Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: Why choose Intrinsic Safety ?
Share
Notification Show More
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Safety Instrumented System (SIS) > Why choose Intrinsic Safety ?

Why choose Intrinsic Safety ?

Last updated: May 13, 2019 7:47 am
Editorial Staff
Safety Instrumented System (SIS)
Share
10 Min Read
SHARE

Intrinsic  safety (IS) is a  low-energy  signalling  technique  that prevents explosions from occurring by ensuring that the energy transferred to a hazardous area is well below the energy required to initiate an explosion.

Contents
Intrinsic safetyThe advantages of intrinsic safetyAvailable power

Intrinsic safety

Why choose Intrinsic Safety ?

The  energy   levels   made   available   for signalling  are  small but useable  and  more  than  adequate  for  the  majority   of instrumentation systems.

The  two mechanisms  being  considered that  could  initiate  an explosion are:

  • A spark
  • A hot surface

The advantages of intrinsic safety

The major advantage of intrinsic safety is that it provides a solution to all the problems of hazardous areas (for equipment requiring limited power) and is the only technique which meets this criterion.

The significant factors are as follows:

a) The IS technique is accepted throughout the There is an increasing acceptance of international  certificates  issued under  the IEC Ex scheme but this has some way to go. Intrinsic safety is an acceptable technique in all local legislation such as the ATEX Directives  and OSHA. The relevant standards and code of practice give detailed guidance on the design and use of intrinsically safe equipment to a level which is not achieved by any of the other methods of protection.

b) The same IS equipment usually satisfies the requirements for both dust and gas

c) Appropriate intrinsically safe apparatus can be used in all In particular, it is the only solution that has a satisfactory history of safety for Zone 0 instrumentation. The use of levels of protection (‘ia’, ‘ib’ and ‘ic’) ensures that equipment suitable for each level of risk is available (normally ‘ia’ is used in Zone 0, ‘ib’ in Zone 1 and ‘ic’ in Zone 2

d) Intrinsically safe apparatus and systems are usually allocated a group IIC gas classification which ensures that the equipment is compatible with all gas/air     Occasionally,  IIB systems are used, as this permits a higher power level to be used. (However, IIB systems are not compatible with acetylene, hydrogen and carbon disulfide.)

e) A temperature   classification   of T4  (135°C)  is normally achieved, which satisfies the requirement for all industrial gases except carbon disulfide  (CS ) which, fortunately, is rarely

f) Frequently, apparatus, and the system in which it is used, can be made ‘ia IIC T4’ at an acceptable This removes concerns about area classification, gas grouping and temperature classification  in almost all circumstances  and becomes the universal safe solution.

g) The ‘simple apparatus’ concept allows many simple pieces of apparatus, such as switches, thermocouples, RTD’s and junction boxes to be used in intrinsically safe systems without the need for certifica This gives a significant amount of flexibility in the choice of these ancillaries.

h) The intrinsic safety technique  is the  only technique  that permits live maintenance within the hazardous area without the need to obtain ‘gas clearance’ certifica This is particularly important  for instrumentation,   since  fault-finding   on  de- energised equipment is difficult.

i) The installation and maintenance requirements for intrinsically safe apparatus are well documented, and consistent regardless of level of  This  reduces  the  amount  of training required and decreases the possibility of dangerous mistakes.

j) Intrinsic safety permits the use of conventional instrumentation cables, thus reducing Cable capacitance and inductance is often perceived as a problem but, in fact, it is only a problem on cables longer than 400 metres, in systems installed in Zones 0 and 1, where  IIC gases (hydrogen)  are the source  of risk. This is comparatively rare and, in most circumstances, cable parameters are not a problem.

Intrinsic safe Available Power Curves

Available power

Intrinsic  safety  is  fundamentally  a low energy  technique  and consequently the voltage, current and power available is restricted.

Figure 1.0 is a simplified illustration of the available power in intrinsically safe circuits and attempts to demonstrate the type of electrical installation in which the intrinsically  safe technique is applicable.

The blue and green curves are the accepted design curves used to avoid spark ignition  by resistive  limited  circuits  in Group IIC and IIB gases. The ‘ic’ curves are less sensitive because they do not require the application of a safety factor in the same way as for

‘ia’ and ‘ib’ equipment. In general the maximum voltage available is set by cable capacitance  (400  metres  corresponds to 80nF which has a permissible voltage of 29V in ‘IIC ia’ circuits) and the maximum current by cable inductance (400 metres corresponds to 400µH which  has a permissible  current  of 300 mA in IIC ia circuits). A frequently used limitation on power is the 1.3W, which easily  permits  a T4  (135°C)  temperature  classification.  These limits are all shown in Figure 1.0

A simple approach is to say that if the apparatus can be operated from a source of power whose output parameters are within the (blue) hatched area then it can readily be made intrinsically safe to ‘ IIC ia T4’ standards. If the parameters exceed these limits to a limited degree then it can probably be made intrinsically safe to IIB or ‘ic’ requirements.

