Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: How to Find the Correct Solenoid Valve Size?
Share
Notification Show More
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Solenoid Valve > How to Find the Correct Solenoid Valve Size?

How to Find the Correct Solenoid Valve Size?

In this article, we discussed how to find the correct solenoid valve size, selection criteria, and example valve sizing equation.

Last updated: October 17, 2023 1:53 pm
Editorial Staff
Solenoid Valve
No Comments
Share
8 Min Read
SHARE

When we speak about solenoid valve sizing, we refer to the amount of flow passing through the valve, also known as the flow factor (Kv).

Contents
Solenoid Valve SizingWhat is the Kv-value?Calculating the Correct Valve SizeExample Solenoid Valve SizingOther Selection Criteria for Solenoid ValvesOperation principleCircuit functionWe should also consider

This Kv-value is a measure of the flow rate for a given medium and pressure drop.

Solenoid Valve Sizing

Before choosing a solenoid valve, we need to know the flow rate to start to determine our choice for the correct valve for our application.

However, just knowing the Kv-value will not allow us to make the right choice all by itself. The circuit function, operating principle, IP rating, medium, pressure, and other selection factors play a significant role.

How to Find the Correct Solenoid Valve Size
Figure: Solenoid Valve

What is the Kv-value?

Our first step will be to determine what this value is, followed by how to calculate it. It is important to note that countries that use imperial units have a slightly different value, the Cv value.

The Cv value is calculated as the volume flow rate of water in gallons per minute at 60 degrees Fahrenheit at a pressure drop of 1 psi. Based on these values, Kv is 1.156 times Cv.

When choosing a solenoid valve, we use the Kv value rather than the pipe size or diameter of the pass-through. The Kv value can vary per valve, and the medium that flows through the valve is still the deciding factor.

Solenoid valves have a standard Kv-value assigned to them. This value represents the amount of water, which has a specific gravity of 1, which can pass through the valve at a pressure differential of 1 bar.

How to calculate valve size using Kv values - Tameson

Calculating the Correct Valve Size

The flow rate of a solenoid valve depends on the shape of the valve’s body (route the media flow takes) and the diameter of the orifice.

The orifice is the diameter of the hole that will be closed off in the valve. If the piping connections of the valve are large, often the orifice will be large as well.

A larger orifice will have greater flow. Besides the flow rate, there are other factors we should know before we can calculate our valve size. 

The first is specific gravity. This is more commonly known as the relative density of materials. We can define specific gravity (G) as the ratio between the weight of a substance and an equal volume of water at 4 °C. At this temperature, it has a density of 1.0 kg per liter. Therefore water has a specific gravity of 1.

We also need to know the inlet and outlet pressures to calculate the pressure drop. Suppose a water pipe in a house has a pressure of 1 bar. This pipe flows to the outside air or atmosphere, which has a pressure of zero bar. This pressure difference of 1 bar is what we call the pressure drop.

The valve we’ve connected to the pipe has a Kv-value of 3. At a pressure drop of 1 bar, the flow rate for this valve is three cubic meters per hour (Kv-value x pressure drop).

We can combine all these factors in the following mathematical equation:

mathematical equation solenoid valve sizing

Where:

Q = Flow rate [m3/hour]

dp = The differential pressure between the inlet and outlet [bar]

SG = Specific Gravity

Kv = Flow coefficient

Example Solenoid Valve Sizing

We will connect a solenoid valve in a farm which is connected to a milk transporting pipe. We need to calculate now the size of the solenoid valve we will choose.

We know the following: 

  • The pressure in the system before the valve is 2 bar. 
  • After the valve is a pipe with an outlet to atmospheric pressure.
  • Milk has a specific gravity of 1.035.
  • We need to pump through between 14 and 15 liters of milk per minute. 

We found a solenoid valve that might suit our needs. This valve comes with a Kv value of 1.25. Will this valve be able to give us the flow we need?

