Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: How Valve Positioners act as Cascade Control Systems in a Loop?
Share
Notification Show More
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Control Systems > How Valve Positioners act as Cascade Control Systems in a Loop?

How Valve Positioners act as Cascade Control Systems in a Loop?

Last updated: November 4, 2020 12:52 pm
Editorial Staff
Control Systems Control Valves
No Comments
Share
2 Min Read
SHARE

Explain how all valve positioners essentially act as cascade control systems in a loop, and why valve positioners generally improve control quality as a result.

Valve Positioners

How Valve Positioners act as Cascade Control Systems in a Loop?

Furthermore, examine this block diagram of an electronic (“smart”) valve positioner and comment on its own internal “control strategy” for achieving optimum positioning:

Answer:

Electronic valve positioners act as controllers of a sort by sensing stem position (PV), comparing that PV against the command value coming from the loop controller (the positioner’s SP), and finally generating its own pneumatic output signal to drive the actuator and move the valve to where it should be.

A potential problem with electronic positioners is the potential to mis-tune its internal control(lers), resulting in oscillations if the internal control is too aggressive and sluggishness if the internal control is not aggressive enough.

Read Next:

  • Pneumatic Valve Positioner
  • Control Valves Pre-Commissioning
  • How to Select a Control Valve?
  • Control Valve Calibration
  • Types of Valve Characteristics

Questions for you:

1. Comment on the “+” and “−” symbols shown in this diagram. Based on these symbols, determine the control action (direct or reverse) for each of the controllers.

2. Certainly, modern “smart” valve positioners promise superior control valve performance than mechanical valve positioners did. Can you think of any potential disadvantages of a smart valve positioner, especially after examining the block diagram in detail?

3. How exactly does a “smart” positioner sense the valve stem’s position?

4. For those who have studied control valve positioners, identify some of the special features offered by a “smart” positioner.

5. Predict the effect(s) of the nozzle plugging inside the positioner’s relay.

6. Predict the effect(s) of the travel sensor failing with a 0% (fully-closed) signal.

7. Predict the effect(s) of the pressure sensor failing with a 100% (full-pressure) signal.

Join the Discussion! Share your answers with us through below comments section.

Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Control Valve Recommended Practices for Harsh Process Conditions
What are Isolation valves? – Purpose, Types, Configurations
Certified Control Systems Technician (CCST) Questions
What is a Annunciator Panel?
Pneumatic Training Course – Download PDF
Commissioning Checklists for Industrial Automation Systems
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
Leave a Comment

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

Process Control Instrumentation Glossary
Control Room and Field Instruments Questions and Answers
How to Do Loop Checks During Plant Pre-Commissioning
UPS Selection Factors for a Control System
Burner Safety Logic for Initial Lighting
Foundation Fieldbus – Advantages, Limitations, Architecture
Basics of Ball Valves
Difference Between the Control Valve and Shut-off Valve

Keep Learning

Pilot operated Solenoid Valve Principle

How Pilot operated Solenoid Valve Works ?

Workstation Healthiness Checks

Workstation Healthiness Checks

Double-acting cylinder - 2

Fluid Power Systems

Water Treatment Control System

Waste Water Control System

Derivative Controller Response

Derivative Controller Principle

Valve Interlock

Valve Interlock

4 way Solenoid Valve Principle

What is a 4-way Solenoid Valve?

Split Range Control for Temperature Control Application

Split Range Control Working Principle

Learn More

Shut down valve

What is Shutdown Valve?

Working Principle of Water Chillers

HVAC Water Chillers Principle

Air Filter Regulator Working Principle Animation

Solenoid Valve Design

Solenoid Valve Selection Criteria

ORP Measurement

Basics of ORP Measurement

Concept of Interlocking in PLC

Concept of Interlocking in PLC

Types of Failures in Industrial Automation Systems

Types of Failures in Industrial Automation Systems

Why 4-20mA Standard is so popular

Why 4-20 mA Standard is so popular ?

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?