Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: Relay circuits
Share
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > PLC Tutorials > Relay circuits

Relay circuits

Relays may be connected together to perform logic and control functions, acting as logic elements much like digital gates (AND, OR, etc.).

Last updated: November 2, 2023 5:00 pm
Editorial Staff
PLC Tutorials
2 Comments
Share
8 Min Read
SHARE

Electromechanical relays may be connected together to perform logic and control functions, acting as logic elements much like digital gates (AND, OR, etc.).

A very common form of schematic diagram showing the interconnection of relays to perform these functions is called a ladder diagram.

In a “ladder” diagram, the two poles of the power source are drawn as vertical rails of a ladder, with horizontal “rungs” showing the switch contacts, relay contacts, relay coils, and final control elements (lamps, solenoid coils, motors) drawn in between the power rails.

Also Read : Digital Logic Gates

Ladder diagrams differ from regular schematic diagrams of the sort common to electronics technicians primarily in the strict orientation of the wiring: vertical power “rails” and horizontal control “rungs.”

Relay circuits

Symbols also differ a bit from common electronics notation: relay coils are drawn as circles, with relay contacts drawn in a way resembling capacitors:

Relay Ladder Diagram Symbols

Unlike schematic diagrams where the association between relay coils and relay contacts is represented by dashed lines, ladder diagrams associate coils and contacts by label.

Sometimes you will find relay contacts labeled identically to the coil (e.g. coil labeled CR5 and all contacts for that relay also labeled CR5) while other times you will find suffix numbers used to distinguish individual contacts within each relay from each other (e.g. coil labeled CR5 and its three contacts labeled CR5-1, CR5-2, and CR5-3).

Another notable convention in relay circuits and their ladder diagrams is that each and every wire in the circuit is labeled with a number corresponding to common connection points.

That is, wires connected together always bear the same number: the common number designates a condition of electrical commonality (all points bearing the same number are equipotential to each other).

Wire numbers only change when the connection passes through a switch or other device capable of dropping voltage.

Also Read : PLC Fail Safe Circuits

Perhaps the most confusing aspect of relay control circuits for students to grasp is the meaning of normal as it applies to the status of relay contacts.

As discussed previously, the word “normal” in this context – whether it be the status of hand switches, process switches, or the switch contacts inside control relays – means “in a condition of rest” or no stimulation.

In other words, a “normally open” relay contact is open when the relay coil is unpowered and closed when the relay coil is powered.

Likewise, a “normally-closed” relay contact is closed when the relay coil is unpowered and open when the relay coil is powered.

To illustrate this concept, let us examine a relay control circuit where a pressure switch activates an alarm light:

Relay Pressure Switch Schematic

Here, both the pressure switch and the relay contact (CR1-1) are drawn as normally-closed switch contacts.

This means the pressure switch contact will be closed when the applied pressure is less than its trip point (50 PSI), and the relay switch contact will be closed when the relay coil is de-energized.

When analyzing the operation of a relay control system, it is helpful to have some way to temporarily denote the conductive status of switch contacts and the energization status of relay coils (i.e. a notation we might sketch using pencil on a diagram to help us follow the operation of the circuit).

A symbology I recommend is the use of arrow and “X” symbols to represent power flow and no power flow (respectively). These symbols clearly denote component status while avoiding confusion with the symbols used to denote normal status of switch contacts.

In this next diagram, we assume the applied pressure is less than 50 PSI, leaving the pressure switch in its “normal” (closed) state:

Relay Control Switch Circuit

Since the pressure is insufficient to actuate the pressure switch, its contact remains in the “normal” state (closed). This sends power to relay coil CR1, thus actuating contact CR1-1 and holding it in the open state.

With CR1-1 contact open, the alarm lamp receives no power. In this example we see the pressure switch in its “normal” state but the relay in the actuated state.

Using arrow and “X” symbols again to represent the presence or absence of power in this circuit, we will now analyze its status with an applied switch pressure greater than 50 PSI:

Relay Coil De-energized

Now that there is sufficient fluid pressure applied to the switch to actuate it, its contact is forced into the actuated state which for this “normally-closed” switch is open.

