Reading: Control Modes of Air Handling Unit (AHU) – HVAC Basics
Share
Notification Show More
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Control Systems > Control Modes of Air Handling Unit (AHU) – HVAC Basics

Control Modes of Air Handling Unit (AHU) – HVAC Basics

In this article, we will learn the different control modes of air handling unit (AHU). Understand the control strategies used in HVAC.

Last updated: May 23, 2023 4:24 pm
Viral Nagda
Control Systems
No Comments
Share
6 Min Read
SHARE

AHU stands for an air handling unit. AHU is a very important application in handling air flow and maintaining temperature, humidity, and differential pressure. This is because proper air is a must for human survival.

Contents
Control Modes of Air Handling UnitNight Cycle ModeOccupied Operation ModeExtended Operation ModeAHU Off Delay ModeFire ModeConstant DAT (discharge air temperature) ControlSequential Control of Output SignalsCompulsory Damper Monitoring Mode

AHU is thus controlled mostly nowadays by industrial automation. Because automation is involved, various techniques have been adapted in a single AHU to run it efficiently.

Control Modes of Air Handling Unit

Control Modes of Air Handling Unit (AHU) - HVAC Basics

A single strategy for running AHU cannot prove worthwhile, because you can overall control the efficiency of HVAC by various control modes. So, there are many control strategies used in an AHU, depending upon the application.

Different types of controls can reduce power consumption, improve the comfort of occupants by means of scheduled operation and also handle alarms more properly.

In this article, we will learn the general types of control modes used in an air handling unit (AHU).

Night Cycle Mode

AHU cools down the temperature during daytime or simply, when occupants are present in a room during working hours. But, during night time, when fewer or no occupants are present, then there is no use to run the Air Handling Unit at full efficiency.

For this, a mode called night mode is programmed in PLC. When night mode is enabled either by a manual switch or automatically (PLC will read current time), then the blower will run at a lesser speed; and the temperature set-point will be increased.

This will make the cooling elements like compressors and chillers run at a lesser frequency. Ultimately, your energy consumption will reduce due to this strategy.

Occupied Operation Mode

 This is the normal running mode of AHU. As discussed earlier, this mode is used during normal working hours with a proper number of occupants.

The blower is run at a nominal speed and the cooling elements run at a normal temperature to maintain temperature and humidity.

Extended Operation Mode

When the number of occupants rises, with the additional requirement of cooling, then this mode is activated either manually or automatically.

Temperature set-points will reduce further and blowers will run at faster speeds. This will make the AHU run more with more power consumption.

AHU Off Delay Mode

Sometimes it is required to turn off the AHU after a delay. This requirement mostly comes in the case of the usage of heaters or humidifiers. If you turn off the AHU along with them, then there are chances of the heater still being hot or moist air still present due to lack of movement of air.

So, in this mode, the heaters or humidifiers are turned off immediately, but the AHU is kept running for some time. This cools down heating coils or removes moist air.

Fire Mode

When the fire is sensed in the system, then the AHU will turn off immediately with all the respective heating and cooling elements.

This enables fire mode in the PLC and during this, fire dampers will remain open fully. When the system goes back to the normal state, then fire dampers will get closed once again.

Constant DAT (discharge air temperature) Control

In constant mode, the discharge air temperature is tried to be kept at a constant value by use of PID. PID will operate on a single set-point and this PID will be controlled by the discharge air temperature.  

Sequential Control of Output Signals

Suppose there are multiple actuators connected in series. Then, this mode is used to control these outputs. One actuator is controlled until the end of its available range before the next actuator is used.

The PID control is divided over multiple actuators. The user can define the order and percentage of the PID control signal for each actuator. This similar control can be used for multiple fans, heaters, dampers, and coolers.

Compulsory Damper Monitoring Mode

This mode makes sure that dampers are opened or closed before starting or stopping the AHU, or the modulating type dampers are run for a certain time to then make AHU functional.

This requires limit switch inputs from dampers. Damper control makes AHU safer to operate because then there will be no issue of clogged air or air not passing through ducts, or even fire not spreading in the room.

These are the general modes used everywhere in AHU systems. You can customize the program in a PLC according to your requirements, for modulating the various heating and cooling elements accordingly. In this way, we saw the different control modes of AHU.

Read Next:

  • Types of HVAC Chillers
  • HVAC Heat Transfer Loops
  • Automation used in HVAC
  • HVAC Objective Questions
  • Valves in HVAC System
Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

How does a Redundant Controller comes in line when the Main Controller fails?
What is Instrumentation and Control ?
ESD System Insights: Signals for Emergency Valve Shutdown Explained
Foundation Fieldbus Split Range Valves
How to Do Loop Checks During Plant Pre-Commissioning
Troubleshooting Current Loops with Voltage Measurement
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
Leave a Comment

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

Difference between Fieldbus, Profibus and HART Protocols
Top 5 Advantages of Human-Machine Interface (HMI)
Determining the Design Purpose of Override Controls
How to Design a Motor Faceplate in Graphics? – SCADA Tutorials
Loop-powered 4-20 mA Transmitter Circuit Voltage drop
How to Write a Program in Ecostruxure Machine Expert HVAC Software?
Add On Instructions Programming – Analog Input Devices in Studio 5000
Compare Modbus, Fieldbus, and Profibus

Keep Learning

Control systems in industrial projects

Interactions With Process Control Systems Philosophy

PID Controller Tuning

How to tune a PID Controller ?

Temperature Control System Example

Chemical Reactor Temperature Control System

What is Static Grounding

What is Static Grounding?

Difference Between SCADA and HMI

Difference Between SCADA and HMI

Automation in Mining Industry

Industrial Automation in the Mining Industry

Manufacturing Execution System in Industrial Automation

Manufacturing Execution System (MES) in Industrial Automation

Sample Schematic Template for Systems Architecture Diagram

Design Document for Project Systems Architecture

Learn More

Instrumentation and Process Control Project Inputs

Instrumentation and Process Teams Interactions in Design Engineering Companies

Flow meter Turndown Ratio

Importance of Flow Meter Turndown Ratio

Basic Pneumatic System

Introduction to Fluid Power and Pneumatics

Installation and Calibration of Level Transmitter

Installation and Calibration of Level Transmitter

Analog Modulators Objective Questions

Analog Modulators Objective Questions

Insertion flow meters

What is an Insertion Flow Meter? – Types, Principle, Advantages

Search tank in Intouch Scada

Tank Filling and Emptying using Intouch Scada Script

Orifice Flow Measurement Formula

Basics of Flow Measurement

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?