Using the calculation, we see the following: 

Example Solenoid Valve Sizing equation

We know now that this valve will give us 0.8992 cubic meters per hour.

If we calculate the liters per minute:

Example Solenoid Valve Sizing formula

This valve will give us 14.98 liters of milk per minute, which is perfect for our application. 

Other Selection Criteria for Solenoid Valves

Now we know that our valve has a flow rate suitable for us; we also need to know several other factors to determine if the solenoid valve is suitable for us. 

Operation principle

Solenoid valves come in three different operating modes: 

  • Direct operated 
  • Semi-direct operated 
  • Indirect operated 

Indirect operated valves need a minimum pressure differential of 0.5 bar for proper operation. This gives the advantage that indirectly operated valves can control large flows with a relatively small coil, thereby reducing energy consumption.

Our system works with a pressure differential of 2 bar and has a relatively large flow.

Circuit function

There are various circuit functions available, 2/2-way, 3/2-way, and more. A 2/2-way ​​valve has two ports (inlet and outlet) and two open and closed positions.

For our application, we need a relatively simple operation with an inlet and outlet, so the 2/2 way valve is perfect.

We also need the valve to open only at the right moment, which means a valve that is closed as standard, or normally closed (NC).

We should also consider

The below are the basic parameters

Pressure

2 bar for our system.

Voltage and Response Time

The response time depends on the construction of the valve, the coil properties, the atmospheric pressure, and the medium’s viscosity.

The response time of DC valves is slower than AC valves. Direct operating valves are faster than indirect valves in most cases.

​IP Rating (Ingress Protection)

Indicates the degree of protection against access to hazardous parts and ingress of water, dust, etc. We need a valve that can withstand washing down and steam cleaning, so a high IP rating such as ​​IP69K.

Once we know all these factors, we can rest assured that the solenoid valve we choose is the correct one for our application.

Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Two Solenoid Valves Working Principle
What is a 4-way Solenoid Valve?
3 Port 2 Position Direct Acting Solenoid Valve Working Principle
Solenoid Valve Troubleshooting Tips
Difference between AC and DC Solenoid Valves
Solenoid Valve Working Animation
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
Leave a Comment

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

DIN Valve Connectors – Definition, Types
Four Way Solenoid Valve Working Principle
Solenoid Valves Types & Functions
Calculate Flow Coefficient Kv of Solenoid Valve
Solenoid Valves Types, Principle & Animation
Solenoid Valves Practical Problems
Solenoid Valve Failure in Plant Start-Up: Identifying the Root Cause
Plant Shutdown Analysis: Valve Closed and SOV Coil Failure

Keep Learning

Solenoid Valve Terminology

Solenoid Valves Terminology

Solenoid Valve Functional Testing

Solenoid Valve Functional Testing

Compare Solenoid Valve Manual reset and Manual Override

Compare Solenoid Valve Manual Reset and Solenoid Manual Override

Solenoid Valve Problems and Solutions

Solenoid Valve Problems and Solutions

Emerson ASCO Solenoid valve references

SIS Solenoid Valves – Safety PLC

2-way solenoid valve Normally Closed

What is a 2-way Solenoid Valve ?

Online Testing of Solenoid Valve

Design and Accessories Required for Online Testing of Solenoid Valve

3-way solenoid valve Normally Open

What is a 3-way Solenoid Valve ?

Learn More

circuit-breaker-working-principle-animation

Circuit Breaker Working Principle Animation

What is Energy Monitoring System

What is Energy Monitoring System ?

Wrong Orifice Installation

How Not to Install an Instrument and Wrong Practices

Electrical-Switches-Working-Animation

Difference between Star and Delta Connections

Control Valves Classification

Classification of Control Valves

Introduction to SCL Programming in Siemens PLC

Types of Expressions in the SCL Language of the Tia Portal

Shockley Diode Working Principle

Shockley Diode Working Principle

RF Level Sensors Principle

RF Level Switches Working Principle

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?