Reading: Configuration of Control Valve in Studio 5000
Inst Tools > Blog > Control Systems > Configuration of Control Valve in Studio 5000
We are going to use a P-AOUT Analog output Add-on block for the configuration of a Control Valve in studio 5000.
Last updated: May 7, 2024 10:01 am
Control Systems
2 Comments
3 Min Read
We are going to use a P-AOUT Analog output Add-on block for the configuration of a Control Valve in studio 5000 and, we will see Analog Output parameters descriptions which we are going to configure.
Follow the below steps for the configuration of the control valve in Studio 5000.
Step 1:
Open Logix designer and open PlantPAx Project file in which all required add-on blocks of PlantPAx library are imported.
Step 2:
Right Click on Main Program and create a new routine as Analog Output.
Configuration of Analog Output devices in Studio 5000
And in the main program, calls the routine using JSR Instruction as shown below.
Studio 5000 JSR Instruction
Step 3:
Double click on the Analog Output routine and click on add-on and select P-AOUT instruction as shown below.
Step 4:
After adding the P_AOUT block we will bind a tag as CV_01 (Control valve 01) in the controller scope.
Configuration of Valve in Studio 5000
Step 5:
After that, click on the 3 dots tab and the parameter window will open where you can select and force the parameters you want.
Control Valve in PlantPAx Project
Inp-tieback: It indicates tieback CV i.e raw output of CV units.
Inp-IntlkOK: If it indicates=1 then all interlocks configured for particular valves are OK.
Inp-NBIntlkOK: It indicates those interlocks which cannot be bypassed are OK or not.
Inp-Ovrd: It indicates whether the input is overridden or not i.e if value=1 then particular input I override and if it is=0 then it is healthy.
Inp-OvrdCV: Target CV can be overridden.
Out CV: It indicates the simulated raw output value of the Control valve.
Sts-Err: It indicates that the control valve is in error. It means input failure.
Sts-Maint: It indicates the control valve is in maintenance mode.
Sts-Prog: It denotes Valve is in program mode.
Sts-Oper: It indicates Valve is in Operator mode.
Step 6:
Now we are going to enter the raw count and its engineering value accordingly which the actual valve will modulate. Enter 0 to 30840 in Raw min and Raw max as shown below and 0 to 100 will be your actual valve target value in%.
Raw Count in PlantPAx DCS
Step 7:
Your valve is configured you can test as shown below, download the logic/routine file in your available controller or in the emulator as I have done.
Studio 5000 valve programming
  • PlantPAx Control System
  • Import PlantPAx Library
  • DCS Technical Evaluation
  • Download PlantPAx Library
  • Compressor Start Permissive
Label the Electrical Circuit Schematic
What is Multi-touch Technology? – Industrial Automation
Control Systems Interview Questions & Answers
Purpose of Gateways, Bridges & Routers in Networking
Capacitive Coupling Effects
Flexible Input Output Modules
2 Comments
  • shubham says:
    September 18, 2022 at 12:48 pm
    how to show failed to open and failed to close in Control valve
  • Aloyce Mpemba says:
    September 7, 2024 at 2:18 pm
    Am from tanzania , I need plc software to install in my computer
Open Platform Communication (OPC)
Building Management System
What is Static Grounding?
PID Controller Response with different Input Signals
What are AI, AO, DI, and DO? – Definition, Examples, Purpose
How to Import PlantPAx Library?
Augmented Reality and Virtual Reality in Industrial Automation
Compare DCS, PLC, RTU
Difference between DCS, PLC, and RTU ?
Electrical Ground Loop
How to Solve Electrical Ground Loop Problems?
Distributed Control System Interview Questions
Emerson Smart Wireless gateway
Modbus Function Codes and Addresses
Zener Barrier Protection
Zener Diode Barrier Principle
PROFIBUS is also a Master Slave protocol
repairs of welding cast refractory lined box over the hot spots
Primary Reformer RFG main Hot Spots threaten Indefinite Outage
Electrical Cables Interview Questions & Answers
Remote Diaphragm Seal Transmitter for Vacuum Application
How Could FB and FC Make Me Professional PLC Programmer
How Could FB and FC Make Me Professional PLC Programmer?
Linear Variable Displacement Transducer (LVDT)
What is LVDT ?
Fence grounding specifications
All About Electric Fence Gates
Analog Electronics Objective Questions – Set 11
PLC Star-Delta starter with interlock
Schneider PLC Example Program for Star-Delta System