Root Cause Analysis for Control Valve passing problem which was started after the overhauling job.
Control Valve Passing Problem
A control valve (globe valve with air to close – diaphragm type actuator) installed in the dirty water service was having major passing issues. So to attend to the passing of the control valve, an overhauling job was taken.
The control valve was properly overhauled in the workshop. After overhauling, stroke checking was done in the workshop itself after a calibration. The calibration type was auto-calibration.
The control valve was having Class IV leakage class. As per class IV, a leakage test was done and the response of the control valve was satisfactory. The control valve was shifted to a new location and installed back.
After taking the control valve inline, again passing was observed. So what went wrong? Let us have a detailed analysis of the scenario.
Probable Cause 1: Control valve having seat or plug damage
Overhauling was done recently and all hard parts of the repair kit were replaced. The control valve was single-line equipment and the control valve was not overhauled for the last 10 years.
Probable Cause 2: Control valve having actuator passing issue
Overhauling was done recently and all soft parts were replaced as the control valve was single-line equipment.
Also, as mentioned above cause, the control valve was not overhauled for the last 10 years.
Probable Problem 3: Control valve having a calibration issue
After the overhauling job, the control valve was auto-calibrated at the workshop itself. The stroke was checked and the response was satisfactory.
Also as per the control valve’s design leakage class, the leakage test was done at the test bench. There was no passing observed.
Probable Problem 4: Damage to the control valve during shifting of the control valve to the location
The control valve was shifted properly with all necessary precautions under the observation of a supervisor and an engineer.
Probable Problem 5: Control valve’s actuator not having proper air supply pressure
Air supply pressure to the actuator was checked and found ok as per the datasheet of the control valve.
Observations of the Job on Control Valve
Observations after taking the control valve for maintenance job again:
- The control valve’s air supply pressure was checked and found ok.
- The control valve’s actuator was checked and no passing was found.
- After isolating the line and checking the stroke of the control valve, it was found that the control valve’s stroke length was less than 100%. Because of this less stroke length, the control valve remained open, and hence passing was observed.
- The control valve was again auto-calibrated. This time the operating stroke length was verified as per the data sheet. The response was satisfactory. Also, the control valve was taken inline. No passing was observed at full design differential pressure across the control valve.Â
What Went Wrong with the Control Valve?
The engineer and the technician, who installed the control valve, were asked about the whole process of installation (Because no mistake was made at the workshop).
On a healthy conversation with the engineer, the team came to know that the control valve was again auto-calibrated at the site after installation.
The reason behind again auto-calibrating the control valve was that after installing the control valve and taking the control valve inline, the control valve was having a hunting issue (2% – 3% hunting). So the supply air pressure was checked and found ok.
The actuator was also ok. So, the engineer decided to auto-calibrate the control valve. So, the line was again isolated and the control valve was auto-calibrated.
The probable reason can be that during the auto-calibration job when the control valve was in line, some foreign material might have been deposited on the seat as the control valve was installed in a dirty water service which has some hard particles also.
So because of this foreign material, the control valve could not fully close and hence the full stroke was less as compared to the original stroke length.
When the control valve was again taken inline, due to the pressure of the water, the foreign material might have gone in downstream creating a space for leakage.
Solution
How can we avoid such issues?
- Always mark the full stroke length and verify it with the stroke length mentioned in the datasheet.
- Do proper line flushing with clean water or air before calibrating the control valve.
- Quick Exhaust Valves
- On-Off Valve Problems
- Control Valve Design Factors
- Solenoid and Motorized Valves
- Control Valve Maintenance