Reading: Electrical Substation – Busbar Arrangements and Layouts
Inst Tools > Blog > Electrical Basics > Electrical Substation – Busbar Arrangements and Layouts
In this article, you will learn about the types of electrical busbar arrangements and layout diagrams in substation.
Last updated: June 7, 2022 11:44 am
Electrical Basics
6 Min Read
What is a Substation?
In the process of electricity generation, transmission and distribution, the voltage needs to be transformed from low to high or high to low as per different requirements. A switching station where this transformation takes place using transformers is known as a SubStation. When this switching station is in a Power House, it is called Switchyard.
What is a Substation?Types of SubstationsBusbar ArrangementsSingle Busbar SchemeMain and Transfer BusbarDouble BusbarDouble Main and Transfer Busbar SchemeMesh Busbar SchemeBreaker and a Half SchemeElectrical Layout Drawings
Substations may be classified on the basis of purpose and location of construction. Depending on the purpose, there are Step-up substations, Primary Grid substations, Secondary substations, Distribution substations, etc.
Depending on the location of construction there are Outdoor substations, Indoor substations, Underground substations, Pole mounted substations.
Busbar Arrangements
There are various kinds of Busbar arrangements adopted for different Substations as per specific requirements.
Some of the factors guiding the selection of the arrangement are voltage level, reliability of supply, flexibility, and cost.
Some busbar arrangements commonly used are –
  1. Single Busbar, Single Busbar with Bus coupler
  2. Main & Transfer Bus
  3. Double Busbar, Double BusBar with Bypass
  4. Double Main and Transfer Busbar Scheme
  5. One & Half Circuit Breaker
  6. Ring and Mesh Busbar
In this scheme, each circuit is provided with one circuit breaker, two isolators on both sides, and a current transformer. It is the simplest and cheapest scheme.
Its limitation is that maintenance of bus and/or circuit breakers cannot be carried out without interrupting the supply.
The limitation of the Single Bus Scheme is overcome by sectionalizing the bus using a bus coupler. By doing this each section acts as an individual bus and maintenance can be carried out without a complete shutdown of the system.
Single Busbar Scheme with Bus coupler
In this scheme, there is an additional transfer busbar along with the main busbar.
When any circuit breaker needs to be taken out for maintenance, its load is transferred to the transfer busbar and the power travels to the main busbar through a bus coupler.
Main & Transfer Busbar Scheme
This way circuit breaker maintenance is possible without interrupting the supply. However, bus maintenance cannot be carried out without a complete shutdown of the system.
Double Busbar
There are two busbars in this scheme and the load can be connected to any of the busbars through isolators.
A bus coupler is also provided for the transfer of load from one busbar to another. The limitation of this scheme is that the feeder is to be shut down when its circuit breaker is under maintenance.
This limitation is overcome by connecting a bypass isolator to one of the main busbar.
Double Busbar Scheme in Substation
Double Busbar Scheme with Bypass Isolator
In this scheme, there are two main busbars with an additional transfer busbar.
When a circuit breaker is out for maintenance, its load is transferred to the transfer busbar and controlled through the bus coupler, without affecting the other feeders.
Mesh Busbar Scheme
In this scheme, a mesh is formed of all the busbars and two circuit breakers are connected in each circuit.
Maintenance of any circuit breaker is possible without interruption in supply.
Mesh Busbar Scheme
Mesh Busbar Scheme
In this scheme, three circuit breakers are used for every two circuits i.e only one spare breaker is provided for two circuits.
Layout drawings showing the actual positions of all equipment are prepared after deciding on the busbar arrangement.
Depending upon the area available, the best possible electrical layout is prepared which takes into consideration phase to phase clearance, phase to ground clearance and shows the actual position of all equipment.
Layout designing shall be done diligently maintaining proper electrical clearances to ensure satisfactory performance of system and safety of working personnel.
A typical layout of a switchyard is shown below:
Typical Switchyard Layout
Electrical Switchyard Section
Typical Switchyard Section
Author: Nitin Kumar
What is a Link Box?
Static UPS and Rotary UPS
Commissioning of VFD Drive
DOL Starter Working Principle
Motor Forward Reverse Control
What is a Lightning Arrester? How does it work?
Bus Riser in Switchgear
Electrical Contactor Interlocking Circuit Explained
What is Electrical Busbar? Types, Advantages, Disadvantages
How to Test a Motor using Megger?
How to Connect a 3 Phase Motor in Star and Delta Connections?
Types of Circuit Breakers, Advantages, Disadvantages
How to Protect Electrical Terminal Blocks From Tampering?
Acceptable Earth Resistance Values
VFD Engineer Roles – Installation and Commissioning
How to Identify Phase, Earth, and Neutral Wires?
Working Principle of Overload Relay
Difference between Power Cables and Signal Cables
corroded tank
Cathodic Protection – Sacrificial Anodic and Impressed Current
Hybrid Solar Power System
Garage Door Roller Shutter
Capacitor Bank
What is a Capacitor Bank?
Motor Slip Calculation
Electrical Motor Terms and Concepts
Current Earth Leakage Circuit Breaker
Types of Earth Leakage Circuit Breaker
Electrical Maintenance Engineer's Biggest Enemy
Electrical Components Overheating – Causes, Troubles, Prevent
Difference Between Circuit Breaker and Fuse
Various Types of Sensors Used in Water Treatment Plant
Various Types of Sensors used in Water Treatment Plant
D.C Tachogenerator Principle
Compounded DC Generator
Compound Generators
Types of Control Valves Noise
Plant Engineering Drawings
Piping and Instrumentation Drawing (P&ID) Tutorials – Part 1
Explosive Limit in Fire and Gas System
What is an Explosive Limit? – Lower Explosive Limit (LEL)
What is Ground
What is Ground, and importance of a Grounding System?