Reading: Stroke Checking Procedure for GCV, SRV, IGV, and LFBV
Inst Tools > Blog > Calibration > Stroke Checking Procedure for GCV, SRV, IGV, and LFBV
Learn the stroke checking procedure for GCV, SRV, IGV, and LFBV using the Mark V gas turbine control system.
Last updated: October 17, 2023 2:14 pm
Calibration Control Systems Power Plant
6 Min Read
GCV / SRV Stroke CheckingIGV Stroke CheckingLFBV Stroke Checking
Make sure that cool down, crank, or off mode is selected (L3ADJ should be 1).
Make sure that Equipment is isolated by the operation department and clearance is given for stroke checking.
Make sure that upstream pipeline gas is vented. L20FSX status should be “1”. Otherwise it can be forced to 1.
Make sure that ALOP and AHOP are running and hydraulic oil pressure is established.
Make sure that your selection of Unit1/Unit2 as per the Gas Turbine-1/2
Make sure that Mark-V Selection is in local.
Insert following signals required for forcing & monitoring the Turning gear speed, Hydraulic pressure, trip oil pressure etc
HQP – Hydraulic pressure
TNH – Turning gear speed
GFOT – Trip oil pressure –Gas fuel
LFOT – Trip oil pressure – Liquid fuel
L20TV1X – Trip solenoid valve of IGV
L20FG1X – Trip Solenoid valve of GCV/SRV
L20FL1X – Trip Solenoid valve of Liq. fuel b/p valve
Enable maintenance password
Go to logic forcing display
Force L4_XTP to 0 (If Turning gear is ON and required to be kept ON, as GT cool down is not over. In this case L4 not to be forced to 1)
If turning gear is off force L4 to 1
Caution: Don’t Force L4 to 1, it will affect machine Turning gear operation
Force the following two signals for stroking the GCV or SRV
* Force L20TV1X to 1 (For energising Trip solenoid valve of IGV)
* Force L20FG1X to 1 (For energising Trip Solenoid valve of GCV/SRV)
If required vent the gas between shut of valve and SRV by forcing L20PSX to 1
If required keep the shut of valve at filter skid close by forcing L20FSX to 0
(Force 1 to open and 0 to close the valve)
Save points and quit Logic Forcing Display. After forcing above points, see gas fuel trip oil pressure GFOT is above 5 bar.
Mark-V Screen
Enable with password
Go to “Auto calibrate” page
Select “Gas Control Valve” or  “Stop/Speed Ratio valve”
Click on “ENABLE COMMAND” SOFT BUTTON
Click on “OK” Soft button
Click on “Enable Manual”
Enter Manual set point, Note down the % of opening and LVDT Voltage.
Select Value – Required value
Enable command & execute
Once the calibration is over, press IDLE ABORT and exit.
IGV Stroke Checking
* Force L20TV1X to 1 and L20FG1X to 1 (For Energising Trip Solenoid valve of ICV)
Mark-V Screen
Select “Inlet Guide vane control”
* Force L20FL1X to 1 (For Energising Trip Solenoid valve of Liq. fuel b/p valve)
Save points and quit Logic Forcing Display. After forcing above points, see gas fuel trip oil pressure LFOT is above 5 bar.
Mark-V Screen
Select “Liquid fuel bypass valve”
  • DCS Commissioning Procedure
  • Gas Turbine Control System
  • Gas Turbine Interview Questions
  • Types of Turbine Protection
  • Forcing and Modifying PLC Logic
How to Create Calibration Records?
How does a Redundant Controller comes in line when the Main Controller fails?
What is Interposing Relay in a PLC System ?
Foundation Fieldbus Installation and Best Practices
What is Marshalling Cabinet?
Types of Industrial Control Systems
Fieldbus Flow Transmitter Configuration
Fiber Optic Cable – Method of Joining and Fusion Splicing
Selection of Weighing Balance and Weight for Calibration
Industrial Automation and Control Systems (IACS)
Chemical Reactor Temperature Control System
Multiphase Flow Meter Calibration Procedure
Differential Pressure Switch Calibration Procedure
Stability and Uniformity of Temperature Bath
Wireless HART Transmitter
How to Commission WirelessHART Transmitter With Gateway
Automation in Mining Industry
Industrial Automation in the Mining Industry
Power Supply Sizing for Industrial Automation Systems
Augmented Reality and Virtual Reality in Industrial Automation
Feedforward with Dynamic Compensation - 3
Feedforward Control with Dynamic Compensation
Pressure and Level Control Loop
Problem on Pressure and Level Control Loops
VPN for Control Engineers
How Important is VPN for Control Engineers?
Controller Components – Part 1 Objective Questions
Averaging Pitot Tube Principle
What is a Torbar? – Averaging Pitot Tubes
DCS System Cabinet
Yokogawa DCS System Maintenance Procedures
PLC Commissioning and Testing
PLC Commissioning and Testing Procedure (Programmable Logic Controller)
Time Response Analysis
Steady-state Errors & Error Constants
Siemens S7-200 PLC Ladder Logic
Programmable Logic Controller (PLC) Questions and Answers – 10
Head Mount Temperature Transmitter
What is a Head Mount Temperature Transmitter? – Advantages
Impressed Current Galvanic System