Diagnostics’. The functionality of processors shall be monitored and if there are any troubles in running the processor, a secondary processor to take over. Also, any errors are to be reported immediately as well

Application-level diagnostics are to be implemented such as external watchdogs, application data integrity checking, and sensor validation to meet the required SIL

Security

In logic solver applications, the Safety code must provide protection against changes to sensor ranges, sensors being placed in manual, final elements being placed in non-safe conditions, changes to SIS set points and delay timers, and SIF conditions being bypassed.

Documentation

All logic solvers must have the below documentation/approvals to be used in SIS applications.

Safety manuals with the version nos. Revision nos to be maintained for traceability.

Detailed Operation, Maintenance, and Diagnostic procedures with different types of modules installed – Processor (CPU), Input, Output & Communication modules.

Data communication/Interface requirements with HMI, Other systems.

Reference:

IEC 61508: “Functional safety – Standard for Electrical, Electronic & Programmable Electronic systems”

IEC 61511: “Functional safety – Safety instrumented systems for the process industry sector”

If you liked this article, then please subscribe to our YouTube Channel for Electrical, Electronics, Instrumentation, PLC, and SCADA video tutorials.

You can also follow us on Facebook and Twitter to receive daily updates.

Read Next:

  • SIS Design
  • SIL Verification
  • SIS Proof Testing
  • Common Cause Failure
  • Intrinsic Safe Calculation
Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Layers of Protection Analysis (LOPA) Interview Questions
Probability of Failure on Demand (PFD)
Safety Instrumented System Interview Questions and Answers
Understanding Safety Integrity Level IEC 61511
BPCS Control System and ESD Safety System of Delta-V DCS
High Reliability of Safety Instrumented Systems
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
Leave a Comment

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

What is Safety Control System ?
SIS Bypass and Impairment – Safety Instrumented System
Applying Probability Laws to a Safety Instrumented System
Free Safety Instrumented System Training Course
SIS Hardware Fault Tolerance – Methods to Overcome HFT issues
Pilot-operated Safety and Relief Valves
De-energize to Safe Loop philosophy
ESD System Insights: Signals for Emergency Valve Shutdown Explained

Keep Learning

Smart Valve Monitoring

SIS Instruments and Valves Inline Testing – Safety Instrumented System

hipps

What is High Integrity Pressure Protection System?

SIS Failures and Reliability - Safety Instrumented Systems

SIS Failures and Reliability – Safety Instrumented Systems

pressurized water reactor

SIS Example : Nuclear Reactor Controls

energized-to-safe-loop

Energize to Safe Loop philosophy

What is HIPPS System in Oil and Gas

What is HIPPS System in Oil and Gas?

SIS System Testing - Safety PLC Control System

SIS System Testing – Safety PLC

Safety Instrumented System Engineer Interview Questions

Safety Instrumented System Engineer Interview Questions

Learn More

Star to Delta Conversion

Star to Delta and Delta to Star Conversion Formula

PLC Program for Automatic Oil and Water Separation Process

Oil and Water Separation Process using PLC Programming

How to Use SMD Components in Electronic Circuits

How to Use SMD Components in Electronic Circuits?

Electrical Cables Interview Questions & Answers

Conductor Size Selection in Distribution Power System

Electrical Machines Questions and Answers

Rotating Electrical Machines Quiz

diode-limiter-principle

Diode Limiters/Clippers Operation

Programmable Logic Controller (PLC) Questions and Answers

Programmable Logic Controller (PLC) Questions and Answers – 4

AC Induction Motor Construction

Basics of AC Induction Motors

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?