Reading: Best Way to Build Troubleshooting Mindset for Automation Engineer
Inst Tools > Blog > Control Systems > Best Way to Build Troubleshooting Mindset for Automation Engineer
In this article, you will learn the best way to build a troubleshooting mindset for the industrial automation engineer.
Last updated: September 28, 2022 2:23 pm
Hussien Ghareb
Control Systems PLC Tutorials
7 Min Read
In this article, you will learn the best way to build a troubleshooting mindset for the industrial automation engineer (PLC and DCS systems).
What is meant by Troubleshooting?System Level TroubleshootingComponent Level TroubleshootingSystem Level TroubleshootingComponent Level Troubleshooting
Hello Automation seekers, hope you all are doing great today in this paper we will discuss one of the most required skills for Automation Engineers which is “Troubleshooting”.
Unfortunately, this skill cannot be learned or educated, it comes by contacting the field to build up your troubleshooting experience.
However, we will scope on some basic principles which will improve our troubleshooting skills amazingly, all we need is to get back and read these words with great care and understanding.
Troubleshooting is the process of finding the cause or fault of a machine malfunction. Faults may cause a machine to do many things.
For example, the fault could cause the machine to stop, skip a step, or perform a step incorrectly.
First Step
There are two basic rules that all of us has to consider whenever we are facing a faulty system, these two concepts have to be the first base in your mindset structure:
  • The Time taken by the troubleshooter to figure out the fault is critical because as all of us know one-minute stoppage of a factory may cost a lot of money.
  • Also, a great point to mention is “how to figure out the faults without causing other faults or without getting the problem bigger?”
As the machine is in a faulty situation, you might unintentionally make an action that would make the problem bigger so you have to be very careful in these situations.
Second Step
Another thing that you have to be concerned about is the “Troubleshooting Level”, mechatronics system troubleshooting can be performed at one of two levels:
  • Systems Level Troubleshooting
  • Component Level Troubleshooting
System-level troubleshooting is a process where the troubleshooter identifies, through observation and measurement, the failed component of a system (i.e. power supply, processor, input or output module, or field device).
Component-level troubleshooting is a process where the troubleshooter repairs the faulty component identified through system-level troubleshooting. This means finding the parts (i.e. IC, resistor, diode) within the component that must be replaced to repair it.
Example
Here we have the WBH (water Bath Heater) system presented in Fig. (1), these types of systems are used to control the temperature of Natural Gas for some reasons that we might discuss later.
Industrial Automation Engineer Troubleshooting
Fig 1
There are a variety of Automation components that handle this system such as:
  • DC power supply module
  • Relays
  • Level transmitters
  • HMI screen
  • Flame control device or any other devices
Assume now that we are facing a faulty WBH system, at first all you need is to identify your machine component clearly.
By getting into the first level we have to check every module and device in our system if it is doing its job correctly?
Once we figured out the faulty module or device then we have just to replace it. As represented in Fig. (2).
Automation Engineer Troubleshooting Tips
Fig 2: PLC Panel
So, with the help of wiring and HMI application (that shows a flame sensor alarm) which it means that the gas goes to the boiler but there is no fire there, so the controller turns off the gas valve for safety and abort the whole operation.
After another carefully trying, we found that there is a fire inside the boiler but why the flame sensor and flame card do not sense it? (Shown in Fig.2)
As you noticed that over some attempts, we get closer to the faulty device, now we have two possibilities (flame sensor, flame controller card).
By getting an individual check for both devices we figured out that the faulty device is the flame controller card.
Fig 3 Flame Card
For now, the problem is solved by replacing the flame card that is represented in Fig. (3), but what about going through the next level by trying to fix the defective flame card?
By going through the next level, we will not just be satisfied with replacing the defective component instead we will go through a detailed level as we can fix the defective device that is shown in Fig. (4).
Component Level Troubleshooting in PLC
Fig 4
As we can see the device consists of a simple PCB (printed circuit board) that contains some electronic components such as resistors, relays, diodes, and capacitors.
The function of this controller is to receive the signal from the flame sensor and convert it into a unique digital signal but in our case, there were some dead capacitors in the controller which do not make the controller sense or see the signal of the flame sensor.
Electrical Circuit Troubleshooting
Fig 5
Finally, the damaged capacitors were replaced and we have made a full maintenance program to the boiler.
Fig 6
Simply we can notice that the component level troubleshooting is harder than the system level troubleshooting but on the other hand instead of buying a new flame controller we solved the problem with just some capacitors which is a great cost-saving.
  • Software Problems in PLC
  • Hardware Problems in PLC
  • DCS System Commissioning
  • PLC Panel Commissioning
  • Circuit Protection Devices
Single-Acting Cylinder Control using Proximity Sensor
PID Controllers in Closed Loop Control Systems – PLC Basics
PLC Output Types
PLC Program for Water Level Control Logic
What is Multi-touch Technology? – Industrial Automation
How a PLC do the Scaling for a Sensor ?
Siemens TIA Portal: Motor Forward Reverse PLC Logic
PLC Count values higher than 999
Programming Schneider PLC Manual Sequential Machine
Things to Take Care of When Designing SCADA System
How to Read an Electrical Wiring Diagram?
Auto Sugar Bag Filling Station
PLC Program for Controlling Sequence of Conveyors with Interlocking
SCADA System
What is SCADA System?
Quantitative PID tuning procedures
CRA Module in Schneider PLC
CRA Module in Schneider PLC – Remote IO Adapter Module
Cascade-Temperature-Control-System
Cascade Temperature Control System
Sequencer Output in PLC
PLC Sequencer Instruction with Example
Ziegler-Nichols closed-loop Tuning
Ziegler-Nichols Closed-Loop Method (Ultimate Gain)
Displacer Level Sensor Working Animation
pressure switch ladder-logic diagram
Draw the appropriate Pressure Switch Symbol ?
foam fire protection system
Basics of Foam Fire Fighting System
Burst Transformers Root Cause Analysis
Root Cause Analysis – Burst Transformers and 11 kV Input Breakers
Digital Electronics Objective Questions – Set 7
baffle-and-nozzle assembly
Pneumatic Sensing Elements
Saybolt Viscometer
Saybolt Viscometer
Siemens CP Module
Communication Processor Module in Siemens PLC