Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: Pressure Reducing and DeSuperheating Station (PRDS)
Share
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Process > Pressure Reducing and DeSuperheating Station (PRDS)

Pressure Reducing and DeSuperheating Station (PRDS)

In Process Industry, the Superheated Steam Temperature and Pressure are reduced in the Pressure Reducing & DeSuperheating Station (PRDS).

Last updated: September 28, 2022 3:31 pm
Shiv Kumar
Process
1 Comment
Share
9 Min Read
SHARE

The superheated steam is generated at the Boiler and is distributed to various locations in the plant through a steam piping network.

Contents
Pressure Reducing and Desuperheating StationComponents of the PRDSOperation of PRDSPressure Loop Control SystemTemperature Loop Control SystemApplications of PRDS stations

In the process industry, there are several auxiliaries at different locations that require different steam parameters (Steam pressure & temperature).

According to their application in the Process Industry requirement, the Superheated Steam Temperature and Pressure are reduced in PRDS.

PRDS is known as the Pressure Reducing and Desuperheating System.

Pressure Reducing and Desuperheating Station

The PRDS usually has two types 

  • Split Type PRDS: In split type, two separate Steam Inlets are provided for the Pressure Reducing Stations and De-Super heater (DSH).
  • Combined Type PRDS: In the Combined type, the Pressure Reducing Station and De-Super heater (DSH) are at the same Steam Inlet.
Pressure Reducing and Desuperheating Station (PRDS)
Split Type PRDS

As the name implies, the Pressure Reducing and Desuperheating Station (PRDS) is a unit that conditions steam from a Main System (Boiler) to an Auxiliary Steam source of supply by reducing steam Pressure and Temperature using a Pressure Control Valve and a Temperature Control valve.

 After Pressure Reduction is done, the steam is then allowed to pass through the Desuperheating station to lower the temperature of the steam to the required value.

Components of the PRDS

PRDS is a combination of Mechanical and Instrumentation components.

  • Pressure Control Valve: It is known as a Pressure Reducing Valve or Pressure Control Valve. The Pressure Control Valve is the main component of the PRDS System. This is used to reduce the pressure of the superheated steam.

In General, the Control Valve is Known as the Final Control Element. And it is the heart of the Instrumentation Loop.

  • Temperature Control valve: it is also known as a De-Super heater or Attemperator, This unit reduces the temperature of the super-heated steam that consists of  Flow  Nozzles, through which atomized water is sprayed to steam to reduce the temperature.
  • Positioner: A Positioner in a Control Valve is a device that interfaces with the PID controller and senses the exact position of the control valve Stem. The Positioner sends the Instrument Air to the Actuator so that the position of the valve stem changes accordingly.
  • Flow Meter: Flow Meter is a device that measures the exact value of the fluid flowing through it. Usually, the flow is measured in Tons Per Hour (TPH).
  • Temperature Element: The Temperature Element senses or detects the hotness or coolness of the body.
  • Pressure Gauge: It is a Pressure sensing device, it only displays the pressure of the fluid flowing through the line.
  • Pressure Transmitters: This Pressure Transmitter Transmits the Pressure Value as the Process Variable (Measured value) to the controller.
  • Temperature Gauge: It is a Temperature sensing device, it only displays the temperature of the fluid flowing through the line.
  • Temperature Transmitter: This Temperature Transmitter (TT) receives the signal value from the Temperature Element (RTD/TC), and transmits the Measured Value as the Process Variable to the controller.
  • Isolation valves: These valves are installed before and after the Control Valve to isolate the fluid flow when the control valve is in maintenance.
  • Safety Valve:  The Safety Valve in the System protects the whole system, when the pressure exceeds the preset limit, the valve opens the body and vents the excess pressure into the atmosphere.

A safety Valve is the most Essential Component in High-pressure Operation.

Operation of PRDS

In a Pressure Reducing and Desuperheating control system, there exist two loops,

  1. Pressure Loop Control System
  2. Temperature Loop Control System

Pressure Loop Control System

Components of Pressure Loop Control System:

This system includes a

  • Pressure Control Valve (PCV),
  • Pressure Transmitter (PT),
  • PID Controller,
  • I/P Converter,
  • Pressure Gauges (PG), etc.
Pressure Loop Control System

The Pressure Control Valve (PCV) in the Pressure loop control system reduces the pressure of the superheated steam by opening the Valve.

The Pressure Value to be reduced is given as a set point to the controller. The Pressure Transmitter senses the outlet Steam Pressure and sends the proportional signal to the PID controller as a Measured value.

The PID controller then compares the Process Variable (Measured Value) received from the Pressure Transmitter with the given SetPoint (SP) and generates an error signal which is then given to the Positioner of the Pressure Control Valve (PCV).

The Control Valve opens and relieves excess Pressure until the Pressure reaches the desired value. When the Steam Pressure reaches the Desired Set Point the control valve gets closed and prevents the further release of Pressure after normal conditions have been restored,

i.e. Process Variable (PV) must be equal to SetPoint (SP).