The first choice, however, is always to choose ‘IIC ia T4’ equipment, if it provides adequate power and is an economic choice, as this equipment  can be used in all circumstances  (except if carbon disulfide  (CS ) is  the  hazardous  gas, in  which  case  there  are other problems).

 Also Read: Difference between DCS & PLC Systems

In practice almost all low voltage instrumentation  can be made

‘IIB ic T4’ as the  limits  are set  by the  least  sensitive  of  the ignition curves in Figure 1.0 (typically 24V 500 mA). The ‘IIB ic’ specification  does restrict  application to Zone 2 and where the hazardous gas is not hydrogen, acetylene or carbon disulfide but is still applicable to a large range of installations.

Conclusion

Intrinsic safety   is  the   natural   choice   for all  low   voltage instrumentation  problems.  Adequate solutions  exist  which  are compatible with all gases and area classifications. The technique prevents  explosions rather  than  retains  them  which  must be preferable, and the ‘live maintenance’ facility enables conventional instrument practice to be used.

Why use intrinsic safety?

The principal  reason for using intrinsic  safety is because it is essentially a low power technique. Consequently, the risk of ignition is minimized, and adequate safety can be achieved with a level of confidence that is not always achieved by other techniques.

It is difficult to assess the temperature rise, which can occur if equipment is immersed in a dust because of the many (frequently unpredictable)  factors,  which determine  the  temperature  rise within the dust layer. The safest technique is therefore to restrict the available power to the lowest practical level.

A major factor in favor of intrinsic safety is that the power level under fault conditions is controlled by the system design and does not rely on the less well-specified limitation of fault power.

Intrinsic safety also has the advantage that the possibility of ignition from immersed or damaged wiring is minimised. It is desirable to be able to do ‘live maintenance’  on an instrument  system, and the use of the intrinsically safe technique permits this without the necessity of special ‘dust free’ certificates.

There is a need to clear layers of dust carefully and to avoid contamination of the interior of apparatus during maintenance but this is apparent to any trained technician. (There is no significant possibility of a person, in a dust cloud that can be ignited, surviving without breathing apparatus).

To summarize,  intrinsic  safety  is the  preferred  technique  for instrumentation where dust is the hazard because:

  • the inherent safety of intrinsic safety gives the greatest assurance of safety and removes concern over overheating of equipment and cables
  • the installation rules are clearly specified and the system design ensures that all safety aspects are covered
  • live maintenance is permitted
  • equipment is available to solve the majority of problems

Articles You May Like :

Preventive Maintenance

Flameproof Equipment ?

Electrical Wiring Terminology

What is Safety Control System ?

Electrical Safety Measures

Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Safety Instrumented System (SIS) Worksheets and Documents
Reliability of a Control System
What is Partial Stroke Test?
What is High Integrity Pressure Protection System?
S84 / IEC 61511 Standard for Safety Instrumented Systems
What is Burner Management System (BMS)?
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

Safety Integrity Level (SIL)
Understanding High Integrity Pressure Protection Systems (HIPPS)
Concept of Redundancy in Control Systems
Functional Safety Questions & Answers
Energize to Safe Loop philosophy
Component De-rating in Control Systems
Automated Block Valve (ABV)
Layers of Protection Analysis (LOPA) Interview Questions

Keep Learning

Process Shutdown

Difference between Process shutdown and Emergency Shutdown

ESD System Insights

ESD System Insights: Signals for Emergency Valve Shutdown Explained

SIS PFD - Safety Instrumented System

SIS PFD – Safety Instrumented System

Parts of Safety PLC

SIS Software Simulation – Safety Instrumented System

SIS Failures and Reliability - Safety Instrumented Systems

SIS Failures and Reliability – Safety Instrumented Systems

safety PLC programming

SIS Logic Solver

Purpose of Emergency Shutdown (ESD) System

Purpose of Emergency Shutdown (ESD) System

Proof Testing - Safety Instrumented System (SIS)

What is Proof Testing? – How to do a Proof Test? – Importance, Methods

Learn More

What is a Network Switch?

Network Switch Requirement in SCADA and DCS Architecture

Instrumentation Colleges in United States

Colleges to Study Instrumentation Engineering in United States

Valve Interlock

Valve Interlock

Questions and Answers in Electrical Machines

Questions and Answers in Electrical Machines

Rack Type PLC

PLC Input Output Modules

corroded tank

Cathodic Protection – Sacrificial Anodic and Impressed Current

RTD Questions & Answers

RTD Questions and Answers

Thermocouple Temperature Ranges

Thermocouple Temperature Range Questions and Answers

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?