Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: What are Analog Inputs? – Analog Signals Processing in PLC
Share
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > PLC Tutorials > What are Analog Inputs? – Analog Signals Processing in PLC

What are Analog Inputs? – Analog Signals Processing in PLC

In this article, we will talk about analog input signals processing in PLC and how can we handle these signals in the automation process.

Last updated: June 17, 2023 2:05 pm
Mahmoud Salama
PLC Tutorials
No Comments
Share
14 Min Read
SHARE

In this article, we will talk about analog input signals processing in PLC and how can we handle these signals in the automation process.

Contents
What are Analog Input Signals?Analog Input Processing in S7-1200 and 1500Analog Inputs in S7-300 and S7-400Which are Best for Control? – Analog or Digital SignalsConclusion

Contents:

  • What are analog input signals?
  • Input analog processing in S7-1200 and 1500.
  • Input analog processing in S7-300 and 400.
  • Which are best for control? – analog or digital signals
  • Conclusion.

What are Analog Input Signals?

Before we dive into how to handle analog input signals in TIA Portal, let’s start by understanding analog inputs first.

Any automation system needs input signals to understand the status of the process to be able to take decisions that will keep the process running and stable. These input signals are either discrete or digital input signals which are in the form of 0 or 1 values. The other type of input is the analog signals.

An Analog signal is simply a continuous representation of a physical quantity in your system, so if you need to monitor temperature or pressure in your process, an analog signal will give you continuous and instantaneous values that correspond to the real changes in the physical quantity.

Analog signals are provided in many standard forms, but most commonly the 0-10V or the 4-20mA. It will depend on the type of analog sensor you are using, and it will also dictate the type of PLC analog module that you can use.

Assume an analog pressure sensor that has a measuring range of 0-10 bar and an output in the form of 4-20mA. Usually, an analog signal will have a linear relationship between the measured physical quantity and the corresponding output.

That means if the sensor is measuring a 0 bar it will give a 4mA signal and if it is measuring a 10 bar it will give a 20mA signal and the same in between will also be linear. See picture 1.

What are Analog Input Signals

Picture 1 – Analog signal representation.

The PLC still can’t understand the 4-20mA of the physical quantity, and here comes the use of the analog module of the PLC. The analog module will make another transformation to this representation so the PLC can actually understand it.

The analog module will convert the analog mA measurements into digital values that depend on the type of the module, but for Siemens PLC, these values are always in the range of 0 – 27648. So if the sensor is mearing 0 bar the output will be 4mA and it will be converted to 0 value inside the PLC. See picture 2.

Analog to digital conversion of the input signal

Picture 2 – Analog to digital conversion of the input signal

The PLC will then convert the 0-27648 values into the equivalent physical measurement depending on your programming which we will get to later. See picture 3.

The scaled measured value inside the PLC

Picture 3 – The scaled measured value inside the PLC.

The analog processing of temperatures is quite different because the temperature sensor behavior with the physical changes is not linear as would a level or a pressure sensor do. That is why there are standardized tables for the different types of temperature sensors that tell which temperature corresponds to which sensor value.

That is why with temperature measurement you would select special types of input modules of your PLC where these standard tables are internally defined and you directly get the temperature value corresponding to the sensor measurement.

That is why you can’t find a temperature sensor that has a voltage or current measurement range written on it. You will only find the sensor type written, for example, PT100, PT1000, KTY84, PTC, and so on.

Analog Input Processing in S7-1200 and 1500

To see how we handle analog signals in modern S7 family PLC, let’s start by creating a new project and adding an S7-1200 CPU. We will also add an analog input/output module. See picture 4.

Analog Input Signals Processing in PLC

Picture 4 – Adding an analog input module.

Now, let’s define our input signal tag, we will assume a pressure sensor that can measure pressure between 0 and 10 bars and gives a corresponding signal between 4 and 20mA.

We will define that input signal in the first tags of the input module. See picture 5.

Define the input signal tag in PLC

Picture 5 – Define the input signal tag.

