Reading: 4-20mA Graphical Calculations
Inst Tools > Blog > Formulas > 4-20mA Graphical Calculations
Last updated: March 27, 2023 9:54 am
Formulas
3 Comments
3 Min Read
An illustration sometimes find helpful in understanding analog signal ranges is to consider the signal range as a length expressed on a number line.
For example, the common 4-20 mA analog current signal range would appear as such:
4-20mA Graph
If one were to ask the percentage corresponding to a 14.4 mA signal on a 4-20 mA range, it would be as simple as determining the length of a line segment stretching from the 4 mA mark to the 14.4 mA mark:
4-20mA Image
As a percentage, this thick line is 10.4 mA long (the distance between 14.4 mA and 4 mA) over a total (possible) length of 16 mA (the total span between 20 mA and 4 mA). Thus:
4-20mA to Percentage Calculation
Percentage = 65%
This same “number line” approach may be used to visualize any conversion from one analog scale to another. Consider the case of an electronic pressure transmitter calibrated to a pressure range of −5 to +25 PSI, having an (obsolete) current signal output range of 10 to 50 mA.
The appropriate current signal value for an applied pressure of +12 PSI would be represented on the number line as such:
3-15psi to 4-20mA conversion
Finding the “length” of this line segment in units of milliamps is as simple as setting up a proportion between the length of the line in units of PSI over the total (span) in PSI, to the length of the line in units of mA over the total (span) in mA:
Solving for the unknown (?) current by cross-multiplication and division yields a value of 22.67 mA.
Of course, this value of 22.67 mA only tells us the length of the line segment on the number line; it does not directly tell us the current signal value.
To find that, we must add the “live zero” offset of 10 mA, for a final result of 32.67 mA.
Calculate 4-20mA Equivalent
Thus, an applied pressure of +12 PSI to this transmitter should result in a 32.67 mA output signal.
4-20 mA into 0-100 % Calculation Formula - Instrumentation Tutorials
  • History of 3-15 psi & 4-20 mA
  • 4-20mA Conversions Easily
  • Zero and Span Calibration
  • Process Variable Conversion
  • Calculate Temperature Transmitter
Calculate Temperature Coefficient of RTD
DP Transmitter Dry Leg & Wet Leg Calculations
Formula to Calculate 4-20 mA from Process Variable
Displacer Level Measurement Calculations
Formula to Calculate Process Variable from 4-20mA
3 Comments
  • Nayan Gohil says:
    August 7, 2016 at 1:54 am
    Thanks for the info.
  • giddaiah says:
    August 7, 2016 at 4:34 pm
    very nice useful for all our inst dept shadnagar hyd
  • mputu kabutoto says:
    October 14, 2021 at 9:12 pm
    l like this courso for me can you send this courso for my email
Siemens Differential Pressure Transmitter Calculations (Flange Type)
Instrumentation Basics – Range Conversion Formula and Examples
Formula for Current 4-20ma to Percentage Conversion
Linear to Square Root Extraction
Turbine Flow Meter Coefficient and Scaling Factor
Input-Output Relationships of Transmitters
Instrument Percent of Span Error
Convert-Linear-%-to-Square-root-%
Formula for Linear % to Square root % conversion
Temperature Transmitter Formula
Calculate Temperature Transmitter Output
Control valve positioner calculation
Calculate Control Valve Stem Position
Scaling Sensor Output to Engineering Units
Gas flow rate Formulas
Gas Flow Formulas
Formula for Linear mA to Square root mA conversion
Percentage-to-Current-Conversion
Formula to Calculate 4-20ma from Percentage
Zero Suppression in level Measurement
Zero Suppression and Zero Elevation Calculations
D flip flop in PLC
D Flip Flop PLC Ladder Logic
Scintillation Counter Theory
Scintillation Counter Principle
Memory Devices Objective Questions – Part 5
Reactive Power Sources and Sinks in Power System
strain gauge changes as it stretches and shrinks
Why Strain Gauge Resistance Changes as it Stretches and Shrinks?
Communicate between the PLC program and HMI program
Design a Program Using Studio 5000 and FactoryTalk View Studio
RTD Calibration
RTD Calibration
Transit Time flow meter Theory
Transit Time Flow Meter Principle