This is a PLC Program to control motor speed using a VFD drive. Learn the PLC programming with real-time industrial examples.
Motor Speed ControlProblem DiagramProblem SolutionList of inputs and outputsPLC Ladder diagram to control motor speedPLC Program ExplainedResult
Motor Speed Control
A VFD drive controls the motor speed. The VFD can be controlled remotely by using PLC/DCS systems.
The PLC has to give set point for VFD drive to control the motor speed, this can achieved either automatically from the PLC or by the operator action from the HMI.
According to set point value, PLC will control the drive speed and VFD drive finally controls the motor speed. Write PLC program for this application using ladder language.
Problem Diagram
PLC Program to Control Motor Speed using VFD Drive
Problem Solution
For controlling we used here PID function so according to set point it will automatically control drive speed.
As per name, PID controller consists main three coefficients: proportional, integral and derivative.
For VFD drive control explanation, we will use setpoint for drive from the PLC (50RPM). PID function will maintain the speed as per setting.
According to set point PID will generate output and the VFD drive receives the PLC input and maintains the required motor speed.
Here we are considering 4-20mA signal for VFD drive input (required speed setpoint from PLC) and feedback from the drive is also 4-20mA which in-turn connected to PLC to display the actual speed in HMI.
Digital Inputs/Analog Inputs
  • PID Enable :- I0.0
  • Manual Enable :- I0.1
  • PID reset :- I0.2
  • 4-20mA signal form drive :- IW64
Digital outputs/Analog output
  • Analog output for drive :- QW80
M memory
  • Set point PID :- MD500
  • PID output for drive :- MW762
  • Run mode by startup :- M0.3
Motor Speed Control
PLC VFD Drive
PLC VFD Motor Speed
PLC Speed Control VFD
Motor Control PLC VFD
VFD Motor Control
PLC Speed Control
For this application, we use S7-1200 PLC and TIA portal software for programming. We can implement this logic by using other PLC also.
Network 1:
In network we configured standard parameters for PID function.
  • “Drive PID”.sRet.r_Ctrl_Gain:- saved proportional gain or P gain for PID (1.0).
  • “Drive PID”.sRet.r_Ctrl_Ti:-Saved integral time or I gain for PID (20s).
Network 2:
“Drive PID”.sRet.r_Ctrl_Td:-Saved derivative time or D gain for PID (0s).
Network 3:
Here we have taken drive PID max output limit and minimum output limit. We have considered here max limit for PID output 100 and minimum limit is 0.
Network 4:
Sampling time of the PID_Compact instruction r_Cycle is determined automatically and usually equivalent to the cycle time of the calling OB. Consider 0.1s for this application.
Network 5:
When PID enable (I0.0) is pressed PID block will be executed. As per SET point (MD500) it will generate output (0-27648) and according to speed drive will give feedback (IW96) to PID.Manual enable (I0.1) is for manual operation and PID reset (I0.2) is for resetting the PID.
Network 6:
Activate Mode after CPU restart If sb_RunModeByStartup = FALSE, the controller will remain inactive after a CPU startup. After a CPU startup and if sb_RunModeByStartup = TRUE, the controller will return to the most recently active operating mode.
Network 7:
When PID enable switch (I0.0) is pressed, Drive (Q0.0) will be enabled.
Network 8:
Moving PID output (MW762) to Analog channel (QW96) of the expansion module of the PLC.
Set 50 RPM form the HMI and enable PID so PID will generate output according to set point. After getting output from PID drive will run on 50 RPM and it will generate mA according to speed. After reaching set point PID will maintain 50 RPM.
In above application we have considered S7-1200 PLC. There are two on board analog inputs (Voltage) in this CPU. So for this application we need consider one more expansion module which has analog input facilities with current range selection.
In TIA portal software, select analog output type > current and range > 4-20mA
Note :- Above application may be different from actual application. This example is only for explanation purpose only. We can implement this logic in other PLC also. This is the simple concept of drive speed control using PID.
All parameters considered in example are for explanation purpose only, parameters may be different in actual applications.
For PID we need to configure so many parameter, here we configured parameters only for our application. Hence all parameters are not configured here.
Result
PLC Simulation to Control Motor Speed using VFD Drive
Author: Bhavesh
  • PLC Analog Signals Wiring
  • Analog Input Card Resolution
  • PLC Interview Questions
  • Sensor Scaling in PLC
  • PLC Output Types
PLC Ladder Program for Automatic Car Wash using Siemens TIA Portal
Data Handling Instructions in PLC Programming
Ladder Logic Example with Timers
2 Comments
  • Pol Francesco says:
    June 1, 2020 at 8:25 pm
    very good
  • imran says:
    May 18, 2022 at 4:44 pm
    please, i have a question. what is MD? what is md500? md763?
Toggle Switch & Sensor: Conveyor and Puncher PLC Program
PLC Programming Videos
What is PID Controller?
Troubleshoot the Status of a PLC Via CPU Indicators
PLC, DCS, and ESD Marshalling Cabinet Checks
Parking Lights PLC Program Explained with Video
PLC Automatic Door Control System – Programming Example
Feedback Monitoring in Safety PLC
Online and Diagnostics of Siemens PLC
How to Use Diagnostic Buffer for SIEMENS PLC?
What is Multi-touch Technology
What is Multi-touch Technology? – Industrial Automation
TIA Portal MOVE Instruction
MOVE Instruction in PLC – What You Need to Know?
PLC Handbook
PLC Handbook
Digital Output Card With Relay and Wet Contact
PLC Digital Inputs
PLC Digital Input and Digital Output Modules
PLC Program for Password Management using Structured Text
80+ PLC MCQ
80+ PLC MCQ Questions
Fire and Gas Systems Loop Checks
Fire and Gas System Loop Checks Procedure
ISA and SAMA diagrams
What is SAMA Diagram?
Types of Boiler Drought
What is a Boiler Draught System? – Purpose, Types, Advantages
What is a Fuse
What is a Fuse ?
Parallel Operation of Alternators
Fluidic Systems Objective Questions
Bourdon Tube Gauge Spiral Spring
What is the Purpose of Bourdon Tube Gauge Spiral Spring?
What is a Photoelectric Sensor
What is a Photoelectric Sensor?