In this article, we are going to discuss one root cause analysis in which a Solenoid solenoid-operated valve (SOV) did not open while start-up of the plant. This article is an interesting one.
Solenoid Valve Failure in Plant Start-Up
After the shutdown of the Nitrogen plant in one unit of a refinery, a start-up was planned.
In the start-up procedure, if the product nitrogen’s purity comes within spec, then the product is diverted to the main nitrogen header by opening a final product on-off valve.
Till then, the product is being vented because it is not in proper specs.
During start-up, the specs of the nitrogen were within the limit. So, the panel engineer gave the open command to the final product on-off valve to divert the product nitrogen to the main header. But the valve did not open and a command vs feedback error was generated.
The panel engineer gave the close command and then again gave the open command to the valve. But the valve did not open. So, he informed instrumentation engineers to check the valve.
The on-off valve was a single-acting valve with a fail condition close. The instrumentation team checked and solved the issue within an hour. Then after stroke checking, the on-off valve was taken inline.
Observations of the Operation & Maintenance Team
During the start-up procedure, when the purity of the nitrogen reached the acceptable limit, the panel engineer gave the open command to the final product on-off valve which diverts the nitrogen to the main header. But the valve did not open.
The panel engineer tried one more time but still, the valve did not open. So, the Instrumentation team was informed about this and they visited the field.
Instrumentation Engineer Activities
The following activity was done by the Instrumentation team in the field
- Checked supply voltage to the SOV. The supply voltage was ok.
- The actuator was checked for passing issues. The actuator was found ok.
- Valve operation is checked by giving direct air to check the valve body’s condition. Valve operation was smooth.
- Disconnected the tubing connecting the actuator and SOV (while open command is present). But no air was coming.
- Checked the resistance of the solenoid valve (SOV) and found that the resistance was 5600 ohm.
The instrumentation team replaced the SOV’s coil and the issue was resolved.
Also, on checking the records, it was found that the preventive maintenance (PM) of this valve was done 5 days before the incident. In PM no observation came and the valve operation was ok.
Root Cause Analysis
A fault tree analysis was made for this incident which is shown below:
As mentioned in the above fault tree analysis, the valve did not open due to the SOV coil having an issue.
Various reasons mentioned below were considered and a conclusion was made. The reasons are:
- The valve did not have any active interlock to close it. Also, permissive to open the valve was ok.
- Instrument air pressure was checked and was found ok as per valve requirement.
- Supply voltage to the SOV in the field was also ok.
- Actuator was also ok and no passing was present.
- Valve was operated by giving direct air to check the body’s condition. The valve operation was smooth.
- SOV’s coil was checked and found that the coil’s resistance was higher than normal. It was 5900 as compared to 55 ohms.
Here, SOV’s coil was not in healthy condition and hence the valve was not opening.
Recommendations
2 recommendations came after this incident. These recommendations should be implemented in every plant.
Recommendation 1: In PM activity of a valve, always check the resistance of the SOV coil. In this case, the resistance might have increased gradually over time. This could have been identified in the PM activity if coil resistance checking was done.
Recommendation 2: In LLF activity, check the SOV’s temperature. Abnormally high temperature of SOV indicates that the coil is heating and action needs to be taken.
its excellent troubleshooting. i have one question that how can we measure the resistance of of SOV coil during normal PM and plant running conditions. we can’t measure the resistance of live electrical equipment, until we disconnect the cable. if we want to measure the resistance of sov coil then valve will be go to fail safe condition. normally its not recommended to check resistance because it will also affect process side