Reading: Explaining Various Types of Analog Instruments
Inst Tools > Blog > PLC Tutorials > Explaining Various Types of Analog Instruments
Study various types of analog instruments like 2, 3, and 4 wire sensors and the analog signal types (volt, ohm, milli Amps).
Last updated: October 17, 2023 2:05 pm
Hussien Ghareb
PLC Tutorials Control Systems
9 Min Read
In our Automation world, there are two basic types of signals that manage the connection between the Field level (Instruments, Actuators) and the Control level, These two types which are (Analog, Digital) signals can utilize and transmit all you need to measure and monitor into your process (Level, Flow, Pressure…).
Digital SignalsAnalog SignalsAnalog Signal ClassificationInstrument Wiring2-wire Analog Sensors3-wire Analog Sensors4-wire Analog sensorsAnalog Signals Types and RangesResolution of Analog CardCalibration of Analog InstrumentLocal CalibrationCalibratorConclusion
First of all, you should be aware of the difference between Digital and Analog signals… so, there is some difference between those two types of signals:
Digital Signals
Digital signals can provide you with just True or False state (1, 0) it could just tell you that there is something here or Not without knowing anything else, unlike the Analog signal which can provide you with detailed information about your measurand as the signal changes with time and it could have any value of (1, 2, 10, 30, 80, 100, 500, -20, 17.3 ……).
Analog Signals
Analog signals do not have any advantages over the Digital signal every signal has its own application, so if we have a tank and we want to know just if the tank is Full or Empty we can use level switches that utilize Digital signal But if we want to know how exact the tank level (10%, 30%, 70.7%, 87% ….) we should use Level Transmitter that utilizes Analog signals.
There are two basic concepts that you should know about any Analog Instrument:
  • Instrument wiring type (2-wire, 3-wire, 4-wire)
  • The Analog signal type (volt, ohm, milli Amps)
Instrument Wiring
The most popular sensor types are 2 wire, 3 wire, and 4 wiring methods.
Any instrument should have a power connection and also a signal connection the advantage of the two-wire Instruments, that the power and signal are merged into one connection so the instrument would have Two-wire that carry the power to the device and also the same two wires transmit the Analog signal.
2-wire Analog sensors
Note: The corresponding Analog card that read the signal must have 2-wire connection feature.
Advantages of 2-wire Analog Sensors
  1. Uses only two wires which are costless and support easy wiring.
  2. Low power consumption
Disadvantages of 2-wire Analog Sensors
  1. The  configuration  is not suitable for power- hungry transmitters.
These types of instruments is not usually used as it considered complex when it compared with the two wiring devices.
In such a situation, the transmitter and receiver of the signal share a 0V line, and the other two wires are supplied by the transmitter to the PLC module.
This method is used for instruments that have a slight high-power consumption so the power wiring is being separated from the signal wires.
Image Courtesy: SensorTips
Advantages of 4-wire Analog Sensors
  1. 4 wire sensors wiring helps to eliminate the problem “Electric Interface”.
  2. Power isolation from Input-Output (IO) module would really help to build a reliable system.
Disadvantages of 4-wire Analog Sensors
  1. Requires additional cable cores.
  2. Requires a  separate power supply for transmitter and controller.
There are three major mediums that can transmit an Analog signal such as:
  1. Voltage ( 0 to 10V, 0 to 5V )
  2. Current ( 0 to 20mA, 4 to 20mA )
  3. Resistance
One of the reasons that make Automation Engineers prefer the analog current signals over the voltage signals is the Voltage drop  in any plant there would be long distance between the field level and control level so in such situation the voltage drop that is dependent on the cable length (which by its role add some resistance) will annoy the analog signal that uses ( 0:10 V ) unlike the ( 4:20 mA ) as the current will not be affected by the cable length as it just needs a closed loop.
Another good point that should be mentioned is that why Automation Engineers prefer the (4:20 mA) over (0:20 mA), the answer is the “FAIL TO SAFETY” principle the Live zero indication in the (4:20 mA) signal which is 4 mA would really help you in case of wire break detection, so if any problem occurred to the wire the (4:20 mA) signal will detect that problem unlike the (0:20 mA) signal would have no change as 0 mA in the range of the signal.
