Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: Boiler Drum Level Control Systems
Share
Notification Show More
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Control Systems > Boiler Drum Level Control Systems

Boiler Drum Level Control Systems

Last updated: March 19, 2019 12:31 pm
Editorial Staff
Control Systems
2 Comments
Share
11 Min Read
SHARE

Drum Level Control Systems are used extensively throughout the process industries and the Utilities to control the level of boiling water contained in boiler drums on process plant and help provide a constant supply of steam.

Contents
Drum Level Control SystemsThe Boiler DrumComponents Affecting Drum Water LevelDrum Level Control StrategiesSingle element Drum level ControlTwo element Drum level ControlThree element Drum level ControlEnhanced three element drum level control

If the level is too high, flooding of steam purification equipment can occur.

If the level is too low, reduction in efficiency of the treatment and recirculation function. Pressure can also build to dangerous levels.

A drum level control system tightly controls the level whatever the disturbances, level change, increase/ decrease of steam demand, feedwater flow variations.

Drum Level Control Systems

In the process industries, boiling water to make steam is a very important procedure. The control of water level is a major function in this process and it is achieved through a water steam interface established in a cylindrical vessel called the drum which is usually lying on its side and located near the top of the boiler.

Providing tight water level control in a drum is accomplished by utilizing one of three types of drum level control: single-element, two-element, or three-element.

The Boiler Drum

Maintaining the correct water level in the drum is critical for many reasons. A water level that is too high causes flooding of the steam purification equipment; resulting in the carry over of water and impurities into the steam system.

A water level that is too low results in a reduction in efficiency of the treatment and recirculation function. It can even result in tube failure due to overheating from lack of cooling water on the boiling surfaces. Normally drum level is expected to be held within 2 to 5cm of the set-point with some tolerance for temporary load changes.

Components Affecting Drum Water Level

Under boiling conditions, steam supporting field products such as bubbles exist below the water/steam level interface. These bubbles have volume and therefore displace water to create a misrepresentation of the true water level in the drum. Another effect upon drum level is pressure in the drum.

Because steam bubbles compress under pressure (if the drum pressure changes due to load demands), the steam bubbles expand or contract respective to these pressure changes. A higher steam demand will cause the drum pressure to drop, and the steam bubbles to expand to give the appearance of a water level higher than it truly is.

This fictitious higher water level causes the feedwater input to be shut down at a time when more water is really required. A surge in water level as a result of the drum pressure decreasing is called ‘swell’. A water level decrease due to drum pressure increase is called ‘shrink’.

Drum Level Control Strategies

The below table depicts three types of drum level control strategies with typical applications for each. While single-element drum level control is acceptable for steady boiler load conditions; as load changes become more frequent, unpredictable, or severe; this type of level control cannot respond quickly enough to compensate.

More information must be included and processed to predetermine the amount of water to be added to the drum to compensate for load changes. The addition of elements (flow and transmitter devices) enables the controller to predict the amount of water added to the drum to maintain drum level set-point.

Types of Drum Level Control System

Single element Drum level Control

This is a very simple kind of drum level control design. It needs single analog input for its operation and in return provides single analog output.

Hence, it is named single element control. “Because there’s no relationship between drum level and steam or feedwater flow, it can be applied only to a single feed pump on a single boiler supplying a relatively stable load.”

Its performance is not as effective as compared to other two level control designs. A typical drum level control with single element module is shown in the figure below.

Single element Drum level Control

The simplest but least effective form of drum level control.

This consists of a proportional signal or process variable (PV) coming from the drum level transmitter. This signal is compared to a setpoint and the difference is a deviation value.

This signal is acted upon by the controller which generates corrective action in the form of a proportional output. The output is then passed to the boiler feedwater valve, which then adjusts the level of feedwater flow into the boiler drum.

Notes:

  • Only one analogue input and one analogue output required
  • Can only be applied to single boiler / single feedpump configurations with relatively stable loads since there is no relationship between drum level and steam- or feedwater flow
  • Possible inadequate control option because of the swell effect

Two element Drum level Control

This drum level control design is particularly suitable in case of single drum boilers where the feedwater is available at a constant pressure.

“Two-element control includes the same level element used for the single-element configuration but has an added steam-flow element that provides a density-corrected mass flow-rate signal to control the feedwater flow.”

In this design, presence of double control elements tends to provide rigid drum level control. A typical drum level control with two element module is illustrated in the figure below.

Two element Drum level Control

The two-element drum level controller can best be applied to a single drum boiler where the feedwater is at a constant pressure.The two elements are made up of the following:

Level Element: a proportional signal or process variable (PV) coming from the drum level transmitter. This signal is compared to a setpoint and the resultant is a deviation value. This signal is acted upon by the controller which generates corrective action in the form of a proportional value.

