Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: Package System Architecture – Control & Instrumentation
Share
Notification Show More
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Control Systems > Package System Architecture – Control & Instrumentation

Package System Architecture – Control & Instrumentation

The control & instrumentation team in the detail design engineering company provides the package system architecture details.

Last updated: March 26, 2024 3:44 pm
Mansoor Mohseni
Control Systems Instrumentation Design PLC Tutorials
No Comments
Share
16 Min Read
SHARE

In engineering and design of industrial projects the word “Package” is frequently used in different technical documents, but what is the meaning of it?

Contents
Package Definition and Supply CycleInstrumentation Engineering Roles in Package Design and Supply CycleProcurement Phase of the ProjectVendor SelectionComplex PackagesPackage System Architecture Design DocumentPackage Interfacing DiagramConsiderations on Package Systems ArchitectureDetailed Design ProjectsBid Phase of the ProjectDetail Engineering Phase of Vendor ActivitiesIndustrial Process Plant ProjectsOverall Project Control PhilosophyConclusion

Package Definition and Supply Cycle

The “Package” word is used as a title for a set of combinations of equipment, devices, and instruments that provide some required process functions, like Material /Fluid Transfer, Compression, Temperature/ Heat Exchange, Material Mixing /Combinations, and so on.

Usually in Engineering Companies, based on the type of required process function or physical characteristics, each Package will be followed for Engineering Design or Purchasing by one dedicated technical discipline known as an Originator, although such package will have technical items relevant to other disciplines too.

In fact, the Originator is a coordinator or a bridge for interfacing with the package vendor for discussion or transferring all technical (and maybe other) points with them.

Package System Architecture

Figure 1: Package Design Engineering and Supply Cycle

Figure 1 shows a simplified Design Engineering and Supply Cycle in Detail Design Engineering Company for some packages which are followed by Package Originator (as an example Rotary Machines Department).

As it is clear, the Package Originator will be front face on communication channels with Package Vendor(s) during the Procurement Cycle, while at the early stages of the project, they shall get all other (company) technical discipline’s comments and requirements for providing complete engineering detail design and accordingly Material Requisition.

Instrumentation Engineering Roles in Package Design and Supply Cycle

Usually, in all Industrial Plant Design, the I&C Engineering Team has vital roles in almost all Package Requisitions with their important effects or consequences, but why?

Since all process parameters of Packages are similar to other plant process functions to be monitored and controlled, so all Packages need some systems and instrumentations for monitoring, control, and protection too. Such required systems and instrument signals may be implemented by plant DCS and ESD or may be applied in dedicated package panels or cabinets.

Regardless of the mentioned cases for required systems, however, the I&C Engineering Team shall provide the required data for detailed design and relevant material requisitions, while they shall continue their designs and activities by monitoring (and commenting on) vendor documents accordingly in harmony with total plant design.

By starting the project, the I&C Engineering Team shall get and analyze the project inputs (similar to other technical disciplines) in order to provide the Control Philosophy requirements of the project and then provide some documents in the same harmony for process plant and package control, monitoring, and safety functions.

Here it shall be emphasized that making the harmony and synchronous design for the whole project plant and packages is very important and all project successes in future phases of plant operation and maintenance (and of course total performance efficiency) have close relationships with the mentioned goal. So the I&C Engineering Team shall consider seriously such design harmony approaches in providing Package System Architecture and Standard (Requirements) Specifications Documents for Packages too (See Figures 1 and 2).

Procurement Phase of the Project

During the Procurement phase of the project, I&C Engineering Team shall provide help and assistance to Package Originators for reviewing the different vendor’s offers on the satisfaction of project requirements and making suitable comments (or even transferring data) in order to make balances for all vendor’s offers (especially from I&C point of view).

Vendor Selection

After vendor selection, the I&C Engineering Team will provide more detailed project requirements to selected vendors during meetings (especially Kick-Off Meeting =KOM) and other project communications and document transfers. In fact they help vendors to reach the best results on system configurations and required instrumentations via clarifications and making comments on vendor documents.

Complex Packages

In some cases (especially for complex packages that have a dedicated system) I&C Engineering Team will attend in Factory Acceptance Test to check successful vendor progress on providing project requirements.

Also for complex packages that need the attendance of package specialists at the project site (such as Site Acceptance Test = SAT or Site Assistance for Commissioning and Start-up), the I&C Engineering Team may have roles for Assistances or Acceptances too. (Again refer to Figures 1 and 2).