The Analog instruments that depends on the Resistance changing is limited and have its own application such as ( Weight – thermal ) process measurements, these kind of instruments might also have some issue when using as the PLC can not differ the resistance of the cable from the resistance of the sensor so you might found the cable resistance adding some values on the actual value of the process.
The Resolution expression is defined as the smallest change in the input signal that would be sensed by the
PLC card, you might have some Siemens Analog cards that are written into its description (8bit, 12bit, 14bit …) that is referred to the resolution of that card.
Assume we have 0 to 10V analog signal and also an analog card that has a resolution of 8 bit so the resolution will be calculated as follows:
Resolution = [10 – 0] / [(28) – 1]
Resolution = 10/255
Resolution = 0.0392 V
So, we can understand now from the previous equation that 0.0392V is the resolution which is the minimum change in the signal that could be detected by the PLC analog card.
Note It is preferred to have a high resolution into your PLC cards as that would give you a detail information about your measurands unlike when you have low resolution.
Every piece of Analog Instrument into your plant must be calibrated, what is meant by calibration is that you adjust your signal levels with the actual process value, most analog instruments came without calibration so, the first thing you should know the calibration of the analog device.
There are two ways for calibration:
Local Calibration
In local calibration, we get into the instrument and adjust the zero-measuring point with the minimum signal level and the span measuring point with the maximum signal level, then the device automatically makes a linear relationship between the Measurand and the signal.
Calibrator
if your device supports HART protocol then you can use the calibrator to configure and calibrate your instrument.
Conclusion
Finally, we can say that if you have the option to select the analog instrument, the best choice for most application is the 2-wire instrument with ( 4:20 mA ) signal level, and also very important.
Note that you must ensure that the analog signal of your device is matching the selection of your PLC card.
  • FB and FC Programming in PLC
  • Cyclic Interrupts in TIA Portal
  • Problem on PLC, HMI, VFD
  • Temperature Error of RTD
  • 4-wire Transmitter Current Loop
FactoryTalk View Studio – Import and Export Tutorial
How to Work with Allen Bradley RsLogix Emulator?
Advanced Skills Required for a PLC Programmer to Get a Job
Raw Counts to Engineering Units : Conversion Formula
PLC Valve Control Ladder Logic Programming
Difference between DCS & PLC Systems
PLC Raw Count Calculation for Pressure Transmitter
Establishing a Modbus Driver for SCADA Indusoft Web Studio
Test and Process Modes in Siemens PLC
80+ PLC MCQ Questions
Compressor Emergency Shutdown Root Cause Analysis
Difference Between Microcontroller and PLC
PLC Basics – Manual Control, Closed Loop, ON-OFF with Hysteresis
What is meant by the Batching Process
Batch Simulator PLC Example Program using LogixPro Simulator
how-a-4-20ma-transmitter-works
How a 4-20mA Transmitter Works?
Ladder Logic for Motor Control
PLC Programming for 3 Motors control in Ladder logic
What is an instruction list language?
Structured Text vs. Instruction List for PLC Programming
Simatic Hardware Configuration
Configuration of Profibus Network in Siemens PLC
Nuisance Alarms
What is Alarm Shelving? – Nuisance Alarms, Types, Suppression
Schneider PLC Programming Example
Schneider PLC Programming Example for Beginners
Level Transmitter configuration in PLC
Scaling with Parameters (SCP) Instruction in PLC
Configuration of Siemens Scada and PLC
Configuration of Input and Output Tags in Siemens Scada and PLC
Gas Filter Correlation (GFC) spectrometer
Gas Filter Correlation (GFC) Spectroscopy
Electronic Devices & Circuits Quiz – Set 12
PLC Program for Traffic Light Sequence using Functional Blocks
Learn PLC Programming
Basics of Ladder Diagram in PLC Programming
Network Theorems Objective Questions and Answers
Control of the Effects of Disturbance Signals by Use of Feedback