Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: PID Controllers Graphical Analysis
Share
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Control Systems > PID Controllers Graphical Analysis

PID Controllers Graphical Analysis

Last updated: April 23, 2020 10:00 pm
Editorial Staff
Control Systems
No Comments
Share
4 Min Read
SHARE

A common exercise for students learning the function of PID controllers is to practice graphing a controller’s output with given input (PV and SP) conditions, either qualitatively or quantitatively.

This can be a frustrating experience for some students, as they struggle to accurately combine the effects of P, I, and/or D responses into a single output trend. Here, I will present a way to ease the pain.

PID Controllers

Suppose for example you were tasked with graphing the response of a PD (proportional + derivative) controller to the following PV and SP inputs over time.

You are told the controller has a gain of 1, a derivative time constant of 0.3 minutes, and is reverse-acting:

Proportional Derivative Controller Graph

My first recommendation is to qualitatively sketch the individual P and D responses. Simply draw two different trends, each one right above or below the given PV/SP trends, showing the shapes of each response over time.

You might even find it easier to do if you re-draw the original PV and SP trends on a piece of non-graph paper with the qualitative P and D trends also sketched on the same piece of non-graph paper.

The purpose of the qualitative sketches is to separate the task of determining shapes from the task of determining numerical values, in order to simplify the process.

After sketching the separate P and D trends, label each one of the “features” (changes either up or down) in these qualitative trends. This will allow you to more easily combine the effects into one output trend later:

PID Controller Graph

Now, you may qualitatively sketch an output trend combining each of these “features” into one graph.

Be sure to label each ramp or step originating with the separate P or D trends, so you know where each “feature” of the combined output graph originates from:

PD Controller Graph Analysis

Once the general shape of the output has been qualitatively determined, you may go back to the separate P and D trends to calculate numerical values for each of the labeled “features.”

Note that each of the PV ramps is 15% in height, over a time of 15 seconds (one-quarter of a minute). With a controller gain of 1, the proportional response to each of these ramps will also be a ramp that is 15% in height.

Taking our given derivative time constant of 0.3 minutes and multiplying that by the PV’s rate-of-change ( dPV/dt ) during each of its ramping periods (15% per one-quarter minute, or 60% per minute) yields a derivative response of 18% during each of the ramping periods. Thus, each derivative response “step” will be 18% in height.

Going back to the qualitative sketches of P and D actions, and to the combined (qualitative) output sketch, we may apply the calculated values of 15% for each proportional ramp and 18% for each derivative step to the labeled “features.”

We may also label the starting value of the output trend as given in the original problem (35%), to calculate actual output values at different points in time.

Calculating output values at specific points in the graph becomes as easy as cumulatively adding and subtracting the P and D “feature” values to the starting output value:

P+D Controller Graph

Now that we know the output values at all the critical points, we may quantitatively sketch the output trend on the original graph:

PID Controller Graph - 5

Credits : Tony R. Kuphaldt – Creative Commons Attribution 4.0 License

Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Instrumentation Engineer in Process Plant Project
What is a Transducer ?
Proportioning Feedforward action
Industrial Automation Pre-Engineering Design Documents – Project & Process
4-20 mA Transmitter Wiring Types : 2-Wire, 3-Wire, 4-Wire
Inductive Coupling Effects
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
Leave a Comment

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

Network Switch Requirement in SCADA and DCS Architecture
Runaway Processes
Heuristic PID Tuning Method
Basics of Motion Controllers
What are the Interlocks for Steam Turbine?
Ziegler-Nichols Open-Loop Method
Instrumentation Engineer Activities & Documents – Detail Design Phase
Features of PID Controller actions

Keep Learning

Serial Communication Error Checking Methods and Algorithms

Serial Communication Error Checking Methods and Algorithms

cascade temperature controller

How to Analyze a Cascade Control Loop?

Basics of FOUNDATION Fieldbus

Difference between Fieldbus, Profibus and HART Protocols

DCS Commissioning Steps

DCS Commissioning Steps

How to Implement Ratio Control in this System

How to Implement Ratio Control in this System?

Functional Design Specifications (FDS) for DCS and SIS Projects

Functional Design Specifications for DCS and SIS Projects – FDS Document

2 wire transmitter current loops

2-wire Transmitters Current Loops

Sources of Static Grounding and Methods to Control

Sources of Static Grounding and Methods to Control

Learn More

Use of Temperature Transmitters instead of Direct Wiring

Difference between Current Transformer and Potential Transformer

Difference between Current Transformer and Potential Transformer

Example of feedback principle

Example of Feedback System

Motor Maintenance

Motor Maintenance, Troubles, Regular Checks, Performance

oxygen Safety Analyzer

Oxygen Safety Analyzer

Infrared Hydrocarbon Gas Detector Calibration Procedure

Infrared Hydrocarbon Gas Detector Calibration Procedure

Stability in Frequency Domain

Time Domain Analysis

Types of Heat Exchangers

Types of Heat Exchangers

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?