Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: Compressor Shutdown Job – Instrumentation Engineer Duties
Share
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Common > Compressor Shutdown Job – Instrumentation Engineer Duties

Compressor Shutdown Job – Instrumentation Engineer Duties

In this article, we will learn the instrumentation engineer duties during a compressor shutdown job of a plant.

Last updated: October 15, 2022 11:47 am
Editorial Staff
Common
No Comments
Share
7 Min Read
SHARE

In this article, we will learn the instrumentation engineer duties during a compressor shutdown job of a plant.

Contents
Compressor Shutdown JobControl Valves and their AccessoriesDifferential Pressure type Flow MetersPressure TransmittersTemperature Transmitters and RTD/Thermocouple SensorsLevel TransmitterVibration ProbesPressure GaugesTemperature GaugesPressure SwitchesFlow SwitchesLevel SwitchesA Controller like PLC and its cards

Before proceeding further, let us see all the instruments used for the safety of the centrifugal compressor or the controlling/operation of the centrifugal-type compressor.

Compressor Shutdown Job

Compressor Shutdown Jobs

The following instruments are installed in a centrifugal compressor:

  1. Control valves and their accessories
  2. Differential Pressure type flow meters
  3. Pressure transmitters
  4. Temperature transmitters and RTD/thermocouple
  5. Level Transmitter
  6. Vibration probes
  7. Pressure gauges
  8. Temperature gauges
  9. Pressure switches
  10. Flow switches
  11. Level switches
  12. Controller: PLC and its cards

Now let us discuss what jobs can be done during the shutdown on all the above-mentioned instruments

Control Valves and their Accessories

Two types of control valves are used in a centrifugal air compressor. One is Inlet Guide Vane (IGV) and the other is a Blow-Off Valve or Anti-Surge Valve.

So, we should do the stroke checking of both control valves. If any issue is found in the control valve during the stroke-checking activity, then we can go for calibration of the control valves.

Here one important thing to note is that the Blow-Off Valve or Anti-Surge Valve is an equal percentage type of valve characteristics in many compressors.

So, refer to any standard document before doing the job on Blow-Off Valve or Anti-Surge Valve. Check the physical condition of the Air Filter Regulator. Replace if necessary.

Replace the pressure gauges if needed. If any Solenoid Valve is present on the control valve, check the solenoid valve as per the standard procedure.

If any other valve accessory is present, then check the same. If a volume tank is present, then check the PSV of the volume tank.

The calibration of the PSV is very important. Make sure that the PSV is calibrated.

Differential Pressure type Flow Meters

Differential pressure type flow meters are installed in the compressor to measure the flow of the gas as well as one of the most important parameters i.e. flow of the cooling water. Hence, during every opportunity, the differential pressure type flow meters should be calibrated.

Also, whenever cooling water is isolated and again normalized there will be air trapped in the DP-type flow meter’s tubing. Hence, after normalization of the cooling water circuit, the DP-type flow meter of the cooling water should be flushed.

The flow of the gas is also used for calculating the Surge value. This Surge value is used in Surge Control System for the protection of the compressor. Inspect the orifice plate if any opportunity is available.

Pressure Transmitters

Pressure transmitters are used to know the pressure of suction, individual stage pressure as well as discharge pressure.

The values of the pressure are also used for calculating the surge value. Check the response of the pressure transmitters and do calibration if needed.

Temperature Transmitters and RTD/Thermocouple Sensors

Temperature transmitters are installed for suction gas, intercooler inlet, intercooler outlet, and discharge gas temperature measurement. The values of suction gas temperature and/or discharge gas temperature are taken for calculation of the Surge value.

The response of the RTD/thermocouple as well as the temperature transmitter should be checked. One important thing to note here is to carry out the inspection as well as the hydro test of the thermowell used for the RTD/thermocouple.

In most cases, thermowells are neglected.

Level Transmitter

Level transmitters are used for measuring the level of lube oil in the lube oil reservoir.

Generally, differential pressure level transmitters are used for the lube oil reservoir level measurement. Calibration of the level transmitter should be done after proper isolation of the lube oil system.

Vibration Probes

Characteristic checking, resistance checking, and response checking of the vibration monitoring system should be done in every shutdown.

Pressure Gauges

Pressure gauges are used for viewing the pressure of the lines on which they are installed.

Calibration of the pressure gauges is necessary because, during emergency conditions like a blackout, pressure gauges can be used to know the pressure in the system or the line on which they are installed.

Temperature Gauges

Temperature gauges also function like pressure gauges. Hence calibration of the temperature gauge is also necessary.

Pressure Switches

Pressure switches are installed in seal gas pressure or some other important pressure parameter on which the compressor should immediately trip.

Ensure that the contact used for the pressure switch remains closed when the pressure is healthy.

Flow Switches

Flow switches are installed in the cooling water flow line. Cooling water is one of the most important factors while the compressor is running. Because during the compression of the gas, the temperature of the gas increases.

Due to increased temperature, the volume of the gas also increases, and hence more energy is needed to compress the gas.

Hence intercoolers are given which have a cooling water flow to reduce the temperature of the gas. When the flow is healthy, the contact should be closed.

Level Switches

Level switches are required to monitor the amount of water in case of an air compressor in the intercooler.

If there is a high level of condensation in the intercooler then the compressor should trip. Here also, when the level switch is healthy, the contact should be closed.

A Controller like PLC and its cards

All connection tightening, panel cleaning jobs, and power supply checking in the PLC panel should be done during the shutdown of the compressor.

Also, Cause & Effect checking and Interlock checking should be done during the shutdown of a plant.

Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

What is Magnetic Tape Recorder ?
Best Online Courses to Learn Electrical Engineering
Measurement of POL, pH, and BRIX in the Sugar Industry
9 Life-Saving Rules for Oil and Gas Industry
Ultrasonic Testing (UT) : Principle, Advantages, Disadvantages
How is Electricity Generated From Solar Energy?
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
Leave a Comment

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

Applications of Robots in Various Fields
Why do Teenagers want to be Entrepreneurs?
Introduction to MEMS (Microelectromechanical Systems)
Everything You Need to Know About Stainless Steel CNC Machined Parts
Difference between DSP and DAC – Digital Electronics
Industrial Automation Sales and Marketing Tools
4-20mA Transmitter NAMUR Signal Levels
Instrumentation documents

Keep Learning

Saybolt Viscometer

Saybolt Viscometer

Streams After Electrical Engineering Graduation

Streams After Electrical Engineering Graduation

YouTube Channels About Tech and Engineering

Awesome YouTube Channels About Tech and Engineering

The Top Services a Great B2B Agency Offers

The Top Services a Great B2B Agency Offers

Power Tool Maintenance

Power Tool Maintenance – When And How To Replace Carbon Brushes

Types of Sensors Used in Automobiles

Types of Sensors Used in Automobiles

Moving Coil Type Velocity Transducer

Moving Coil Type Velocity Transducer

Basic Pneumatic System

Introduction to Fluid Power and Pneumatics

Learn More

PLC Program for an Alternate output circuit

PLC Program for Alternate Output Circuit with Latched Function

Electro Chemical Transducers Objective Questions

Electro Chemical Transducers Objective Questions

inductance transducer

Inductance Type Pressure Transducers Principle

Measure AC Voltage using Multimeter

How to Measure AC Voltage using Multimeter

Ground Plate

Grounding of Telecommunication Systems

Spectrometers Questions and Answers

Total Reflection Spectrometer Questions & Answers

Home Automation Project Ideas

Best Home Automation Project Ideas for Engineering Students

Transmission Lines Protection Questions Answers

Transmission Lines Protection Questions Answers

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?