Instrumentation Detail Design Engineering

 Figure-2: Package Design and Supply Cycle as one of the Main Parts of I&C Engineers Roles and Responsibilities (In Detail Design Engineering Company)

Package System Architecture Design Document

As mentioned above, the I&C Engineer Team shall help the package originator and also vendors to better understand the details of project requirements on package system requirements (in harmony with the process plant). Such a target may be achieved by producing a Package Control Block Diagram or Package System Architecture Diagram by the I&C Engineering Team. Since some packages may not have any dedicated system, sometimes this document is called a Package Interfacing Diagram (which may be a better title).

The main approach of such a document shall be clarifying the main required systems and signals interfacing of the package with process plant (main) control and safety systems (DCS & ESD) further to the definition of different important locations in which those packages may have interfaces with them.

If a Package System Architecture Diagram is provided based on Design Document System Architecture, it may be more useful since their definitions and locations may be uniform. Format uniformity of System Architecture Documents will help the I&C Engineering Team to extract required similar data for the provision of data in other documents like Layouts, Power Consumption, Wiring Diagrams, and so on, while generally, it will help any study on plant process control philosophy for everyone to be understandable easily.

Package Interfacing Diagram

Figure 3 shows a sample of a schematic template for providing a Package System Diagram or Package Interfacing Diagram in Detail Design Engineering Company, which is applicable for almost all Package System Architecture /Interfacing types.

(If it is compared with the Design Document for Project System Architecture Diagram mentioned in References you may find similarities in the format of documents).

Package Control Block Diagram

Figure 3: Package Systems Architecture / Package Interfacing Diagram Schematic Template. (Provided by Detail Design Company)

Considerations on Package Systems Architecture

By reviewing Figure 3 we can mention some considerations on the Design Document for Package System Architecture below:

This template can cover all types of packages with different system /signal interfacing types, so you may easily provide a Typical or Dedicated Diagram for all project packages.

Notice that each diagram can be provided based on different scopes of package inclusions, while easily being modified due to more detailed negotiation with package vendors (if required) accordingly. (See Figures 4, 5, 6)

Package Interfacing Diagram

Figure-4: Heater Package System Architecture Diagram (Package Interfacing Diagram) – Simple Package without Control/Auxiliary Panel

Such a design diagram shows a general view of required functions or system parts of the package, and not necessarily the exact type of them. On the other hand, it is schematically and not a detailed document. As an example, the shown symbols for panels or cabinets are schematically and not representations of the exact dimensions (models) or quantity of them.

This document easily helps vendors to better understand the different main locations of the project plant and so their package parts distribution accordingly. However, it easily defines the battery limits for the scope of supplies (and works) of different parts.

As an example, the vendor can see the exact scope of supply for required powers and cables (which are crucial points in making future conflict problems or discussions) and the technical basis for any limitations discussions (like special cables, or cable length limits).

DCS Package System Architecture

Figure-5: Antifoam Dosing Package System Architecture Diagram (Package Interfacing Diagram) – Simple Package without Control/Auxiliary Panel

Detailed Design Projects

Some detailed design projects or companies may not produce a Design Document for Package System Architecture Diagram and they transfer project conditions by some texts or explanation documents.

Although they follow their procedures for doing the jobs, it shall be noticed that sometimes (and especially for complex packages) such diagrams can easily represent better and faster than several text sheets.

Bid Phase of the Project

During the bid phase of the project, all package vendors were asked to prepare primary Package Vendor System Architecture based on Design Document One.

Then balancing and comparison of different received offers would be done better (uniformly) and easily. However, selected vendors can prepare detailed documents accordingly with more details.

Instrument Package System

Figure-6: Refrigeration Package System Architecture Diagram (Package Interfacing Diagram) – Simple Package with Complete Dedicated Control/Auxiliary Panel

Detail Engineering Phase of Vendor Activities

Since during the detail engineering phase of vendor activities, they should provide a type of document for defining their package interfacings.

So using the Design Document for Package System Architecture will be a good guide for their document format and (required) information, while Package Vendor System Architecture shall have more exact details including detail types, models, and also quantities. (See Figure-7)

Instrumentation For Equipment Packages

Figure-7: Sample of Vendor Document for Package System Architecture Diagram (Package Interfacing Diagram) – Boiler Package

Although the Design document for Package System Architecture may be very useful, but it shall be attached to other explanation documents which define the exact project requirements and specifications. I&C Engineering Team may provide such items as Tag Number Ranges, Requisition Notes (mentioned in Package Requisition), Standard Specification for Instrumentations Supplied with Packages, Standard Specifications for Control and Safety Systems (PLCs) supplied with Packages (sometimes instead of two specifications Detail Design Company may provide just one specification as “Standard Specification for Instrumentation and Control & Safety Systems supplied with Packages”).

