Electrical engineering root cause analysis (RCA) related to burst transformer and related problem solved.
| Category: | Electrical |
| Equipment Type: | Bus ducts, Switchgear, Transformers, |
Burst Transformer Problem
An 11000/400V and an 11/3.3KV transformer burst – a pre-SC treatment & breakers reliability enhancement era problem.
Why burst breakers?
System insulation resistance (IR) loss common in the pre-SC treatment era caused phase-phase short several rated fault currents.
The transformer secondary breaker did not trip within 30 mS (milli-second) as expected though the protections relay commanded in time. The too-long current flow burst the breaker and the transformer.
Such problems vanished after the Silicone Compound (SC) application and Switchgear mechanical improvements described above.