As we said before, the input module can work with different input signals, whether it is 0-10V or 4-20mA, so we need to assign the right configuration for our sensor.

As we said the pressure signal is given in the form of 4-20mA so we will configure our input channel to that. See picture 6.

Siemens PLC Configure the input channel

Picture 6 – Configure the input channel

Now that we finished the hardware configuration part, we will start programming our handling code. To do so, we will create a function FC so we can reuse it each time we have an analog signal to process. Inside this FC we will create the logic which will handle the analog signal and convert it into the physical measured value.

In TIA Portal there are predefined instructions that we can use to do just that, these instructions are the NORM_X and the SCALE_X instructions. See picture 7.

NORM_X and SCALE_X instructions

Picture 7 – NORM_X and SCALE_X instructions

As you can see, the NORM_X will normalize the analog input into a value between 0 and 1, and then the SCALE_X will be used to scale this normalized value to the range of the measured physical value, which in our sensor case between 0 and 10 bars.

We used a function FC instead of writing our code directly in the main OB1 to make our code reusable with any analog signal. Each time I have a new analog input signal I will just drag and drop the FC block into our main OB1 and just write the associated parameters of the required input. See picture 8.

PLC Analog Signal Processing

Picture 8 – Drag and drop your FC.

When you drag and drop the FC into your main OB1, you will be asked to provide the associated parameter of this function call.

In our case, the input signal is the pressure sensor and the ScaledMIN and ScaledMAX are the measurement value range of 0-10 bars. See picture 9.

Pressure sensor configuration in PLC

Picture 9 – Assigning the function parameters to our pressure sensor.

If I have a new analog input, then I won’t have to recreate the PLC logic again, I will just drag and drop the FC into the main OB1 and assign the new sensor parameters.

Let’s assume that we now have a new analog sensor for measuring the level inside a water tank between 0 and 100 % of the tank. We will do the same steps as we did before, starting with defining the new input tag. See picture 10.

PLC level sensor logic

Picture 10 – Define new level sensor

Next, we will configure the input channel for the level sensor as we did in picture 6. We will assume the same configuration.

Next, we will just drag and drop the FC we created and just assign the parameters of the level sensor. See picture 11.

Analog Inputs in Siemens TIA Portal

Picture 11 – Reusing the FC with the level sensor.

As you can see from the previous picture, this is one of the many advantages of using functions FCs in your logic as it helped reduce the amount of programming we made.

Now you have a generic code that can be reused many times with any input analog signal you can need in your PLC project.

 See the next simulation for input signals processing in Siemens PLC.

PLC Analog Inputs

Analog Inputs in S7-300 and S7-400

To see how we handle analog signals in older S7 family PLCs like S7-300, let’s start by creating a new project and adding an S7-300 CPU.

The PLC chosen already have enough analog input channels, so we won’t add any analog modules. See picture 12.

Analog Input Processing in S7-300 and S7-400

Picture 12 – Add an S7-300 PLC.

Then we will define the new analog sensor tag, we will assume a pressure sensor that has a measuring range between 0 and 100 bar and an output of 4-20mA.

We will configure the PLC input channel as we did before with the S7-1200 to fit our analog input sensor. See picture 13.

Tia Portal Analog Input

Picture 13 – Configure the input channel.

Now to the PLC coding part, the instruction in s7-300 that is used to handle analog processing is different from the s7-1200.

In the S7-1200 PLCs, we have to use NORM_X and SCALE_X. but with the S7-300 we don’t have the normalized instruction, only a SCALE instruction is used. See picture 14.

PLC SCALE instruction in S7-300

Picture 14 – SCALE instruction in S7-300

As you can see from the previous picture, the SCALE instruction in S7-300 is kind of similar to the NORM_X and SCALE_X instructions combined together. There is one more clear difference which is the BIPOLAR input.  

