Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: Different Control Valve Flow Characteristics
Share
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Control Valves > Different Control Valve Flow Characteristics

Different Control Valve Flow Characteristics

Last updated: July 1, 2025 6:22 am
Editorial Staff
Control Valves
2 Comments
Share
8 Min Read
SHARE

Control Valve Flow Characteristics is the relationship between the percentage of valve opening on the flow rate. The choice was a control valve with flow feature that is important as well With a large selection of the appropriate valve.

Contents
Linear CharacteristicsEqual Percentage CharacteristicsQuick Opening or Fast Opening CharacteristicsModified Parabolic CharacteristicsInherent Control Valve Flow CharacteristicsInstalled Control Valve Flow Characteristics

For a device that serves to divide the flow features in each model. Trim is designed series of control valves. This will affect the rheological properties (flow. characteristics).

There are three most common control valve characteristics viz Linear, Equal % and Quick-Opening.

Linear Characteristics

A control valve is labelled LINEAR if its inherent flow characteristics can be represented by a straight line on a rectangular plot of flowrate F (or % F, or Cv or % Cv) versus % travel m (or Z for opening position) at the ideal condition of constant valve pressure drop (DPV).

Therefore equal increment of travel or opening m produce equal increment of flow F (or Cv) at constant valve pressure drop (DPV). If m represents travel and F represents flowrate, then dm = k dF, where k is a proportional constant.

Thus the valve gain or sensitivity, which is change in flow F divided by the change in travel m is constant, whether at low flow or high flow i.e. valve gain Kv = Df/dm = constant, independent of flowrate and valve opening.

Note also that the valve gain Kv is the slope (tangent) of the rectangular plot of flowrate F (Y-axis) versus valve travel or position m (X-axis). The slope remains constant and independent of flowrate throughout.

The flow rate can be varied with the percentage of opening of the control valve. 10% as the valve opens to allow the flow rate is 10%, 15% or more by opening the valves would cause the flow rate was increased to 15% as well, this is called Linear Characteristics.

Equal Percentage Characteristics

A control valve is said to be EQUAL % if equal increment of valve travel or opening m (or Z) produces equal PERCENT (%) increment in flow F. If this occurs at the ideal condition of constant valve pressure drop (DPV), the valve is said to be inherently EQUAL %.

Therefore dm = k1 (dF/F) x 100%

where k1 is a proportional constant.

Hence valve gain Kv = (dF/dm) = k1 F where k1 is a proportional constant.

Note that the valve gain Kv is not constant but increases as flow increases. Hence at low flow when the control valve is just opening, the valve gain is low and its flow change is insensitive.

At high flow at the upper portion of travel, the valve gain is high which means that the flow increases rapidly (sensitively) for the same increment in valve travel.

On a rectangular plot of flowrate F (Y-axis) versus valve travel or position m (X-axis), the slope is flattish near the initial travel position m (X-axis), but increases rapidly with flow as the valve opens at the upper portion of travel.

Quick Opening or Fast Opening Characteristics

The Quick-Opening characteristic control valve has a flat disk instead of a contoured valve plug. Its flow (or Cv) increase rapidly to its maximum flow with minimum initial valve opening. At the initial or lower portion of travel position, the valve gain Kv is too high for use in modulating control.

Thereafter, the slope is flattish, where the flowrate hardly increases with valve opening m. Therefore, such control valve is limited to ON-OFF service and application or in specific application which requires fast initial release or discharge of flow.

Modified Parabolic Characteristics

Other less common types of characteristics include the “modified parabolic” which is approximately mid-way between the Linear and Equal % characteristics, giving fine throttling action at low valve travel (like Equal %) and approximately linear characteristic for the upper portion of travel.

The so-called ‘hyperbolic’ characteristic rectangular plot is “bowed”, below the Linear characteristics. These two characteristics (Quick-Opening, modified parabolic) are mentioned here for interest sake only as the Linear and Equal % characteristics can meet almost all control requirement.

Control Valve Flow Characteristics

The characteristics graph is divided into two types.

