Reading: PLC Crane Movement Control with Limit Switches
Inst Tools > Blog > PLC Tutorials > PLC Crane Movement Control with Limit Switches
Learn how to control crane movement with limit switches using the CX-Programmer software in the OMRON PLC system.
Last updated: September 30, 2024 4:50 pm
6 Min Read
This article discusses the PLC program to control crane movement using the OMRON PLC in CX-Programmer software. In this PLC program, the Trolley Part of the Crane can move Left or Right and the Hoist Part of the Crane can move Up or Down. The movement of the Trolley Crane and Hoist Crane must be limited so as not to exceed the safety limit using the Limit Switch. This system allows the Crane to be controlled Up or Down and Left or Right by providing a safety function.
Program ObjectivePLC I/O AddressingPLC Crane Movement Control
Program Objective
The PLC program has 4 main buttons:
  1. The UP_BUTTON (0.05) is used to move the Hoist Crane Up.
  2. The DOWN_BUTTON (0.04) button is used to move the Hoist Crane Down.
  3. The LEFT_BUTTON (0.02) is used to move the crane to the Left.
  4. The RIGHT_BUTTON (0.03) button is used to move the Crane to the Right.
  5. The EMERGENCY (0.06) button is used to Stop all Crane movement in case of emergency but does not turn OFF the system.
Limit Switch is used as a safety system to prevent the crane from moving beyond the safety limit.
  • LS_UP (0.09) is used to limit the highest position of the Hoist Crane, preventing the Hoist Crane from moving too High.
  • LS_LEFT (0.07) is used to limit the crane’s reach when it moves too far to the Left.
  • LS_RIGHT (0.08) is used to limit the crane’s reach when it moves too far to the Right.
PLC I/O Addressing
CommentInput (I)Output (Q)Memory Bits
START_SYSTEM0.00
STOP_SYSTEM0.01
LEFT_BUTTON0.02
RIGHT_BUTTON0.03
DOWN_BUTTON0.04
UP_BUTTON0.05
EMERGENCY0.06
LS_LEFT0.07
LS_RIGHT0.08
LS_UP0.09
OUT_LEFT 100.00
OUT_RIGHT 100.01
OUT_DOWN 100.02
OUT_UP 100.03
SYSTEM_ON  W0.00
IR_LEFT  W0.01
IR_RIGHT  W0.02
IR_DOWN  W0.03
IR_UP  W0.04
RUNG 0 (START SYSTEM)
In this Rung, when the START_SYSTEM (0.00) button is pressed, the memory bit SYSTEM_ON (W0.00) will be in the HIGH state. Because the KEEP (011) instruction is used, the memory bit SYSTEM_ON (W0.00) remains in the HIGH state even though START_SYSTEM (0.00) button has been Released.
The memory bit SYSTEM_ON (W0.00) will become a LOW state if the STOP_SYSTEM (0.01) button is Pressed.
Trolley and hoist PLC control
RUNG 1 (LEFT BUTTON)
In this Rung, when the memory bit SYSTEM_ON (W0.00) is in the HIGH state and the LEFT_BUTTON (0.02) button is Pressed, the memory bit IR_LEFT (W0.01) will be in the HIGH state.
RUNG 2 (RIGHT BUTTON)
In this Rung, when the memory bit SYSTEM_ON (W0.00) is in the HIGH state and the RIGHT_BUTTON (0.03) button is Pressed, the memory bit IR_RIGHT (W0.02) will be in the HIGH state.
RUNG 3 (DOWN BUTTON)
In this Rung, when the memory bit SYSTEM_ON (W0.00) is in the HIGH state and the DOWN_BUTTON (0.04) button is pressed, the memory bit IR_DOWN (W0.03) will be in the HIGH state.
RUNG 4 (UP BUTTON)
In this Rung, when the memory bit SYSTEM_ON (W0.00) is in the HIGH state and the UP_BUTTON (0.05) button is pressed, the memory bit IR_UP (W0.04) will be in the HIGH state.
RUNG 5 (LEFT OUTPUT)
In this Rung, Output OUT_LEFT (100.00) will be ON when the NO contact of memory bit IR_LEFT (W0.01) is in the HIGH state. The OUT_LEFT (100.00) output will be OFF if the EMERGENCY (0.06) button is Pressed or if the NC contact of Limit Switch LS_LEFT (0.07) is in the HIGH state.
OMRON PLC crane automation
RUNG 6 (OUTPUT RIGHT)
In this Rung, Output OUT_RIGHT (100.01) will be ON when the NO contact of memory bit IR_RIGHT (W0.02) is in the HIGH state. The OUT_RIGHT (100.01) output will be OFF if the EMERGENCY (0.06) button is Pressed or if the NC contact of Limit Switch LS_RIGHT (0.08) is in the HIGH state.
RUNG 7 (OUTPUT DOWN)
In this Rung, Output OUT_DOWN (100.02) will be ON when the NO contact of memory bit IR_DOWN (W0.03) is in the HIGH state. The OUT_DOWN (100.02) output will be OFF if the EMERGENCY (0.06) button is Pressed.
RUNG 8 (OUTPUT UP)
In this Rung, Output OUT_UP (100.03) will be ON when the NO contact of memory bit IR_UP (W0.04) is in the HIGH state. The OUT_UP (100.03) output will be OFF if the EMERGENCY (0.06) button is Pressed or if the NC contact of Limit Switch LS_UP (0.09) is in HIGH state.
  • PLC Program for Mailbox with Counting
  • Dosing Pump PLC Programming Logic
  • PLC Programming based on Logic Circuit
  • Schneider Electric PLC Timer Problems
  • PLC Programming 3 Motors with Priority
PLC Logic Functions
PLC Program for Boolean Expression
PLC Compressor Control Ladder Logic
Example of Flip-Flop PLC Program for Lamps Application
Positive and Negative Edges using Statement List Language
Basic PLC Alarm Programming Example
Types of Digital Outputs in PLC
Push button Motor PLC Logic
PLC Program for Entry and Exit Control of Car Parking
Example of PID Control Instruction
How to Configure PID in Siemens PLC?
Namur Digital Input Card
What is Namur Digital Input Card?
Comparison of Proportional Integral Derivative Controllers (PID)
DCS Marshalling Cabinet
Traces in TIA Portal
What is Trace Function in Tia Portal?
Introduction to GOC controllers
Mitsubishi Electric GOC Controllers
PLC Program for Valves
PLC Pump Permissive Interlocks
Allen-Bradley PLC Program
Sourcing output module in PLC
Which Connection is Best for PLC? – Sinking or Sourcing
Capacitive Transducers Objective Questions
Pressure-sensing level transmitter
Moving Pressure Sensing Level Transmitter from Top to Bottom
Single-Phase Full Wave AC-DC Converter Quiz
BLDC Motor Vs AC Induction Motor
Instrument Air Quality
Feedforward Control Questions & Answers
Differences between Watts and Volt Amps