Reading: Yokogawa DCS Tutorials – Configuration of Analog Input (Transmitter)
Inst Tools > Blog > Control Systems > Yokogawa DCS Tutorials – Configuration of Analog Input (Transmitter)
In this article, we will learn how to do the configuration of analog input (transmitter) in the Yokogawa Centum VP DCS system.
Last updated: November 27, 2021 10:22 pm
S Bharadwaj Reddy
Control Systems PLC Tutorials
8 Comments
7 Min Read
In this article, we will learn how to do the configuration of analog input (transmitter) in the Yokogawa Centum VP DCS system. The DCS abbreviation is Distributed Control System.
Yokogawa DCS TutorialsDCS Configuration of Analog Input (Transmitter)
Here we will configure a new transmitter in the Centum VP software.
You need to have some details before configuring a new transmitter in the DCS system.
Yokogawa DCS Tutorials - Configuration of Analog Input (Transmitter)
First, you need the details of the Analog Input Card where you are going to connect the new transmitter.
Also, you need the location details of this analog input card in the system cabinet like FCS number, IOM details, Node number, and then AI card slot number.
You can get the details from the Nest Loading list.
Also Read: What is Nest Loading List?
The below animation will help you to understand the configuration procedure of a new flow transmitter in the Yokogawa DCS.
Yokogawa Centum VP DCS Analog Input Configuration
Follow the below steps to configure a new transmitter in DCS.
Step 1: Open Field Control Station
Open the System View software.
You may have one or more number of FCS (Field Control Station) in your plant.
Go to the required FCS where you want to add a new transmitter. The FCS selection depends on your plant area and the location of the new transmitter. Check your plant control system documents for more details.
Field Control Station in Yokogawa
Step 2: Go to IOM
Next, go to the IO module page in the selected FCS.
You have to expand the FCS folder and again expand the IOM folder.
IOM in Yokogawa DCS
Step 3: Go to Node
Next, You have to go to the respective node where the AI module is installed.
You can get the details of FCS, IOM, Node location details from the Nest Loading list.
Open Node in Centum VP DCS
Step 4: Go to Analog Input Card
Next, select the analog input card (AAI841-H) and open it.
The location AI card details can be found in your plant nest loading list.
Analog Input Card in Yokogawa Centum VP
Step 5: Configure New Tag
Next, you have to add the tag name in the respective AI module channel.
Here the tag syntax is “%%I11FT1101”
Then go to file and download.
Configure New Tag in Centum VP DCS
Step 6: Go to Function Block Builder
Now go function block builder for creating the faceplate of the new tag.
Function Block Builder in Centum VP DCS
Step 7: Select the Control Drawing
Open the respective control drawing builder or choose any empty drawing.
Control Drawing in Yokogawa DCS
Step 8: Open the Control Drawing
Here, we selected a new control drawing.
Control Drawing Builder in Centum VP
Step 9: Insert Function Block
Right-click on the screen and select the “Insert” option and then click on “Function Block”
Insert Function Block in Centum VP
Step 10: Insert PIO Block
Here select the “PIO” block from the drop-down menu.
Insert PIO Block
Step 11: Enter the New Tag in PIO Block
Now we have to enter the same tag name in the PIO block.
In this example, our tag is %%I11FT1101
Enter the New Tag in Centum VP
Step 12: Right-click and select Function Block
Again we need another function block for the faceplate.
Yokogawa Function Block
Step 13: Select PVI Block
Go to the menu and search for PVI block.
Insert PVI Block
Step 14: Insert PVI Block
Now select PVI block (Input Indicator Block).
Each PVI block creates a faceplate for the tag after download.
Input Indicator Block in Centum VP
Step 15: Enter Faceplate Tag in PVI Block
Now we have to add a name for the PVI block.
In this example, we named the tag “11FI1101”.
This tag name is used for the faceplate.
Enter Faceplate Tag
Step 16: PIO and PVI Blocks are Ready
Now both PIO and PVI blocks are created.
We need these two blocks when adding a new transmitter for monitoring purposes.
Step 17: Connect the PIO and PVI Blocks
Select the wire from the top menu and connect the PIO and PVI blocks as shown in the below image.
Step 18: Right-click on PVI Block
Now we have to add the details of the new transmitter in the DCS system.
Right-click on the PVI block.
Step 19: Select Edit Detail
Select the “Edit Detail” option.
Select Edit Detail in Centum Vp
Step 20: Enter Transmitter (Tag) Description
Now a new window will be opened and it is called “Function Block Detail Builder”.
In this window, you can find different tabs like Basic, Tag, Input, Alarm, Output, Connection, Others.