Inherent Control Valve Flow Characteristics

The control valve Manufacturer can only state the Inherent valve characteristics, which refer to the flowrate, valve travel position relationship, when the pressure drop across the control valve is constant.

Note that the pressure drop across the control valve can be almost constant only if the piping system pressure drop is concentrated at the control valve and not distributed along the pipeline.

This means that the pipeline must be of very short length with minimum pressure-reducing-devices or equipment in series with the control valve.

Such a condition rarely exist in actual installation except in the control valve Manufacturer test facilities, where the control valve characteristics are obtained using very short length of piping.

Such ideal valve characteristics are the valve Inherent characteristics.

Installed Control Valve Flow Characteristics

The control valve Installed characteristics refer to the relationship between the volumetric flowrate through the valve AND the valve travel or opening position, as the valve is opened from its closed position to various degree of opening, when the pressure drop across the valve varies.

Note that the pressure drop across the valve varies in most actual installation, influenced also by various pressure-reducing devices in series with the control valve, such as the pipe length, pipe fittings and various types of valves, flowmeter and process equipment. In general, the pressure drop across these devices also vary with the flowrate squared.

Thus constant valve pressure drop rarely exists except in the ideal conditions of the Manufacturer’s test Lab. A control valve displays its Inherent characteristics at such ideal conditions. In actual plant installation, it displays the actual or Installed characteristics. The Installed valve characteristics can be very different from its Inherent or ideal characteristics.

The flow properties actually happens when we mount the valve into the pipe, filling in already. This chart looks at it will not match the Inherent Flow Characteristics.

Installed Control Valve Flow Characteristics

Read Next:

  • Interview Questions on Valves
  • Inherent vs Installed Valves
  • Valve Trim Characteristics
  • Different Valve Types
  • Choked Flow of Control Valve
Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

What is Gate Valve ?
How Sliding Stem Valves Work ?
Safety Relief Valve Questions & Answers
Two Solenoid Valves Working Principle
Valve Characteristics – Quick Opening, Linear & Equal Percentage
How Diaphragm Valves Work ?
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
2 Comments
  • Prem says:
    May 14, 2019 at 8:02 pm

    Good

    Reply
  • Shreyash Patel says:
    October 30, 2024 at 9:28 pm

    very nice.. and good .

    Reply

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

How to Protect Pumps from Cavitation? – Reasons, Solutions
How to Select Control Valve Failure Mode
Solenoid Valve with Manual Reset Working Principle
Purpose of 100% and 30% Feed Control Valves in a Power Plant
Electronic Valve positioners
Difference between PCV and PRV
Control Valve Interview Questions and Answers
What is Globe Valve ?

Keep Learning

Purpose of Isolation valve

What are Isolation valves? – Purpose, Types, Configurations

Solving Critical Control Valve Hunting

Solving Control Valve Hunting: Instrument Troubleshooting

Difference between Globe Valve and Gate Valve

Difference between Globe Valve and Gate Valve ?

needle valve applications

Applications of Needle Valves

Air Pressure Regulator cut-away diagram

Air Pressure Regulator Questions

Control Valves Questions and Answers

Control Valve Questions and Answers

Difference between Butterfly Valves and Ball Valves

Difference between Butterfly Valves and Ball Valves

Types of Pneumatic Valves

Types of Pneumatic Valves : Poppet & Spool

Learn More

Difference between IP Address and MAC Address

Difference between IP Address and MAC Address

Digital Electronics Multiple Choice Questions

Diode-Transistor Logic (DTL) Objective Questions

PLC Instructions

Program Flow Control Instructions in PLC Programming

Factors to Consider When Choosing Power Tools

Factors to Consider When Choosing Power Tools

Densitometers Principle

Vibrating Tube Densitometers Working Principle

Causes of PLC Stop Mode

Various Causes for PLC Going in Stop Mode

CAN Protocol with the OSI Model

Basics for CAN Bus Protocol – Controller Area Network

Electrical Ground Loop

How to Solve Electrical Ground Loop Problems?

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?