Reading: System Cabinet Health Checks – PLC and DCS Industrial Automation
Inst Tools > Blog > Control Systems > System Cabinet Health Checks – PLC and DCS Industrial Automation
In this article, we discussed the steps to be followed during the health checks of the PLC and DCS system cabinet.
Last updated: August 24, 2021 11:47 pm
Control Systems PLC Tutorials
2 Comments
Here DCS stands for Distributed Control System. and PLC stands for Programmable Logic Controllers.
System Cabinet
DCS System Cabinet
Step 1:
Collect the corresponding Work permit.
Step 2:
Note down the system cabinet panel tag/reference name which will be available on top of each cabinet door (Example: 10-3-01).
Step 3:
Check the working condition of the door locking system by operating twice.
Step 4:
Check the LED status in the CPU card.
Yokogawa DCS CPU
In both CPU cards, HRDY & RDY – LED lamp should glow and in one of the CPU cards CTRL LED should glow.
CTRL LED indicates the controller that is in active state. The HRDY & RDY LED shows the healthiness of the CPU card.
Quiz: Test on DCS
Step 5:
Check the BUS communication status LED in the CPU card.
SEND, RECEIVE of BUS1 and BUS2 LED should blink continuously.
Step 6:
Check for any diagnostic alarms on Processor, redundancy module, IO modules, communication cards, PSU cards.
Step 7:
Check the 5V and 24V DC supply voltages in the power supply card.
Step 8:
Check once all the cooling fans running condition.
Fans are located at the top of the panel and the fan switch will be at the rear side of each panel.
Step 9:
Check the Fan Failure and Temperature Detection Unit (FFTDU) alarm status.
The F-ok, T-ok LED should glow.
If anything is faulty then the fault LED will glow which will be located on the right side of the panel front.
Step 10:
Check the tube light condition by activating the door limit switch which will be on the top corner of each panel.
Step 11:
Check for any loose connections in the panel.
Step 12:
Check the Grounding of the control panel.
Step 13:
Check all the empty slots are properly covered by dummy plates.
(No slots should be open)
Step 14:
Measure the incoming UPS supply voltage.
Step 15:
Measure the utility supply voltage at MCB which will be available on the rear side of the panel.
PLC System Cabinet
Step 16:
Check the sealing of spare cable entry slots at bottom of the panel.
Step 17:
Clean all the filters of the panel
Step 18:
Check and ensure cables are properly dressed and cable ducts are covered
Note: All panels must be closed after preventive maintenance activity has been done.
Interest to add any further checks? Share with us through below comments section.
  • DCS Troubleshooting
  • Commissioning of DCS System
  • DCS Control System Spares
  • Yokogawa DCS Architecture
  • DCS System Layout
PLC 1 Push Button to Turn ON or OFF 1 Output
Memory Structure of Siemens PLC
Configuration of Profibus Network in Siemens PLC
ON and OFF a Group of Outputs by One Push button PLC Logic
Complete PLC Project: Traffic Light Auto and Manual Automation
2 Comments
  • Virendra Mishra says:
    January 4, 2023 at 12:04 pm
    I am Heading Instrumentation / Automation department in Rallis India Limited ( A TATA Enterprise ) which is having Manufacturing units at 5 locations. I am Interested in New letter.
  • Yohanna Thomas says:
    September 12, 2024 at 12:04 pm
    hello
OB1 – Main Cyclic Organization Block in TIA Portal
Commissioning Documents for Instrumentation Engineers
Identify Faults in PID Control Loop
How to Implement Ratio Control in this System?
Steady-State Process Gain
How to do Force in GE PLC Proficy Machine Edition?
Modbus Communication between Delta PLC with VFD
Voting System in PLC
Voting Concept in Package Safety System
Retro-Reflective Sensor
Pumping System in Industrial Automation
Basic Pumping System Application Used in Industrial Automation
SinkingOutput
Difference Between the Sinking and Sourcing?
Centralized vs Decentralized Automation Systems
Things to Take Care of When Designing SCADA System
Wonderware Recipe Manager Plus
What is Recipe Management in SCADA?
Automatic Car Door Simulation
Automatic Door Operation PLC Programming and Simulation
Process Alarms Types
Process Switches and Alarms
Magnetostrictive instruments
Magnetostrictive Level Measurement
Flow Measurement Questions and Answers
Demister Pads Problem
Problems with Demister Pads – Root Cause Analysis (RCA)
Types of NMR Spectrometers Questions & Answers
Transistor Amplifier Working Principle
PLC Program for Automatic Heating and Mixing of Products
Heating and Mixing of Products using PLC Example Tutorial
Industrial Automation and Control Systems (IACS)