Reading: Captive Power Plant Trip Root Cause Analysis
Inst Tools > Blog > Root Cause Analysis (RCA) > Captive Power Plant Trip Root Cause Analysis
In this article, we will learn the captive power plant (CPP) trip root cause analysis. It is equipped with Frame-V Gas Turbine Generators.
Last updated: November 3, 2021 7:09 pm
The captive power plant (CPP) in the Onshore Gas Terminal (OGT) is set up to meet the power and steam requirements of the process and utility systems in the OGT complex.
Incident SummaryProbable CausesObservationsRoot Cause AnalysisMeasures to avoid such incidents in futureDocuments and Reports
The CPP is equipped with two M/S GE make Frame-V Gas Turbine Generators (GTG) of capacity 20.5 MW each; both the GTGs would be in operation each operating at part load as per the design philosophy.
The hot flue gas from each GTG is diverted to the respective HRSG (Heat Recovery Steam Generator) to produce process steam.
Each HRSG is equipped with a supplementary firing system and is designed to meet the peak load of 66 TPH of High-Pressure steam generation (36 Kg/cm, 256 Deg°C).
Both the HRSGs would be operating at part load. CPP is also equipped with fuel gas conditioning skids to ensure the quality of fuel gas used in GTG.
Recently the Captive power plant has tripped on —DATE— at 05.55 hrs on electrical protection (earth fault).
Incident Summary
On —date— Gas turbine-2 which was running at normal operating conditions tripped due to electrical protection generated from generator relay protection panel at 05.55 hrs lead to production loss.
The generator is provided with electrical protection on stator earth fault of 1N>1. EDG failed to start automatically due to PMCC-1 (Emergency PMCC) normal incomers didn’t trip during a blackout.
The incomers were switched on manually and the Emergency diesel generator was started.
Probable Causes
  1. Actual earth fault in generator stator winding.
  2. Malfunction of the current sensing device.
  3. Transient earth fault in the downstream electrical system.
Observations
  1. The generator relay protection given a trip command on electrical  protection (stator earth fault 1N> 1)
  2. The trip valve setting in  generator  protection  relay (MICOM) for stator earth fault is 5Amps with 600 milli seconds delay.
  3. The actual current sensed by the protection system was 88Amps.
  4. The  generator  panels  were  physically  inspected  for  any  fault  and  there  is  no significant evidence for short circuit founed.
  5. The CT was physically checked and found to be good.
  6. Generator differential protection relay not operated.
  7. 11KV bus differential relay is not operated.
  8. No alarm/tripping indication in downstream electrical distribution systems
Root Cause Analysis
  1. From  the  observations  above,  it  is  derived  that  the  probable  causes  1 and  2 mentioned above is not the reason for this trip.
  2. Further to ascertain the healthiness of the generator stator,  the generator excitation was kept on manual  and excitation voltage was slowly and gradually increased up to
  3. 11KV and there is no abnormality observed.
  4. As there no alarm/tripping  in the downstream electrical distribution system, the exact point of fault remains uncertain. The trip may be due to transient fault initiated from generator downstream electrical system.
  1. Relay calibration and testing to be carried out in complete electrical system.
  2. Over  all  Relay  coordination  study  for  longest  chain  in  OGT  (CPP  substation  to substation)  needs to be carried  out and final  relay setting  recommendation  of the study is to be implemented.
  3. Through inspection for possible entry for rodents in the entire electrical  system to be carried out
  4. Regular pest control in all electrical systems to be carried out.
Mark Vie system sequence of events
  • Trip Valve Principle
  • Erratic Radar Level Gauge
  • Basics of Alarms and Trip
  • Choked Control Valve Trim Cage
  • Amine Pump Root Cause Analysis
Amine Pump Trip – Root Cause Analysis
Pump 3-monthly Seal Leaks threaten entire Plant Shut down Indefinitely
Thermocouple Extension Lead Problem
Root Cause Analysis for Plant Trip Due to Work on Incorrect Tag
Multistage Flash Drums Erratic Level Readings
Centrifugal Compressor Outage Reduced – Root Cause Analysis
Magnetic Flow Meter Liner Damaged and Winding Burnt
Root Cause Analysis – Burst Transformers and 11 kV Input Breakers
Erratic Radar Level Gauges Delays a Refinery Commissioning
Failed Letdown Valve Shuts down a Urea Plant Several Hours
Carbamate Plunger Pump Packing Problems Eliminated
Thermowell Shank to Flange Repeat Weld Leaks
Panel and Field Pneumatic Controller’ Bumpless Transfer Issues
Cooling Tower fan FRP fan blades saves and saves
Bently Nevada Proximity Probe
Root Cause Analysis for Vibration Probe Not Responding
Control Valves - Repeat Actuator Diaphragm Bursts
Control Valves – Repeat Actuator Diaphragm Bursts
Glass Bottle Level Gauge
Antifriction Bearings Caused Machine Changeovers Posed Outages
Flanged Rotameter
Flanged Rotameter Caused Pipe Weld Cracks and Gives Wrong Readings
Leaky Boiler Drum Level Switch
Leaky Boiler Drum Level Switch Stops NH3 Plant Commissioning
Root Cause Analysis on Hunting of Control Valves
Heat Exchanger Root Cause Analysis
Heat Exchanger Root Cause Analysis (RCA)
BP Refinery Explosion
Learnings from the BP Refinery Explosion at Texas City
S7 Organizational blocks
Siemens PLC Tia Portal – OB100 Start-up Organization Block
AI Technology in Video Surveillance
Next-Generation Security Surveillance Systems – AI Technology
Synchronous Motor Is Not Self Starting?
MOS Digital Integrated Circuits Objective Questions
water filter level control system
Practical Process Control System Questions & Answers – 6
Flapper nozzle system
Flapper Nozzle Questions
Calculate the 0%, 50%, and 100% Calibration Points