The I-Device function can be used to exchange data between two PLCs very easily. An I-Device is simply a PLC that is used as an IO device. That means the PLC will act as an IO module providing inputs and receiving outputs with the other PLC.
I-device function enables PROFINET to communicate not only with subordinate devices like IO controllers, but also IO communication with other higher-level or central controllers as an IO device.
Most of the S7 family PLCs support the I-Device feature but some controllers don’t depending on the firmware version for example:
  • S7-300 (from firmware version V3.2)
  • S7-1200 (from firmware version V4)
You can simply know if your controller has the I-device feature or not by going into your PLC PROFINET interface properties and checking for the “operating mode” option. See pictures 1a and 1b.
picture 1a. PLC doesn’t support I-device
From the picture, we can’t see the “operating mode” option, so we know that PLC doesn’t support the I-device feature.
PLC supports the I-device feature
Picture 1b. PLC supports the I-device feature
As you see from the picture, this PLC supports the I-device feature.
A PLC with the “Intelligent IO device” configuration is called an I-Device. An I-Device is like a standard IO device and needs to be handled like one. This means that the I-Device is also connected to a higher-level IO controller.
So , an I-device will act as an IO module, but it is also still a PLC, so it still acts as a controller if you want it to.
The guiding principle of the I-Device method is to use the known process image in a CPU. From the higher-level IO controller’s view, communicating to an I-Device is similar to communicating to a distributed IO with the usual read and write processes at inputs and outputs.
From the I-Device’s view, data transfer to a higher-level IO controller is also analog to the data transfer to the local or assigned distributed IO via inputs and outputs.
 There are two possibilities for configuration:
  •  Configuring an I-Device within a project.
  • Configuring an I-Device that is used in another project
When configuring an I-Device for another project, STEP 7 enables you to do this by exporting a configured I-Device in a GSD file. The GSD file can be imported in the other project or the other engineering system like other GSD files.
This allows not only for communication within the project, but also communication across projects and data exchange between different manufacturers in a tried and tested way. We will show that in another article.
In this article, we will show the Configuration of the I-device within the same Siemens PLC project.
We will assume that we have two PLCs in our project, CPU 1516-3 PN/DP which will act as the controller in this configuration, and CPU 1214C which will act as the I-device.
Start by adding the two PLCs into your TIA Portal project and setup a Profinet connection between them. See picture 2.
picture 2. Setup connection between two PLCs.
Now, we need to configure the CPU 1214C PLC as an I-device.
You do that by going to the Profinet interface properties and from the operating mode option you click on the IO device option. See picture 3.
picture 3. Select IO device.
After that, you need to assign the I-device to a higher-level controller which is the CPU 1516-3 PN/DP PLC in our project.
To do that just select that PLC from the Assigned IO controller drop-down list. See picture 4.
Siemens I-Device Programming
picture 4. Assign the I-device to the controller.
After that, the I-device is now connected and assigned to the controller PLC. See picture 5.
Siemens PLC Communication Guide
picture 5. The I-device is assigned to the controller PLC.
The next step is to exchange the data between the I-device and the controller with what is known as transfer areas.
 Transfer areas are the IO areas that are used to exchange data between the I-Device and the higher-level IO controller.
Go to the “I-Device Communication” section. Click the first field of the “Transfer areas” column. TIA Portal will create a predefined name that you are able to change. As you can see from picture 6.
Siemens Automation Networking
picture 6. Create a transfer area
Select the type of communication relationship: currently, only CD can be selected. See picture 7.
Industrial Communication Siemens
Picture 7. Choose CD communication option.
Once you select the CD option, a transfer area will be created and the addresses of the IO controller and I-device will be automatically created. See picture 8.
Siemens S7 Communication
Picture 8. Transfer area is created.
The addresses are pre-assigned automatically, if required, you can adjust the addresses to your environment and specify the length of the transfer area to be transferred consistently.
To create another transfer area as before, just press the “add new”, see picture 9.
Siemens PLC Network Configuration
picture 9. Add new transfer area.
As we said before, data exchange is based on the simple processing image concept, which means you always send an output and receive an input.
Also note that the arrow you see in previous picture indicates the flow of information between the I-device and the controller. So if I send data from the controller to the I-device then the arrow will be from the controller to I-device and the address of controller will be output and address of I-device will be input and vise verse as you can see from previous picture.
Also keep in mind that it is always better to rename your transfer areas to proper indicating names. See picture 10.
Advanced PLC Interconnectivity
Picture 10. Rename your transfer areas.
To load the PLC project data, select both controllers one after the other in the project navigation and load the project into the respective module.
Note that, because we don’t have actual hardware devices, we can’t simulate this feature.
Download this PLC project files.
  • Source Code
  • PDF Document
In the next article, we will show another way to communicate and exchange data between two PLCs in the same project or in different projects.
  • Free PLC Training for Students
  • S7-1200 Hardware Configuration
  • Factory IO and Siemens Tia Portal
  • How to Choose a PLC for a Project?
  • What is Multi-touch Technology?
PLC Energize or De-energize the Outputs based on Events
RSLogix 5000 PLC Programming Procedure
Evaluating Industrial Automation Projects Return on investment (ROI)
Relay circuits
Remote Factory Acceptance Test
Siemens PLC Interview Questions and Answers
Instrumentation Earthing
Why Use Normally-Closed Contact for Stop Buttons?
Schneider Electric PLC Timer Problem: Vacuum Cleaner
PLC Programming for Traffic Barrier Control
DCS Commissioning Steps
Control Algorithms in PLC Programming
Motor Stop Interlock for Changing the Direction PLC Program
PLC Programming for Weight-Based Packaging
How to Program Sequential Outputs in PLC
PLC Conversion Program
How to use Converters in PLC
PLC Program Upload
How to Upload Siemens PLC Programs?
Offline UPS
UPS Working Principle and Types – Offline and Online UPS Systems
DCS
DCS
Dissolved Oxygen Analyzer Questions and Answers
Gas Turbine Generator Control System
Gas Turbine Control System
PLC Ladder Logic Simulator Mobile Apps For Android
How do AC drives work
How do AC Drives Work? – Variable Frequency Drive (VFD)
Master Control Reset (MCR) ladder logic
How to use Master Control Reset (MCR) Instruction in PLC
catalytic-gas-detectors-principle
Catalytic Gas Detectors Principle
IoT Project Ideas for Beginners - Internet of Things
100 IoT Project Ideas for Beginners – Internet of Things