Reading: PLC Program for Controlling Sequence of Conveyors with Interlock
Inst Tools > Blog > PLC Tutorials > PLC Program for Controlling Sequence of Conveyors with Interlock
PLC Conveyor Interlock. : A feeder drops material on the conveyor which sends material for further process through one more conveyor.
Last updated: November 3, 2023 2:30 pm
5 Comments
3 Min Read
 This is a PLC Program for controlling the sequence of conveyors and interlocking them.
PLC Conveyor InterlockProblem DiagramProblem SolutionList of Inputs/OutputsPLC Controlling Sequence of Conveyors with InterlockProgram Explained
Problem Description
A feeder drops material on the conveyor which sends material for further process through one more conveyor. The conveyor must start automatically when the material is dropped.
Implement a PLC program for this application using ladder diagram language.
Problem Diagram
Problem Solution
In this system, we will consider S7-300 PLC and TIA portal software for programming.
The feeder has a motor mounted to feed material on conveyor belts.
Load cells are installed at the bottom of conveyor belts to detect if material is present on the conveyor belt.
When material falls on the conveyor belt 1, motor 1 should start, and when material is present on the conveyor belt 2, motor 2 remains ON.
Switches can also be used sometimes to detect material’s presence. But for more reliable operation, Load cells can be used as shown in the diagram above.
Inputs List
  • START PB :- I0.0
  • STOP PB :- I0.1
  • Load cell 1 :- I0.2
  • Load cell 2 :- I0.3
Outputs List
  • Cycle ON :- Q0.0
  • Conveyor 1 motor :- Q0.1
  • Conveyor 2 motor :- Q0.2
  • Feeder motor :- Q0.3
PLC Conveyor belt
PLC sequence of conveyors
Program Explained
Network 1:
Cycle ON (Q0.0) lamp will start when START PB (I0.0) will be pressed and cycle can be stopped by pressing STOP PB (I0.1).
Network 2:
Feeder motor (Q0.3) will be ON when cycle is ON.
Network 3:
If cycle is ON and load cell 1 feedback is detected, conveyor motor 1(Q0.1) will be ON.
Network 4:
If cycle is ON and Conveyor 1 (Q0.1) or load cell 2 feedback (I0.3) is detected, conveyor 2 motor (Q0.2) will be ON.
Note :- Above application may be different from actual application. This example is only for explanation purpose only. We can implement this logic in other PLC also. This is the simple concept of conveyor logic and interlocking them, we can use this concept in other examples also.
All parameters considered in example are for explanation purpose only, parameters may be different in actual applications. Also all interlocks are not considered in the application.
Author: Bhavesh
  • Tank Heating Control using Heater
  • PLC Analog Input Sampling
  • Automatic Empty Bottle detection using PLC
  • PLC Two Way Switch Logic
  • Counters using PLC
Tia Portal – Optimized and Standard Data Block Access
Basic PLC Exercise on Heater and Cooler for Students
Automatic Highway Lights Program using RTC in Omron PLC
#18 PLC Best Practices – Store PLC Hard Stop Events from Faults
Programmable Logic Controller Questions and Answers
5 Comments
  • Archimedes says:
    November 1, 2018 at 5:18 am
    Hello sir! Can you restore the download pdf option that you had before? It was great!
    Thank you
    • S Bharadwaj Reddy says:
      November 2, 2018 at 9:08 am
      Hi, We have an issue with the pdf download. soon we will restore the option.
  • Archimedes says:
    November 2, 2018 at 9:21 pm
    Great news! Thank you sir for this information and keep on your effort to this very helpfull site!
  • Laurentiu says:
    November 15, 2018 at 1:27 pm
    Hello, I see you have not yet solved the problem with downloading pdf files, can it by the end of the year? I’m very much in my personal training. I really like and am fan of your site 🙂
      November 15, 2018 at 2:26 pm
      Hopefully, We are working on it.
Siemens PLC programming: BCD, Integer, Double Integer, Real
Tia Portal – OB10 Time of Day Interrupt Organization Block
XG5000 PLC Programming for Automatic Exhaust Fan
How to implement SR Flip Flop using PLC Ladder Logic
Why is 24 Volts Commonly used in PLC Systems?
Programmable Logic Controller (PLC) Scan Time – Types, Theory
PLC Program for Temperature Control using Thermostat
Factory IO PLC Course
Factory I/O PLC Automation Training Course (Free)
Fixed PLC
Open Loop and Closed Loop System Questions
How to choose between PLC and DCS Systems
How to Troubleshoot a PLC System
How to Troubleshoot a PLC System?
How-to do Security of SCADA Systems
How-to do Security of SCADA Systems?
Allen Bradley PLC communication is established
Procedure for Connecting Allen Bradley PLC and PC – RS Logix 500
Ladder Diagram Example using Memory Bits and Set Coils
Servo Level Transmitter Principle
Enterprise Resource Planning in Industrial Automation
What is ERP in Industrial Automation? – Enterprise Resource Planning
Fast Adder & Serial Adder Multiple Choice Questions
AC Voltage Controllers Quiz
Power Systems MCQ Series 10
Mechanical Strainers
Strainers
electrical-drives-questions-answers
Electrical Drives Questions & Answers