Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: Root Cause Analysis for FRP Line Damaged due to On-Off Valve
Share
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Root Cause Analysis (RCA) > Root Cause Analysis for FRP Line Damaged due to On-Off Valve

Root Cause Analysis for FRP Line Damaged due to On-Off Valve

Root Cause Analysis for FRP line damaged due to On-Off Valve operation due to high instrument air pressure to the actuator.

Last updated: October 3, 2022 4:35 pm
Editorial Staff
Root Cause Analysis (RCA) Control Valves
1 Comment
Share
4 Min Read
SHARE

An FRP line was continuously getting damaged (cracks were observed). This was occurring very frequently (once per 15 to 20 days).

Contents
On-Off Valve ProblemOn-Off Valve Root Cause AnalysisObservations

On-Off Valve Problem

An FRP line was installed in one plant for supplying water to a mixing tank. The line size was 10 inches. An On-Off valve, an isolation valve, a pressure transmitter, and a flow transmitter were installed in the same line. Almost after every 15 to 20 days, the FRP line got damaged near the On-Off valve.

So, what can be the probable reason for frequent damage to the FRP line?

On Off Valve Root Cause Analysis

On-Off Valve Root Cause Analysis

Probable Problem 1: FRP line not having proper supports 

FRP line was installed as per standard and sufficient support was also provided.

Probable Problem 2: FRP line might be thin as compared to the standard / required thickness

FRP thickness verified with standard documents. FRP line thickness was perfect. 

Probable Problem 3: High vibrations in FRP line

No vibrations were observed in the FRP line while the water was passing through the line.

Probable Problem 4: High pressure of water flowing through the FRP line.

The pressure of the water is confirmed through the pressure transmitter. The pressure was below maximum operating pressure.

The standard operating pressure was 6 kg/cm2 while the maximum pressure observed during the feed inlet to the tank was 2.8 kg/cm2 due to the unavailability of one out of three feed pumps.

Probable Problem 5: Design issue in the line size and On-Off valve sizing

Design side all parameters reverified with the vendor. All sizing found ok.

Observations

Observations after frequent visits to the FRP line during different timings:

During normal operations, the FRP line was very steady like all other lines in the plant. But, whenever the On-Off valve was given close command, the valve got operated by creating a heavy sound.

So, on continuous observation of the valve, it was found that the valve is the main root cause of the FRP pipe getting damaged.

What went wrong?

On further checking by the Instrumentation team, the Instrument air pressure to the On-Off valve was found 6.5 kg/cm2.

(Some basic information:  The on-off valve is having a butterfly-type body. The on-Off valve size is 8 inches.

Also, the fail action of the valve is fail-open.  So, the air is required to close the valve. As per the datasheet, Instrument Air pressure to the actuator should be a maximum of 4.5 kg/cm2)

The instrumentation team checked the operation of the valve with 6.5 kg/cm2 air pressure and found that the valve movement during the closing time was very fast. This also caused very high vibration and jerks during closing.

So, after a detailed study, it was concluded that there are 2 main reasons for this FRP line getting damaged

  1. On-Off valve operation during close command was damaging the line which is due to high Instrument Air Pressure to the actuator.
  2. Already the pressure of the water in the line was low i.e. 2.8 kg/cm2 as compared to the standard 6 kg/cm2 pressure. This was due to the unavailability of a feed pump. Hence this condition also amplified the damage caused by the On-Off valve movement.

Immediately, the Instrument Air pressure to the On-Off valve was normalized to 4.5 kg/cm2. Also, this point was included in LLF to check the Instrument Air pressure of all valves.

Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Cooling Water Circulating Pump Low throughput Resolved
SIS Final Control Elements
Repeat Failures of Letdown Valves
Control Valve Interview Questions and Answers
Air Cylinder Consumption Calculation for Control Valves
Globe Valve Seat and Disk
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
1 Comment
  • power systems says:
    October 7, 2022 at 10:09 am

    very good and useful infomation

    Reply

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

What is Instrument Air Manifold ?
Choked Flow of Control Valves
Fire burnt Ammonia Converter Thermocouples Problem
What is Piston Check Valve ?
Poor Power Factor Boosted – Industrial Electrical Problems
Too often done riskily repaired Roof Hot Spots eliminated forever
Self-Actuated Valves, Pneumatic & Hydraulic Actuators
[RCA] Pump Low throughput Eliminated

Keep Learning

Valve Technician Interview Questions

Valve Technician Interview Questions

Rupture Disc

Working of Rupture Disk

Jacket Added Seawater Pipe Spool

Seawater Pipeline Spools from day-1 leaks threaten Plant Shutdown

ball Valve Animation

Basics of Ball Valves

What is a Servo Valve?

What is a Servo Valve? – Principle and Advantages

Refrigeration Compressor Turbine Not-tripping when needed Trip

Refrigeration Compressor Turbine Not-tripping when needed Trip

Single Bearing Motor Stator Winding

Critical High KiloWatt Motor Winding Burnout Threats

Pressure Correction Pneumatic Instrumentation

Pressure Correction Pneumatic Instrumentation

Learn More

Stability in Frequency Domain

Feedback Compensation

Omron PLC Mixing System

Mixing Program with Timers and Counters in Omron PLC

Vibrating Fork Level Switch Working Animation

Vibrating Fork Level Switch Working Animation

differential-pressure-transmitter-calibration-procedure

Differential Pressure Transmitter Calibration Procedure

Difference Between Adhesion and Cohesion

Difference Between Adhesion and Cohesion

Identify the Pressure Gauge Error

Identify the Pressure Gauge Error

Types of Electrical Loads

Types of Electrical Loads

capacitor-filter

Capacitor Filter Working Principle

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?