Industrial Process Plant Projects

Usually, Industrial Process Plant Projects include so many packages, and so several I&C specialists (from the I&C team) work on different packages, or even during the project execution cycle, one package may be followed by a sequence of specialists, while any difference in their approaches may cause some problems in project progress (or in the integrity of Overall Project Control Philosophy). Using the same schematic template for Package System architecture can make uniformity and continuity approaches for all of them.

Referring to Figure 1, some package vendors may use separate external I&C team or even sub-vendors for the implementation of the Instrumentation and System Requirements of their package. In such cases, Design Document of Package System Architecture can help package vendor to better and faster discuss with their sub-vendors on transferring project requirements (for their estimations and setting project schedules).

Design Document for Package System Architecture further to the I&C Engineering Team can help other technical disciplines for definition of their battery limits and required scope of supply (As an example such a diagram will help the originator and also the Electrical Team to clarify such items like skids and power requirements).

In some projects or companies, instead of using the same schematic template, they may use separate and different formats of diagrams (and they may use them just for some limited packages).

Overall Project Control Philosophy

Please notice that although in such a trend, they will make their project targets, but it may cause some dispersions on the integrity of the Overall Project Control Philosophy. Sometimes a bit of dispersion may cause big future problems in process plant operations and related activities like operator training, supplying spare parts/ items, special safety notices for different types of operation and maintenance, and so on.

Although using the same schematic template will help the I&C Engineering Team keep convergence on their activities, but sometimes, and for special cases they may need further auxiliary diagrams to define more detail of project requirements too.

Figure 8 shows a sample auxiliary diagram provided for one special case of the package (Belt Conveyor) which shall have exact signals based on project requirements. (See Figure-8)

Field Instrument package

Figure-8: Sample of Auxiliary Document for Package System Architecture Diagram (Package Interfacing Diagram) – Belt Conveyor Required Detail Signals

Conclusion

Providing a Package System Architecture Diagram by the I&C Engineering Team (in Detail Design Engineering Company) before the BID stage will be very useful for project progress (better and faster) while it may help keep the same approach as Plant Control and Safety Systems (DCS and ESD) and accordingly keeping uniform integrity of Project Control Philosophy. However, package vendor can use it for issuing their similar document for representing package detail interfacings.

References:

  1. Instrumentation and Control Project Package
  2. Design Document for Project System Architecture
  3. Vendor Document for Project System Architecture
Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Difference Between PLCSIM and PLCSIM Advanced? – Siemens PLC
DCS Program to Maintain Draft in Furnace
Instruments Tapping Points – Common versus Individual
Advanced PLC Programming for Defective Parts Sorting
Motor Classic Control Circuits using Single Push button
Basic PLC Ladder Programming Example
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
Leave a Comment

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

What is a Feedback Control System? Types & Advantages
PLC Program for Alternate Output Circuit with Latched Function
PLC Logic: Control Spray Nozzle, Fans, and Puncher
PLC Program to Simulate Gate Array Logic
Communication between Wincc and Tia Portal
High-end Programmable Logic Controller – Schneider PLC
PLC Program for Latching and unlatching Circuit
What is DCS? (Distributed Control System)

Keep Learning

PLC Project Examples for EcoStruxure Machine Expert

PLC Project Examples for EcoStruxure Machine Expert

PID Controller Graph - 3

PID Controllers Graphical Analysis

level of liquid inside a vessel

Concept of Redundancy in Control Systems

PLC Timer Programming Examples on Coffee Machine

PLC Timer Practice Exercise: Coffee Machine Programming

Siemens S7 300 and STEP 7 PLC program using SIMATIC Software

How to Run Multiple Motors with a Single VFD

How to Run Multiple Motors with a Single VFD?

Siemens PLC Course for Beginners

Siemens PLC Course for Beginners: Problems and Solutions

Motor Stop Interlock for Changing the Direction PLC Program

Motor Stop Interlock for Changing the Direction PLC Program

Learn More

Top 5 Advantages of Human-Machine Interface (HMI)

Top 5 Advantages of Human-Machine Interface (HMI)

Oxygen Analyzer Principle

Oxygen Analyzer Working Principle

Electrical Machines Questions and Answers

Induction Machine Circuit Quiz

Drum water level control

Closed Loop Control System : Boiler Water Level Control System

Importance of Unit Measurement

Importance of Unit Measurement

Transistor as an Amplifier in Common Emitter

Transistor as an Amplifier in Common Emitter

Manual Call Point Testing Procedure

Manual Call Point Testing Procedure

Dry Contact in PLC

What is a Dry Contact? – Basics of PLC Wiring

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?