Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: Solenoid Valve Problems and Solutions
Share
Notification Show More
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Control Valves > Solenoid Valve Problems and Solutions

Solenoid Valve Problems and Solutions

Today in this article we will learn various solenoid valve problems and their solutions with troubleshooting steps.

Last updated: July 21, 2022 1:42 pm
Editorial Staff
Control Valves Solenoid Valve
1 Comment
Share
5 Min Read
SHARE

Today in this article we will learn various solenoid valve problems and their solutions with troubleshooting steps.

A solenoid is one of the main components of a valve. The failure rate of the solenoid valve is also more as compared to other valve accessories.

This article will help you do troubleshoot in case the solenoid valve malfunctions or creates a problem.

Solenoid Valve Problems and Solutions

Solenoid Valve Problems and Solutions

Follow the below-mentioned procedure to troubleshoot the solenoid valve in case the valve does not open or close as per the requirement.

  1. Check whether the air supply to the solenoid valve is established or not.
  2. The air supply pressure from the Air Filter Regulator (AFR) to the solenoid valve should be according to the air pressure required by the valve mentioned in the datasheet.
  3. Check the AFR bowl (bottom), if there is moisture content or not. If moisture is there, then flush the AFR as well as the whole downstream system. Take clearance from the Plant Operation team before flushing the system. This action may operate the valve.

For doing the steps mentioned below, take clearance from Plant Operation for operating the valve.

  • In the solenoid valve, check for the vent port healthiness. Many times, the vent port is getting choked due to bugs or if the bug arrester is not installed or due to dirt. Clean the vent port and bug arrester if found choked.
  • To confirm whether the solenoid valve’s vent port is clean or not, operate the solenoid valve manually if the manual latching system is present or give a command through the control system to operate the valve. During the command, valve will do open and close, the air from the vent port should come out with good pressure and good flow (the aim is to know that the vent port is clear) because the actuator’s one compartment will empty out its air.
  • Now remove the tubing from the actuator side and during command changeover (ON/OFF) from the system side, a clicking sound from the solenoid valve should come. That means the coil is energizing. Also, the air path should change i.e. air should come out from another port or if only one outlet port is there then it should reverse the condition i.e. air will stop if it was coming and vice versa.
  • If a clicking sound is coming during command changeover (ON/OFF), the air path is not changing then the solenoid valve’s body is having the issue. Open the body as per instructions from the vendor manual and do servicing or replace the piece.
  • Check for continuous venting from the solenoid valve’s vent port. If continuous venting of air is there, then either the solenoid valve or the actuator is passing. Remove the tubing and check the solenoid and actuator one by one for passing issues.
  • If the clicking sound is not coming from the solenoid valve while giving command from the system, then first check the voltage. If there is no change in voltage during command changeover (ON/OFF) from the system, then check the connections in the junction box.
  • If connections in the junction box are found ok, then check connections in marshalling cabinet. Also, check the fuse healthiness in marshalling cabinet. Replace the fuse with the fuse of the same rating if the fuse is blown. Then take a trial of the solenoid valve.
  • If still voltage is not received in the field, then check whether the DO i.e. digital output is turning ON or OFF when the command is given from the engineering system.
  • If everything is found ok, then check the cable resistance from the marshalling cabinet to the field. If found open or with high resistance, then change the cable pair with a spare one.

(While giving command (ON/OFF) from system, the magnetic field will generate in solenoid valve’s coil in one condition. We can check the magnetic field using an iron metallic piece)

  • If voltage is present but a clicking sound is not coming, then disconnect the cables and check the coil resistance.
  • Coil resistance should be as per vendor manual specifications (it should not be high resistance in megaohm and not in very low single digit ohm). If the coil is found not ok as per its resistance, then replace the coil.
Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Control Valve Questions and Answers
How to Select Control Valve Failure Mode
How Diaphragm Valves Work ?
Valve Interlock
Root Cause Analysis for FRP Line Damaged due to On-Off Valve
Working Principle of Self Operated Valves
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
1 Comment
  • RAIMUNDO PEREIRA DOS SANTOS says:
    June 11, 2023 at 6:07 pm

    Excellent content. Thank you very much.

    Reply

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

Why we Measure Control Valve flow coefficient (Cv)?
What is a Disc Valve ?
What is Split Range Control Loop ?
Control Valve Stroke Test Procedure
Difference between Rotary Shaft Valves and Sliding Stem Control Valves
SIS Final Control Elements
Solenoid Valve Failure in Plant Start-Up: Identifying the Root Cause
Classification of Gate Valves

Keep Learning

Air Release Valve

What is an Air Valve? Purpose, Types, Advantages, Disadvantages

Control Valves Classification

Classification of Control Valves

Thermostatic valves Principle

Thermostatic Valves Working Principle

Control Valve Relation between Cv and Kv

Control Valve Relation between Cv and Kv

Level Control Valve with Horizontal Float

Level Control Valve with Horizontal Float

Plant Shutdown Analysis: Valve Closed and SOV Coil Failure

Plant Shutdown Analysis: Valve Closed and SOV Coil Failure

PRV

Direct-actuated Safety and Relief Valves

Classification of valves

Introduction to Types of Valves

Learn More

Siemens PLC

Will PLCs become obsolete?

Intelligent MCC

What is Smart or Intelligent MCC?

What is a Network

What is a Network ?

Pressure Gauges with Diaphragm Sensor Principle

Pressure Gauges with Diaphragm Sensor Principle

Pressure Gauge Functional Testing

Pressure Gauge Functional Testing

different PLC brands of Distributed IO

What is Distributed IO? – Decentralized Peripherals in PLC

Voltage Control Methods at Distribution System

Factors affect Voltage Level Selection in Service System

PLC Programming for Train Detection and Gate Operation

PLC Programming for Train Detection and Gate Operation

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?