Electrical engineering root cause analysis (RCA) related to Frequent Feeder-A Lightning Arrester (LA) Bursts.
Lightning Arrester (LA) Bursts ProblemRoot Cause AnalysisAuthor’s Comments ProvedProblem Solved
Article Type:Root Cause Analysis (RCA)
Category:Electrical
Equipment Type:Bus ducts, Switchgear, Transformers,
Author:S. Raghava Chari
110 KV exclusive Feeders-A & B running side-by-side feed power to the plant from the grid-connected 6-Km away thermal power station.
Feeder B’s Lightning Arrester (LA) never burst, but Feeder A’s several times a year especially on slightly windy days.
Root Cause Analysis
The author instrument engineer then commented in common problems solving meeting, “Feeder B Lightning Arrester has never burst; hence, selected Lightning arresters are Ok for our application.
Perhaps, Feeder-A conductors accidentally contact the Electricity Board’s 220 KV transmission conductors. Hence, I suggest a team inspecting the Feeder-A along its entire route”.
Surprisingly, the electrical graduate and long electrical experienced Maintenance Manager and other electrical engineers ignored and even ridiculed it saying, “Rigorous electrical standards on HT power lines routing and maintaining distance between bare conductors prevent such accidents.”
Based on fancy theories they installed very expensively higher voltage Lightning Arrester (LA), and a fast-acting carrier trip system. But Feeder-A, LA bursts persisted.
The author on becoming maintenance manager sent a team of two plant electrical engineers, two electricity board engineers to inspect Feeder-A conductors along its 8-km route.
He sent a snake charmer also with the team so that the electrical engineers inspect the conductors carefully and the snake charmer guards them against the likely snakes along the route.
The team did find excessively sagged 220-kV line conductors, which could easily contact Feeder‑A conductors, even at slight winds.
Problem Solved
The author prevailed upon the Managing Director to permit the plant doing the necessary repairs though not its responsibility according to the thermal station engineer’s requirements.
Thus free from red tape, the plant contractor modified the 220 KV lines supports as necessary in the record 3 days.
Nuisance Feeder-A Lightning Arrester bursts vanished forever.
Author: S. Raghava Chari
  • Insulation Resistance (IR) Problems
  • Burst Transformers & Input Breakers
  • Failing Weigh Feeders and Drives
  • Transformers Coolers Problems
  • Motor Rampant Winding Burnout
Turbine Flow Meter (TFM) Field Calibration Uncommon Request
Heat Exchanger Root Cause Analysis (RCA)
Thermocouple Wires and Extension Lead Issues
Flanged Rotameter Caused Pipe Weld Cracks and Gives Wrong Readings
Replace Failed Motors Quickly and Easily
Totally Enclosed Fan Cooled (TEFC) Motors Rampant Winding Burnouts
Primary Reformer – Each Turnaround done expensive Tubes Repairs
High-pressure Service Level Transmitters Misunderstood Zero Drifts
Hunting of Control Valves
Cooling Tower Fans Frequently Failing
Pump 3-monthly Seal Leaks threaten entire Plant Shut down Indefinitely
NH3 Storage Tanks Ammonia Gas Venting Issue – Root Cause Analysis
Piston No-Diaphragm Seal Instrument
Seal Pressure Instruments Root Cause Analysis
Valve Actuator Passing
Lessons Learned from Actuator Passing Incidents
Amine Pump Trip - Root Cause Analysis
Amine Pump Trip – Root Cause Analysis
Mechanical Engineering Plant Problems Solved
Mechanical Engineering Plant Problems Solved – Root Cause Analysis
repairs of welding cast refractory lined box over the hot spots
Primary Reformer RFG main Hot Spots threaten Indefinite Outage
Control Valve Plug Stem and Gland Leaks
Repeat Control Valve Plug Stem and Gland Leaks
Target Flow Transmitter Problem
Unreliable Ammonia Flow Transmitter Reading and Problems
Valve Positioner Torn apart
Pipeline Shakes Torn apart Valve Positioners
Allen-Bradley MicroLogix controller
Programmable Logic Controller (PLC) Questions and Answers – 15
Diagonalization
Wedge Flow Meter
Wedge Flow Meter Principle
Modbus
Modbus : History, Structure, Modes, Addressing, Functions
Internet of Things (IOT)
History of Internet of Things (IOT)
Types of Limit Switches
Types of Limit Switches – Principle, Advantages, Disadvantages
How to use Fire Fighting Hydrant
Fire and Safety
Advantages of Redundant System
Redundant Automation Systems – Need and Advantages