The BIPOLAR input is used to indicate if the value at the IN parameter is to be interpreted as bipolar or unipolar. The parameter can assume the following values:

  • BIPOLAR = 1 then the input integer value is assumed to be between -27648 and +27648. For example, when the analog sensor gives us an output in the range of -10V to +10V
  • BIPOLAR =0 then the input integer value is assumed to be between 0 and 27648. For example, when the sensor gives us an output in the range of 0-10V

 And this is simply how to handle analog input signals in both S7-1200 and S7-300 PLCs.

Downloads:

  • Analog Input Signals in PLC – PDF Logic
  • Analog Inputs in Siemens Tia Portal

Which are Best for Control? – Analog or Digital Signals

Look, both signals are critical and useful for any automation system, but I personally prefer to use the analog signals if I can, because having analog signals measurements for the process’s physical quantities will give me continuous monitoring of process parameters which will enable me to better track and control my process.

Also, having continuous monitoring of the parameters will enable me to set different control logic for different signal values, it will make it easier to have a value range for controlling the process and another value ranges for alarms and warnings of the process deviating from normal operation.

Conclusion

  • An Analog signal is a continuous representation of a physical quantity in your system.
  • Analog inputs are most commonly provided in the 0-10V or 4-20mA range.
  • Analog signal processing means converting the analog 4-20mA signal into a range of values that corresponds to the real physical quantity and that the PLC can understand.
  • In the modern S7 family of PLCs like S7-1200, handling analog signals is done using the NORM_X and the SCALE_X instructions.
  • In the older S7 family of PLCs like S7-300, handling the analog signals is done using the SCALE instruction, which is basically a combination between the NORM_X and the SCALE_X instructions.

If you liked this article, then please subscribe to our YouTube Channel for Instrumentation, Electrical, PLC, and SCADA video tutorials.

You can also follow us on Facebook and Twitter to receive daily updates.

Read Next:

  • HMI Screen Design Applications
  • Static and Temp Variables in PLC
  • Power Supply Sizing for Systems
  • How to Read the PLC Datasheet?
  • Firmware Version of a PLC System
Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

PLC Programming for Weight-Based Packaging
PLC FBD Program for Bottle’s Capping with Rotating Mechanism
Basic PLC Ladder Programming Example
PLC Logic GATE Program
PLC Memory Organization – Data Files and Program Files
Advanced Skills Required for a PLC Programmer to Get a Job
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
Leave a Comment

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

PLC Program for Motor Starter
What is Profinet and How to Configure in Siemens PLC?
Difference between DCS & PLC Systems
PLC Program for Temperature Control using Thermostat
#17 PLC Best Practices – Log PLC Uptime and Trend it on HMI
Transferring Data Across PLC Systems – TSEND_C and TRCV_C
PLC Example on Switch Program with Timers
PLC Program to Control Gas Pressure using Closed-Loop

Keep Learning

Ethernet IP Commissioning Tool software

How to Configure IP Address in Rockwell PLC?

TIA Portal MOVE Instruction

MOVE Instruction in PLC – What You Need to Know?

Ferrule Example

Ferrules and Cross Ferruling

PLC Programming Example on Bottle Line Control

PLC Programming Example on Bottle Line Control

What is RS Linx - Types of Softwares in Rockwell Automation

What is RS Linx? Types of Software in Rockwell Automation

Omron PLC Online Training Course

Omron PLC Online Training Course

Tank Level Control Process in PLC

Tank Level Control in PLC

Wiring in PLC System

Wiring in a PLC Control Panel

Learn More

Routine Tests of Transformers

Transformer Testing – Routine Tests of Transformers

Download Modscan software

How to Use ModScan Software for Testing Modbus Communication?

Difference between Anode and Cathode

Difference between Anode and Cathode

ESP8266 WiFi Module Projects

ESP8266 WiFi Module Projects for Engineering Students

Ladder Logic Counters Instruction

Up Counter PLC Program

principle of time base generator

Time Base Generator

Root Locus Concepts Objective Questions

Root Locus Concepts Objective Questions

Temperature Sensor Failure

Temperature Sensor Failure

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?