Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: SIS Instrument Sharing – Transmitters Shared for BPCS and SIS Example
Share
Notification Show More
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Safety Instrumented System (SIS) > SIS Instrument Sharing – Transmitters Shared for BPCS and SIS Example

SIS Instrument Sharing – Transmitters Shared for BPCS and SIS Example

In Safety Instrumented System (SIS), Instrument sharing may be considered with due caution to ensure all protection layers are independent.

Last updated: May 21, 2022 10:48 am
Editorial Staff
Safety Instrumented System (SIS)
1 Comment
Share
4 Min Read
SHARE

In Safety Instrumented System (SIS), Instrument sharing may be considered based on the system configuration and available sensors or final control elements with due caution to ensure that all protection layers are independent.

Contents
SIS Instruments SharingSafety Instrumented System Sharing BasicsA basic example of Independent Protection Layer creditsTransmitters Shared for BPCS and SIS ExampleBasics of SIS Instruments SharingSharing KeypointsCaution with Instruments Sharing

SIS Instruments Sharing

  • The layer of Protection Analysis (LOPA) conservatively assumes that every Independent Protection Layer (IPL) is independent and provides integer order of magnitude risk reduction credits.
  • Sharing Rules have been developed for practical application, using international standards such as IEC for guidance.
  • Any sharing typically violates the assumptions and calculations behind LOPA.

Safety Instrumented System Sharing Basics

  • Each Layer of Protection is like a barrier or wall that can prevent something from happening, hence proper care is to be considered while sharing instruments.
  • Each IPL may have different strengths, or effectiveness (IPL credits) and hence diversified instruments can be considered while sharing.
  • Each IPL must be independent – common elements (common mode failures) may reduce or eliminate the strength of some or all layers. when the instruments are designed for sharing ensure to avoid common power, instrument tapping, etc.

A basic example of Independent Protection Layer credits

If the protection layers are not independent, then the shared components must be made stronger to make up for the lack of independence.

The below picture shows the Independent protection layer (IPL) credits with

Safety Instrumented System – 1 credit

Safety Relief Protection System (Ex. Rupture disk) – 1 credit

Basic Process Control System – 1 credit

Pressure Safety Valve – 2 credits

Total – 5 credits

Sharing BPCS and SIS Field Instruments

Transmitters Shared for BPCS and SIS Example

In this below example, two Temperature transmitters are shared for BPCS and SIS.

transmitters shared for BPCS and SIS

Basics of SIS Instruments Sharing

The Sharing basics as below

1. Sum of the LOPA credits

Design as SIL-2 (SIL-1 + BPCS LOPA credits).

2. Increased diagnostics

Shared instruments need 90% diagnostics.

70% for smart NAMUR instruments,

20% for “open/short circuit” detection plus Deviation Alarm between redundant sensors.

3. Independent usage of sensors

BPCS must select the signal (high or low) that will drive the process to a safe state.

Sharing Keypoints

  1. Sharing without an SIS is allowed (Like for Operator response to alarm & BPCS functions), but the shared components must be treated (designed, documented, tested, and audited) as SIS elements. [It may be less confusing to just make it a SIL-2 SIF!!]
  2. Duplication of shared code for independence (instead of different selection mechanisms).
  3. Sharing of the Initiating Event (if the sharing rules are allowed per calculation tools)
  4. It is allowed to share only once.
  5. It is not allowed to share a set of sensors between [BPCS, SIS & ALARM], [IE, SIS & ALARM], etc. The only exception is motor starters.
  6. The maximum “Sum of the LOPA credits” is 3.

Caution with Instruments Sharing

If shared components “could be” the cause of the initiating event, then it’s not allowed to share.

If you liked this article, then please subscribe to our YouTube Channel for Electrical, Electronics, Instrumentation, PLC, and SCADA video tutorials.

You can also follow us on Facebook and Twitter to receive daily updates.

Read Next:

  • What is HIPPS System?
  • Emergency Block Valves
  • SIS Common Cause Failure
  • SIS Verification & Validation
  • Testing and Repair Deferral
Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Transistor Failure Rate Calculation
SIS Instruments and Valves Inline Testing – Safety Instrumented System
Understanding Emergency Shutdown Button Installation (ESD)
Safety Integrity Level (SIL)
Free Safety Instrumented System Training Course
Layers of Protection Analysis (LOPA) Interview Questions
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
1 Comment
  • Taekbeom Kwon says:
    November 20, 2023 at 1:28 pm

    Hello, I have a doubt in the sharing.
    What norm allows the sharing sensors between BPCS and SIS, as well as grants each credit either for BPCS and SIS?
    Though these were defined as IPLs.
    I’ll be perfect if you would mention the clause as well.

    BR
    Taek

    Reply

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

SIS Application Program – Safety Instrumented System
What is a Logic Solver? – Safety PLC
S84 / IEC 61511 Standard for Safety Instrumented Systems
Purpose of Emergency Shutdown (ESD) System
What is Partial Stroke Test?
SIS Verification & Validation – Safety Instrumented System
Direct-actuated Safety and Relief Valves
SIS Logic Solver

Keep Learning

Process Override Switch

What is Process Override Switch (POS)?

energized-to-safe-loop

Energize to Safe Loop philosophy

hipps

What is High Integrity Pressure Protection System?

Project Management of Safety Instrumented System

Project Management of Safety Instrumented System (SIS)

Typical schematic of Butterfly valve

Automated Block Valve (ABV)

Emergency Shutdown System Philosophy

Shutdown Philosophy

failure rate of a component - 1

Failure rate and MTBF of Safety Instrumented Systems

Safety PLC System

SIS Maintenance – Safety Instrumented System

Learn More

Dissolved oxygen measurement using Optical Fiber Communication

Fiber Optic Sensors

List of Documents Required for Testing and Calibration Laboratory

List of Documents Required for Testing and Calibration Laboratories

Digital Electronics Multiple Choice Questions

Register-Transistor Logic (RTL) Objective Questions

Safety Instrumented Systems are different from Basic Process Control Systems

Safety Instrumented System Handbook – SIS Tutorials

Basic Temperature Sensors MCQ

Basic Temperature Sensors MCQ Questions Answers

PLC Training Data Tables FIFO and LIFO

FIFO Instruction in Allen Bradley PLC Programming

Breather Valve Working Principle

Breather Valve Working Principle

PlantPAx DCS

Introduction to PlantPAx Distributed Control System

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?