Steam Flow Element: a mass flow rate signal (corrected for density) is used to control the feedwater flow, giving immediate corrections to feedwater demand in response to load changes. Any imbalance between steam mass flow out and feedwater mass flow into the drum is corrected by the level controller. This imbalance can arise from

  • Blowdown variations due to changes in dissolved solids
  • Variations in feedwater supply pressure
  • Leaks in the steam circuits

Notes:

  • Tighter control of drum level than with only one element
  • Steam flow acts as feed forward signal to allow faster level adjustments
  • Can best be applied to single boiler / single feedpump configurations with a constant feedwater pressure

Three element Drum level Control

“Three-element drum-level control is suited for handling variable feedwater pressure or multiple boilers with multiple feedwater pumps.”

In this design, three elements are used, each for controlling level, steam and feedwater flow respectively. This system offers far better and advanced drum level control as compared to all other systems.

For best control, correct flow values of both steam as well as feedwater must be maintained with regard to density. A typical drum level control with three element module is shown in the figure below.

Three element Drum level Control

The three-element drum level control is ideally suited where a boiler plant consists of multiple boilers and multiple feedwater pumps or where the feedwater has variations in pressure or flow. The three-elements are made up of the following:

Level Element & Steam Flow Element: corrects for unmeasured disturbances within the system such as

  • Boiler blowdown
  • Boiler and superheater tube leaks

Feedwater Flow Element: responds rapidly to variations in feedwater demand, either from the

  • Steam flow rate feedforward signal
  • Feedwater pressure or flow fluctuations

In order to achieve optimum control, both steam and feedwater flow values should be corrected for density.

Notes:

  • The three-element system provides tighter control for drum level with fluctuating steam load. Ideal where a system suffers from fluctuating feedwater pressure or flow
  • More sophisticated level of control required
  • Additional input for feedwater flow required

Enhanced three element drum level control

The enhanced three-element drum level control module incorporates the standard three element level components with the following improvements:

  • The three-element mode is used during high steam demand. The two-element mode is used if the steam flow measurement fails and the module falls back to single element level control if the feedwater flow measurement should fail or if there is a low steam demand.
  • The drum level can be derived from up to three independent transmitters and is density compensated for pressure within the boiler drum.

Notes:

  • Tighter control through a choice of control schemes. Drum level maintained on failure of steam or feedwater flow measurements
  • This module introduces an additional level control loop Boiler drum level control

Read Articles :

  1. Single Element Drum Level Control System
  2. Two Element Drum Level Control System
  3. Three Element Drum Level Control System
Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Process Control Loop Testing
Interview Questions on PID Controllers
Explaining Various Types of Analog Instruments
Functional Design Specifications for DCS and SIS Projects – FDS Document
Emergency Stop Switch Spurious Trip
Learn about PLC, DCS, RTU, SCADA, and PAC
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
2 Comments
  • jonathan says:
    August 6, 2016 at 11:12 pm

    good data

    Reply
  • manish says:
    August 8, 2016 at 5:20 pm

    Sir I want details with simple explanation of Motorized Control Valve and details related to thermal power plant

    Reply

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

Overview of Split Range Control
Difference between Cold Standby and Hot Standby
Hardwired I/O and Serial I/O – Differences Explained
Modbus Function Command Formats
What is PID Controller?
What is a Network Connector? – Types of Connectors
Heat Exchanger Temperature Control
Project Planning and Implementation of PLC or DCS Control System

Keep Learning

What is FAT and SAT?

What is FAT and SAT? Difference between them

What we need to Know before Tune a PID Controller

What we need to Know before Tune a PID Controller ?

Two Out of Three Logic

Alarm and Trip Systems

List of 100 Questions Related to Distributed Control Systems (DCS)

List of 100 Distributed Control Systems Questions (DCS)

Internet of Things (IOT)

History of Internet of Things (IOT)

DCS Alarm Summary Dashboard using Microsoft Power BI

DCS Alarm Summary Dashboard using Microsoft Power BI

Unmanaged Switch

Managed Switch vs Unmanaged Switch

What is Static Grounding

What is Static Grounding?

Learn More

GuideLines for Loop Checks

How to Do Loop Checks During Plant Pre-Commissioning

Function of Racks in PLC System

Function of Racks in PLC – Types of SIEMENS S7-400 PLC Racks

Thermocouple Calculations

Free Download Thermocouple Calculator

Why have been limits imposed on the frequency ratio for thermowells?

Displacement Level Transmitter in situ calibration

Displacer (buoyancy) Level Transmitter Principle, Limitations, Design, Installation & Calibration

Fiber Optic Patch Cord

What is a Fiber Optic Patch Cord? – Types, Explained

Electric Circuits Objective Questions

Electric Circuits Objective Questions – Set 10

Pressure Gauge Dial

Information on the Pressure Gauge Dial

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?