Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: What is Cable Schedule and Junction Box Schedule?
Share
Notification Show More
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Instrumentation Design > What is Cable Schedule and Junction Box Schedule?

What is Cable Schedule and Junction Box Schedule?

Last updated: August 14, 2020 9:23 am
Editorial Staff
Instrumentation Design
No Comments
Share
4 Min Read
SHARE

Cable and Junction Box schedules are deliverables prepared by instrumentation and control design engineers in EPC or EPCM Companies. In this article, we shall learn about the same.

Contents
Inputs RequiredCable ScheduleJunction Box Schedule

Inputs Required

 Below listed references are the required inputs for the preparation of the document “Cable Schedule”.

  • P&IDs
  • Instrument Index and Instrument I/O List
  • I&C Design Basis
  • Basic Engineering Design Data

Cable Schedule

Cable Schedule is a document containing a list of Instrument cables. This document shows cable as well as gland required by each instrument or connection.

The information of the cable schedule consists:

  • Cable Number
  • Cable Type / Specification
  • Cable Size
  • Cable Length
  • Source and destination termination description
  • Cable gland type and size for each incoming cable

Cable schedule is a reference in preparing Material Take-Off of cable for procurement. However, cable length shown on this document is approximate only. Therefore, there should be a contingency for material procurement to allow spare for cable cutting, unexpected barriers in the field, riser, etc.

Cable schedule will be referred also during the construction phase; however, it is not recommended to cut the cable based on the length information stated on the cable schedule. For actual cutting during installation, the common practice is to pull the cable from its drum and cut it in the field.

This is how a typical Cable schedule looks like.

Cable Schedule

Junction Box Schedule

First, let us learn about the Junction Box.

The junction box is an enclosure used for cables interconnection between field devices and the control room.

It encloses terminal strips for cable termination. Junction box shall be designed to suit environmental condition where the box will be installed and shall have certification of Ingress Protection code and hazardous area protection which conform to the classified area.

Junction Box consists of the following parts, but not limited to:

  • The terminal block which comprises terminal strips for cable connections
  • Gland plate (for non-metallic junction box) for cable gland earthing
  • An insulated earth bus bar for overall cable screen termination (optional, drain wire could be connected to terminal strip)
  • Breather/drain plug
  • Mounting Rail complete with end bracket

The typical Junction Box layout

Junction Box layout

JB Schedule is a document containing a list of instrument JB. This document shows cable as well as gland required by each instrument or connection.

The information of the JB schedule consists:

  • JB Number
  • JB Type / Specification
  • JB Size
  • JB Location/Area
  • Source and destination termination description
  • gland type and size for each incoming cable

JB schedule is a reference in preparing Material Take-Off of JBs for procurement.

JB schedule will be referred also during the construction phase, however, it is not recommended to install JBs based on the location information stated on the JB schedule. For actual installation, the common practice is to refer Location Layout.

Interest to add any further points? Share with us through below comments section.

Author: Kalpit Patel

Read Next:

  • Fieldbus Network Topologies
  • DCS Wiring Schemes
  • Control Valve Accessories
  • Instrument Loop Diagram
  • Instrumentation Earthing
Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Process Variable Damping of Transmitter
System Architecture and Process Control Systems Philosophy
Float-type Level Switch to Control a pump
Thermowell Insertion and Immersion Length
Instrumentation Earthing
What is the thermal effect on Sensors?
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
Leave a Comment

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

Magnetic Flow Meters Installation Guidelines
How to Calculate Heat Load in Electrical/Electronic Panel Enclosure
Control Valve Selection Tips
Compliance Table Application (for Procurement Service Cycle)
Air Cylinder Consumption Calculation for Control Valves
Instrumentation Deliverables Generated from 3D Modeling
Level Instruments Design Rules
Testing of Pneumatic Systems

Keep Learning

IS Loop Formula

Difference between Intrinsic Safe and Non-Intrinsic Safe Cables

Types of Cables

Types of Cables, Purpose, Advantages, Disadvantages, Applications

Field Instruments

Is Vacuum affects Field Instruments in Industries?

What is NEST loading=

What is Nest Loading? – DCS and PLC Control Systems

Explain operation of the circuit

Explain Operation of the Lamp Circuit ?

Control system architecture diagrams

Vendor Document for Project Systems Architecture

Instrumentation and Process Control Project Inputs

Instrumentation and Process Teams Interactions in Design Engineering Companies

Determine the statuses of all lamps and relay coils in the circuit

Determine the Status of Lamps and Relays in the Circuit ?

Learn More

Pressure Gauge pulsation damping

Pressure Gauge Pulsation Damping

Pre-Startup Safety Review (PSSR)

Pre-Startup Safety Review (PSSR)

Process Control Terms

143 Process Control Terms and Glossary – Questions Answers

Example Ladder Logic Diagram

What is Relay Logic ?

Sand Probe Functional Testing

Sand Probe Functional Testing

What is Wellhead Control Panel?

Different Types of HVAC Applications

Different Types of HVAC Applications

Shutdown Manager

What are Pre-Shutdown, Shutdown, and Post-Shutdown?

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?