Reading: Pulverizer Electrical Problem Solved
Inst Tools > Blog > Root Cause Analysis (RCA) > Pulverizer Electrical Problem Solved
Electrical engineering root cause analysis (RCA) related to pulverizer poor availabilities and the problem solved.
Last updated: September 28, 2022 3:08 pm
S Raghava Chari
3 Min Read
Pulverizer ProblemAuthors SolutionBenefits of the RCA Solution
Article Type:Root Cause Analysis (RCA)
Category:Electrical
Equipment Type:Bus ducts, Switchgear, Transformers,
Author:S. Raghava Chari
Pulverizer Problem
Why low on stream hrs? Because of the V-belts coupling the 1500 RPM motor and 750 RPM pulverizer last max a month!
Why? The reasons are:
  1. Because of corrosion and dust frozen Inoperable belt tensioners, the crew crow bar the first belt into first drive and driven pulleys’ grooves and crow bar it to the last grooves, groove by groove. All belts go this way. Thus they are ½ dead right at installation
  2. Belts running in the hygroscopic dust deposited pulley grooves slip, squeal to the high heavens and die within a month or often sooner
  3. Consequent 750 sets of V-belts and 24 pulleys sets changes reduce pulverizer availabilities to 50%, require frequent pulverizers changeovers etc. and tire the operation and maintenance crew unbearably and reduced production by 10 to 15%
Authors Solution
A few days ponder showed a way out:  the author recalled his college day pole changing motor topic; though he did not understand Motors application Handbook” given winding change details, and electrical engineers were diffident, a smart re-winder rewound a test motor for 750 RKM.
Its tire coupling coupled to a pulverizer did so well that all enthusiastically modified all the pulverizers’ drives within a month.
The below are the mentioned benefits of the author’s solution.
  1. Rs 5, 00, 000 yearly savings from no pulleys and no belt changes
  2. No Crew overtime payments
  3. 5% less power consumption i.e. yearly recurring Rs 5, 62, 000 – 1980 costs –  savings
  4. Far higher pulverizers and motors bearing lives
  5. Pulverizers and hence plant availability shot by 10%
  6. Freedom from boring, repetitive and low-tech tasks boosted technicians and operators morale
  7. The operation and maintenance crew freed of dull low tech repeat chores thanked the author and spent the saved time for knowledge improvement
  8. Thanks to items 1-5, the modification pays for itself in a day
Author: S. Raghava Chari
  • Poorly Built Switchgears
  • Lightning Arrester Burst
  • 110 KV Connection to Feeder
  • Transformer Problem Solved
  • Replace Failed Motors Quickly
Erratic H2 Flow Rotameter
CO2 Stripper Old Differential Pressure Transmitter Stopped Working
Hunting of Control Valves
CO2 Stripper Collapsed Internals Revamp
Serious Constraints Prevent using an Available Turbine Flow Meter
Cooling Tower fan FRP fan blades saves and saves
Fired Boiler Induced Draft Fan (IDF) Failures Upset all Plants Operations
Too often done riskily repaired Roof Hot Spots eliminated forever
Thermocouple Extension Lead Problem
Pump 3-monthly Seal Leaks threaten entire Plant Shut down Indefinitely
11 KV Bus A to Bus B Phase Check Problem
A Plant Bucket Elevators chains too short chain lives problem eliminated
Junction Box Cooler
Junction Box Internal Corrosion Problems and Solutions
Arc Fault Breaker (AFB) Electrical Problem Solved
Centrifugal Compressor outage reduced
Centrifugal Compressor Outage Reduced – Root Cause Analysis
Valve Actuator Passing
Lessons Learned from Actuator Passing Incidents
Incident Investigation: Motor Operated Valve Lesson
Doubtful Temperature Readings
Doubtful Temperature Readings threatens Soaking Pit Wrecks
Plant Shutdown Analysis: Valve Closed and SOV Coil Failure
Mechanical Temperature Indicators (MTI) Problem
Various Codes used in CNC Programming
Instrumentation Standards
Electronic Equipment Purging Principles & Standards
Butterfly valve Principle
Short Notes on Different Valve Types
Transmitter Detailed Specifications
How to Calculate Heat Load In Electrical Panel
How to Calculate Heat Load in Electrical/Electronic Panel Enclosure
Air Cylinder Consumption Calculation for Control Valves
Types of Pressure
Types of Pressure – Instrument Questions and Answers