This open condition deenergizes relay coil CR1, allowing relay contact CR1-1 to spring-return to its normal status (closed), thus sending power to the alarm lamp.

From this analysis we see that the lamp fulfills the function of a high pressure alarm, energizing when the applied pressure exceeds the trip point.

We typically find confused is assuming the switch contact will be in the same state it is drawn in. This is not necessarily true. The way switch contacts are drawn merely reflects their normal status as defined by the switch manufacturer, which means the status of the switch when there is no (or insufficient) actuating stimulus present.

Whether or not the switch will actually be in its normal state at any given time is a question of whether or not a sufficient stimulus is present to actuate that switch.

Just because a switch is drawn normally-closed does not necessarily mean it will be closed when you go to analyze it. All it means is that the switch will be closed when nothing actuates it.

This exact same principle applies to relay ladder-logic programming in electronic control systems called PLCs (Programmable Logic Controllers).

In a PLC, a digital microprocessor performs the logic functions traditionally provided by electromechanical relays, with the programming for this microprocessor taking the form of a relay diagram (also called a “ladder-logic” diagram).

Also Read : Pressure Switch Logic using PLC

Credits : by Tony R. Kuphaldt – Creative Commons Attribution 4.0 License

If you liked this article, then please subscribe to our YouTube Channel for PLC and SCADA video tutorials.

You can also follow us on Facebook and Twitter to receive daily updates.

Read Next:

  • Relays in Ladder Logic Tutorials
  • Power System Protection Questions
  • Pneumatic Relay Questions
  • Analyze the Relay Circuit
  • Animation of Electromagnetic Relay
Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Smart Automation Solutions: PLC Logic for Stairway Lighting
How to Convert an Electrical Diagram into PLC Program?
PLC Automatic Irrigation System
PLC Program for Trash Compactor
#15 PLC Best Practices – Safe State when PLC Restarts
How to Create Faceplate in FactoryTalk View Studio?
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
2 Comments
  • Henry says:
    May 22, 2019 at 2:58 am

    great stuff!

    Reply
  • Esequiel M Esquibel says:
    April 14, 2025 at 11:17 pm

    Please show me a schematic with 2oo4 relays

    Reply

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

Compare Servo Motor and Stepper Motor
PLC based Metro Automation Project
What Factors Affect the Choice of PLC Programming Software?
Types of Cables used in Industrial Automation
PLC Code to Start & Stop Motor and Pump as per Logic
Machine Tool and Coolant Control: PLC Ladder Logic Design
Move, Move Bit, Move Digit – Examples of Omron PLC Programs
What is a Surge Protection Device? – Principle, Types, Advantages

Keep Learning

PLC offline data of a project are compared

Compare Two Offline PLC Projects

Siemens PLC Simulator and Plant Simulation Software

How to use Simulator in Siemens PLC?

Simple PLC example Hardware configurations

Muting Functions of Safety Control Circuits – PLC Example

Siemens Communication between PLCs using I-Device

Tutorial: Siemens Communication between PLCs using I-Device

Top PLC Manufacturers

PLC Brands Software Information

How to program a running hours meter in PLC

Allen Bradley Studio 5000: Motor Running Hours PLC Program

Design a PLC program for Operational Sequence of Packaging Process

Design a PLC program for Operational Sequence of Packaging Process

PLC Karnaugh maps

How to Simplify PLC Coding Using Karnaugh Maps?

Learn More

Three Phase Electric Current Flow Animation

Symmetric Three Phase Electric Current Flow Animation

Siemens CPU Clock Memory

Alarm Acknowledge using PLC

Download Free HMI software – CODESYS

Electronic Meters Questions & Answers

Electronic Meters Questions & Answers

Negative Readings in Gas Detectors

Why Negative Readings in Gas Detectors ?

RTD Testing Methods

RTD Testing Methods in Calibration Laboratory

Network Theorems Objective Questions and Answers

Network Theorems Objective Questions and Answers

Top 100 Electrical Machines Projects for Electrical Engineers

Top 100 Electrical Machines Projects for Electrical Engineers

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?