Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: Hunting of Control Valves
Share
Notification Show More
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Root Cause Analysis (RCA) > Hunting of Control Valves

Hunting of Control Valves

The control valve started hunting and not operating properly i.e. command vs feedback error and this problem led to production losses.

Last updated: August 6, 2023 2:09 pm
vicky
Root Cause Analysis (RCA) Control Valves
No Comments
Share
6 Min Read
SHARE

Control Valve is one of the most important equipment of a plant. Control of pressure, flow, temperature, level, and many other quantities is done using this control valve.

Contents
Hunting of Control ValvesFault Tree Analysis:Root Cause AnalysisFindings in the workshop after opening positioner

Today in this article we will discuss one incident in which a new industry was observing failure in many control valves one by one which led to process upset many times.

Hunting of Control Valves

Instrument Engineers of a well-known new industry were facing a serious problem of abnormal operation of various control valves across different plants and different sections of the whole industry.

The problem was that the control valve started hunting and not operating properly i.e. command vs feedback error. This led to production losses and sometimes tripping of the whole plant due to disturbance of various parameters like pressure, flow, temperature, or level.

Some of the reasons for the hunting of the control valves were:

  1. The body of the valve gets stuck
  2. Actuator passing issue
  3. Low air pressure setting from the air filter regulator
  4. Instrument Air tube leak
  5. Instrument Air tube choke
  6. Instrument Air pressure fluctuations
  7. Problematic positioner

Let us deep dive into this problem and see how the Instrument engineer solved the stated problem of control valve hunting.

Instrument engineers carried out a fault tree analysis. Let us have a look at the fault tree analysis.

Fault Tree Analysis:

Fault tree analysis was made for control valve hunting. Fault tree analysis is shown below:

Hunting of Control Valves

As seen from the above fault tree analysis, various causes were identified for the problem statement “Control valve hunting randomly leading to process disturbance”.

Various reasons were taken into consideration as seen from the above fault tree analysis:

  • The body of the valve gets stuck
  • Actuator passing issue
  • Low Instrument Air pressure set from air filter regulator
  • Instrument Air tube leak
  • Instrument Air tube choke
  • Instrument Air pressure fluctuations
  • Problematic positioner

The final conclusion from the fault tree analysis was that the positioner of the control valve was having the issue. Let us see what all things were checked and how this conclusion was made.

Root Cause Analysis

Root Cause Analysis for Control valve hunting randomly leading to process disturbance:

When the Instrument Engineers visited the field to check various control valves having the same problem, they did the following activities to identify the root cause:

  1. The instrument team gave direct air to the control valve’s actuator. This was done to verify whether the control valves are getting stuck in the body or not. But all the control valves were operating smoothly when checked through direct air.
  2. Also, the instrument team checked the condition of the actuators. The actuators were not passing.
  3. The pressure setting of all the air filter regulators was checked. The setting on the air filter regulator was as per the air pressure requirement by the control valve as mentioned on the tag plate.
  4. All the instrument air path was checked thoroughly. No leakage was found.
  5. Also, the instrument air tube was checked for choking. No tube was found in choke condition.
  6. Instrument air pressure was monitored for a few hours and also at different time intervals. But the instrument air pressure was found steady.
  7. The instrument team checked the positioner’s output. The output air from the positioner to the actuator was fluctuating (verified through the gauge given on the positioner). Hence instrument team removed the positioner and opened the positioner in the workshop.

Findings in the workshop after opening positioner

After opening the positioner, everything was found intact. No physical damage was found in the positioner. After disassembling each and every component of the positioner, one strange thing was observed. The I/P’s air filter was having foreign material deposited on it.

A similar observation was found in many other positioners. So, the instrument team simply replaced the I/P’s air filter in one of the positioners and installed it back. The positioner started working fine.

Root Cause Analysis on Hunting of Control Valves

(Image only for reference)

After meetings and discussions, the instrument team came to the conclusion that the instrument’s air quality was not good. Foreign particles in the instrument air were causing the choking in the I/P filter. Because of this choking, the I/P couldn’t perform properly and hence cause the control valve to hunt.

After this incident, all the Instrument Air Headers were flushed and the operation department also took steps to improve the instrument air quality. After all air header flushing jobs, the control valve hunting issue was observed very rarely.

If you liked this article, then please subscribe to our YouTube Channel for Instrumentation, Electrical, PLC, and SCADA video tutorials.

You can also follow us on Facebook and Twitter to receive daily updates.

Read Next:

  • Quick Exhaust Valves
  • On-Off Valve Problems
  • Control Valve Design Factors
  • Solenoid and Motorized Valves
  • Control Valve Maintenance
Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Gas Cooler Re-tubing Done Successfully (Root Cause Analysis)
Pressure Switch Frozen Screwed Cover Extends the Plant Shutdown
Solenoid Valves Types, Principle & Animation
Effect of Differential Pressure on Control Valve Lift
Gearbox within week Failing Journal Bearing upset Plant Operations
Solenoid Valve Working Animation
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
Leave a Comment

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

Air Filter Regulator Working Principle Animation
Failing Weigh Feeders and Mechanical Variable Speed Drives (VSD)
Basic Steps and Procedure for the Repair of Control Valve
Basics of Control Valves
What is a Hydraulic Valve? and their Types
What is Instrument Air Manifold ?
How to Do Maintenance of Control Valve Which is Stuck in Field?
What is a Hydraulic Actuator ?

Keep Learning

Minimum Oil Circuit Breaker (MOCB) Spares & Service

Minimum Oil Circuit Breaker (MOCB) No Vendor Spares & Service

Valve Basics, Sizing, and Actuators Books

Valve Basics, Sizing, and Actuators Books

Selecting the Proper Failure Mode

How to Select Control Valve Failure Mode

Reformer Fan Bearing Change Times cut by 90%

Reformer Fan Bearing Change Times cut by 90%

Repeat Safety Valve Popping

Repeat Safety Valve Popping caused Urea Plant Shutdown

SMART Control Valve Positioner

Electronic Valve positioners

3-way solenoid valves control instrument air pressure

Solenoid Valve’s Energized or De-energized State ?

Butterfly Valve

Butterfly Valves Construction, Types, Stem & Bonnet Assembly

Learn More

Types of PLC

#14 PLC Best Practices – Restrict Third-party Data Interfaces

DCS Vs PLC

Difference between DCS & PLC Systems

Comparison of Absorption Chillers and Electric (Compression) Chillers

Difference between HVAC Absorption Chillers and Electric Chillers

Installation of Proximitor

Determine Lifting of Shaft using Proximity Sensor

What is a K Factor

Flow Meter K-factor and Calculations

DCS ESD Logic Overview Graphic Display

Automation System Process Functionalities

11 kV, 3.3 kV, and 400 V systems insulation resistance (IR) Problems

11 kV, 3.3 kV, and 400 V systems insulation resistance (IR) Problems

Radiochemical Questions and Answers

Liquid Scintillation Counters Questions & Answers

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?