PV=SP

The Steam Inlet Isolation Valve and Outlet Isolation Valve of the Pressure Control Valve (PCV) are controlled with two remotely operated motorized valves for isolating the Pressure Control Valve during maintenance.

Temperature Loop Control System

Components of Temperature Loop Control system:

Temperature Loop Control System

This System includes a

  • Temperature control valve (TCV),
  • Temperature Element (TE),
  • Temperature Transmitter (TT),
  • PID Controller,
  • I/P Converter,
  • Temperature Gauge (TG).
  • The water strainer is provided at the inlet to prevent the entry of dust particles into the Temperature Control Valve & Spray nozzles.
  • The Pressure Gauge at the inlet indicates the pressure of the atomized spray water.
  • The Temperature Control Valve (TCV) regulates the quantity of the water to be sprayed.
  • The water inlet and outlet isolation valves are used to isolate the Temperature Control Valve, whenever maintenance of the control valve is to be carried out.
  • The Bypass valve allows spray water flow to continue whenever the Temperature Control Valve is under maintenance or becomes inoperable.
  • The non-return valve prevents the backflow of steam into the water pipeline.

The Attemperation water is sprayed at high velocity through Spray nozzles in an adequate quantity. To reduce the temperature of superheated steam to the required temperature.

The Temperature element (TE) senses the outlet Steam Temperature and gives a proportional current signal to the PID controller via the Temperature transmitter (TT).

The PID controller then compares the Process Variable (Measured Value) received from the Temperature transmitter (TT) with a given SetPoint (SP), generates an error signal, and is then given to the Positioner of the Temperature Control Valve (TCV)

This  valve opens accordingly and sprays atomized water through the spray nozzle until the steam temperature reaches the set value, and re-closes to prevent the further spray of water after normal conditions have been restored,

i.e. Process Variable (PV) must be equal to SetPoint (SP).

 PV=SP

DeSuperheater has two types:

  1. Integral type DeSuperheater: In this type, the DeSuperheater is built with the actuator and a spray nozzle.
  2. Non-Integral type DeSuperheater: In this type DeSuperheater and spray nozzle are separate units.

Usually, all power plant uses Split type and Integrated-type PRDS

Applications of PRDS stations

  1. PRDS for process heating applications in sugar, food, textile, paper, etc.
  2. Deaerator, Ejector PRDS for the boiler.
  3. Turbine By-pass PRDS.

The steam required for the process (Sugar Industries, Distilleries) is called exhaust steam which is at low temperature and pressure.

 Note: Inlet Steam is the Main steam and outlet Steam is Exhaust Steam

A Safety Valve is used at the outlet of the system to ensure that the pressure does not exceed the preset limit. When the pressure exceeds the preset limit the safety valve opens and relieves the excess pressure to the atmosphere, when the pressure reaches its preset limit the Valve gets closed.

Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Refrigeration Compressor Turbine Not-tripping when needed Trip
143 Process Control Terms and Glossary – Questions Answers
Cartridge Filters
Superheated Steam Temperature Control System
Difference Between Single-stage and Multi-stage Compressor
Introduction to Wastewater Treatment Works and Pumping Station
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
1 Comment
  • Tejas Gandhi says:
    July 30, 2024 at 11:54 am

    Fantastic article…Thanks for sharing such an amazing content with us.Good job.Keep it up.

    Reply

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

Water Treatment Plant
Reciprocating Compressors
Bucket Steam Trap
What is EDI in a Water Treatment Plant? – Electro deionization
Heat Exchanger Root Cause Analysis (RCA)
Hydraulic System
Components of Water Treatment Plant
Process Control High Level Alarm Fault Analysis

Keep Learning

Filters in Compressors

Filters in Compressors

Impulse Steam Trap

Impulse Steam Trap

Precoat Filters

Precoat Filters

CO2 Absorber Graphics in DCS

CO2 Absorber Corroded Wall Thickness & Weld Building

Water Treatment Plant

Difference Between ETP, STP, and WTP – Treatment Plants for Water

Steam Turbine Driven Centrifugal Compressors Leak due to Broken Instrument

Discharge Head 3‑monthly leaks of Steam Turbine Driven Centrifugal Compressors

What is Heat Pump Water Heater?

What is Heat Pump Water Heater?

Compressor IP Case Discharge Temperature Gradually Increases

Compressor IP Case Discharge Temperature Gradually Increases

Learn More

SCADA Run

PLC Based Industrial Conveyor Ladder Logic

Advantages and Disadvantages of Network Topology

Advantages and Disadvantages of Per Unit System

Process Control Instrumentation Terms Glossary

Process Control Instrumentation Glossary

Single layer PCB

Step-by-Step Guide: How PCBs are Manufactured from Start to Finish

Dual-junction thermocouple circuit

Find Thermocouple Ouput Voltage

Chromatography Questions & Answers

Chromatography Questions & Answers

displacer level transmitter cylindrical weighs

Displacer Level Transmitter 5-point Calibration

Component De-rating

Component De-rating in Control Systems

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?