In the basic tab, you can enter your faceplate description in the “Tag Comment” field.
Enter Faceplate and Tag Description
Step 21: Enter Transmitter (Tag) Range in DCS
Next, go to the “Input” tab. Here you can define the LRV and URV of your transmitter.
Fill the Low limit value (LRV) and High limit value (URV) as shown in the below image.
Enter Tag Range in DCS
Step 22: Set Engineering Unit
In the Basic tab, you can define the required engineering unit for the new transmitter.
Set Engineering Unit in Yokogawa DCS
Step 23: Click Update button
Then click the update button
Click Update button in Function Block Detail Builder
Step 24: Close Function Block Detail Builder
All settings are done, close the function block detail builder window.
Step 25: Go to File menu
Click on the File menu.
New Transmitter Configuration in Centum VP DCS
Step 6: Initiate Online Download
Select the “Download” Option.
Next, an online download will be started for this FCS. A pop-up confirmation window will appear and press ok.
Online Download in Yokogawa DCS
Watch Video: Yokogawa DCS Offline Download
In this article, we discussed the basic settings required for the configuration of a transmitter in a DCS system.
We have many other features available like defining the alarms, displaying the transmitter value in graphics, creating trends for the new tag, etc. We will discuss these topics in upcoming articles.
If you liked this article, then please subscribe to our YouTube Channel for Instrumentation, Electrical, PLC, and SCADA video tutorials.
You can also follow us on Facebook and Twitter to receive daily updates.
  • DCS Troubleshooting
  • Commissioning of DCS System
  • DCS Control System Spares
  • Yokogawa DCS Architecture
  • DCS System Layout
Distributed Control System & Motor Control Center Interface Philosophy
Remote Connectivity to Industrial Automation Systems
Allen Bradley Powerflex VFD
PLC Example on Switch Program with Timers
PLC Based Product Sorting Machine System – Lift Control
How to do Scaling for Analog Input in RSLogix 500?
8 Comments
  • zubair says:
    December 23, 2021 at 12:19 pm
    very helpful material please carry on your data is very perfectively managed.
  • Syed Farman says:
    January 28, 2022 at 2:43 pm
    I want to get basic knowledge of Dcs system.
    • Charles Isimite says:
      January 30, 2024 at 12:56 am
      Good work.
  • Rahul Kumar says:
    January 18, 2024 at 11:41 pm
    please provide DCS training course
  • Isaiah Mugabe says:
    February 4, 2024 at 5:04 pm
    GREAT STAFF. THANK YOU SO MUCH
  • Ehsan Khademi says:
    March 29, 2024 at 11:13 pm
    Hi,
    How can I monitor an Analog Input signal that described abow, monitor in HIS?
  • ben says:
    April 19, 2024 at 2:50 am
    hi,
    thank you for this great effort and great tutorial, I was wondering where to define the alarms treshold for this transmitter as I don’t see any place in PVI block for this purpose.
    kind regards
    • Editorial Staff says:
      April 19, 2024 at 9:44 am
      1. PVI Block > Edit Properties
      2. Open Faceplate > Tuning
What is a Watchdog Timer in PLC?
MCQ on PLC (Programmable Logic Controller)
Advanced PLC Conveyor Control: Forward and Reverse Rotation
PLC Programming Projects for Beginners
Communication between InTouch Scada and Allen Bradley PLC
PLC Automatic Pedal Switch for Speed Control
Safety Door Interlock PLC Program
Compare DCS, PLC, RTU
Difference between DCS, PLC, and RTU ?
Push button Motor PLC Logic
Siemens Tia Portal Function Block
Function Blocks in PLC (FBs) – What You Need To Know?
How to Delay a Sensor Signal in PLC?
Free WinCC SCADA Training Course
Free SCADA Training Course
Download Modscan software
How to Use ModScan Software for Testing Modbus Communication?
PID Controller Tunning Manually
PID Controller Parameters Tuning Manually
Features of Scada Which are Must in an IoT System
Cars Garage Counter From the Same Door PLC Logic
Chlorine dioxide measurement principle
Chlorine dioxide Analyzer Principle
Accelerometer Vibration Probe
Accelerometer Vibration Probe Principle
Time Division Multiplexing Objective Questions
Pneumatic Actuators
Self-Actuated Valves, Pneumatic & Hydraulic Actuators
Thermocouple Law of Intermediate Metals
Thermocouples Law of Intermediate Metals
How to Start Writing SCL in Siemens PLC
Rules for Writing SCL Language in Tia Portal
Pressure Transmitter Re-Range Questions