Reading: Ladder Logic for Stair-Case wiring using Toggle Switches
Inst Tools > Blog > PLC Tutorials > Ladder Logic for Stair-Case wiring using Toggle Switches
Last updated: March 4, 2021 3:22 pm
2 Min Read
Design Ladder Logic for Stair-Case wiring using two Toggle Switches in programmable logic controllers (PLC).
  • I0.0 & I0.1 : Input toggle switches.
  • Q0.0 : Output signaling device(bulb, motor etc.)
This ladder logic of stair-case wiring works on the X-OR logic i.e, Y is (A.B^) + (A^. B)
Suppose initially only I0.0 is pressed and I0.1 remains open physically as shown then the upper branch of rung 1 goes TRUE  and Q0.0 gets energized.
Now , if I0.0 is also pressed then it will make its interlock N-C contact I0.1 to go open and as a result Q0.0 de-energizes .
Again, if switch I0.0 is pressed it will also make its interlock contact I0.0 in parallel branch to go again N-C , which in turn makes the parallel branch logic true and Q0.0 again energizes but if the I0.1  input is also pressed again the logic goes FALSE and Q0.0 again de-energizes. This is the basic concept of an X-OR logic gate.
Motor Start Stop Logic using PLC
PLC Program for Blinking Lamp
Multi Way Switches using PLC
How to use PLC Sub Routines
Down Counter PLC Logics
PLC Programming Example with Pushbutton and Motor
How to Use Diagnostic Buffer for SIEMENS PLC?
Statement List (STL) to Find Highest Value
PLC Trainer Demo Download
Produced Tags and Consumed Tags in Studio 5000
Motor Speed Control using VFD and PLC Programming
Schneider Electric PLC Timer Problem: Vacuum Cleaner
PLC Programming for Baking with Auto and Manual Modes
Extended Timer Logic in PLC
What is a Floating License? – Automation Software Systems
Split Range Control Application using PLC Ladder Logic
Difference Between Industrial Computer (IPC) and Normal Computer (PC)
Single-acting Pneumatic Cylinder operation with Limit Switch
Single-acting Pneumatic Cylinder Operation with Limit Switch
Learn PLC in Hindi
Learn PLC in Hindi
Top 100 PLC Objective Questions and Answers
PLC Program with 2 Toggle Switches and 4 Motors
How to set password in Siemens HMI
How to Password Protect HMI in Siemens TIA Portal?
how-a-plc-do-the-scaling-for-a-sensor
How a PLC do the Scaling for a Sensor ?
SCADA Graphics
What is SCADA ? How does SCADA Works ?
Observer Systems
Fieldbus Pressure Transmitter Configuration
Foundation Fieldbus Pressure Transmitter Configuration
Industrial Electronics Objective Questions and Answers
principle of time base generator
Time Base Generator
RTD lead resistances Wiring
Resistance Temperature Detectors Working Principle
Wet Dust Suppression system
Wet Dust Suppression System
Control of the Effects of Disturbance Signals by Use of Feedback
Basics of Thyristor
Basics of Thyristor