Instrumentation engineering root cause analysis (RCA) of failed letdown valve as it leads to urea plant shut down for several hours.
| Category: | Instrumentation |
| Equipment Type: | Control Valves |
Introduction
Reactor outlet Control Valve PCV 205 lets down 220 bars of effluent into the 20‑bars first flash separator.
The author from other users’ feedback had stocked a spare valve, two inner valves (IV; plug + stem assembly), and two-seat rings.
He named the spare valve PCV 205 (S), to tell it apart from the original PCV 205.
Failed Letdown Valve Problem
After commissioning 3 weeks, Hi-Hi reactor pressure tripped the plant: still, many relief valves popped and created a chaotic situation.
Post chaos quelled inspection found a hundred percent open PCV 205 scale reading indicated that the reactor pressure control system functioned properly, yet the reactor hi-hi pressure trip and chaotic plant shutdown (SD).
From this, the author concluded: detached plug → the flow close design seated it on the seat → reactor overpressure → hi-hi trip shutdown the CO2 feed compressor and the liquid NH3 and carbomate feed pumps → yet the popped relief valves and chaotic SD
Immediate Solution
The crew replaced the failed PCV 205 with PCV 205 S in 8-hours; unscrewing the rust frozen 3” CS screwed flanges from PCV 205 and screwing these on PCV 205 S delayed the task by 1½ hours.
Crew dissembling the PCV 205 at the shop found
1) unscrewed and detached plug from the 1 to ¾” NF threaded stem step;
2) corroded stem and plug threads.
Root Cause Analysis
The author’ Root Cause Analysis is:
- The admitted passivating air into the feed stream is unable to reach the stem to plug thread crevices; hence the threads corrosion and high stem to plug cavity clearance
- Consequently, flow turbulence fluttered the plug severely; eventually, the plug to stem securing pin sheared and the plug detached from the stem.
- Flow position the plug on the seat – flow close design control valve (CV) – and stopped the flow; hence, the catastrophic overpressure caused plant shutdown (SD)
Remedial Steps
Fearing a quick problem repeat the author readied PCV 205 ASAP using the spares. In addition, he got shop-made CS flanges screwed to PCV 205 to avoid the last occasion delay.
The author asked all to find a plug to stem joint strengthening or other methods to be free of the problem forever.
Read Next: Repeat Failures of Valves
Author: S. Raghava Chari
- Valve Positioners Failed
- Errors and Faults in Siemens PLC
- Electrical Engineering Problems
- Pressure Taps Block Valves Leaks
- Unstable & Drifting Values of Transmitter