Reading: Types of Digital Outputs in PLC
Inst Tools > Blog > PLC Tutorials > Types of Digital Outputs in PLC
In this post, we will understand the various types of digital outputs used in PLC like relay, triac, and transistor.
Last updated: October 17, 2023 2:02 pm
6 Min Read
In this post, we will understand the various types of digital outputs used in PLC.
Digital Outputs in PLCTypes of ContactsWorking of a RelayPLC OutputsTypes of Digital OutputsSinkSourceRelayTriacTransistor
There are four basic types of inputs and outputs in a PLC.
  1. digital inputs,
  2. digital outputs,
  3. analog inputs, and
  4. analog outputs.
Here, we will consider the various types of digital outputs in the PLC. Before going into the types, let us consider how an output functions in a PLC.
A digital output is nothing but a switch that a PLC operates to turn on or off the output device. It is controlled by the logic written inside the PLC.
Types of Contacts
Traditionally, there are three contacts for operating an output.
  1. COM (Common),
  2. NO (Normally Open), and
  3. NC (Normally Closed).
See the below image for reference.
Digital Output Contacts
COM is the common terminal that connects both the NO or NC contacts according to the trigger given. Consider this as a part of an electrical switch.
When the switch is in off condition, the COM and NC terminals are connected with each other.
When the switch is in on condition, the COM and NO terminals are connected with each other.
Working of a Relay
Now, let us go one step more ahead to the working of a relay.
Basic Concepts of the Safety Relay
In a relay, there are five contacts – two for power supply and three as mentioned above. When the relay is given supply, the contacts change from COM and NC to COM and NO.
Refer to the below image. The potential will not flow between plus and minus contacts unless they contact each other through relay contacts.
So, when the relay is energized, the potential will flow from plus to minus through the COM and NO paths.
Consider this supply as a part of a device or instrument (shown as the green box). This will then energize the device indirectly.
Digital Output with Power Supply
PLC Outputs
This is the same logic for a PLC output. They have two contacts
  1. either NO and COM or
  2. NO and NC.
When the output is logically turned on from PLC, the internal contacts switch their position accordingly as discussed and turn on the field device connected at it.
Refer to the below image for the PLC control part as discussed.
PLC contacts
Now, discussing our topic, the types of digital outputs mean the types of potentials that can be given to the COM terminal.
There are only two voltages available in a PLC. They are
  1. DC, and
  2. AC.
There are three types of outputs. They are
  1. Relay,
  2. Triac, and
  3. Transistor.
Before going into these types, we have to understand the two types of current that flow in a circuit. They are
  1. Sink, and
  2. Source.
Sink
The sink is the type where negative potential will flow from the NO or NC terminals.
Source
The source is the type where positive potential will flow from the NO and NC terminals.
This is decided by either giving a negative or positive potential at the common terminal respectively. In the above image, the PLC output is source type.
Let us study each PLC output type in detail:
Relay
If the output type is a relay, that means you can give any potential (DC or AC) to the common terminal.
When the output is energized, it will accordingly allow the flow of current to the device and make its contact closed.
Relay Parts
As the name suggests, it has a mechanical contact inside for switching the output. Due to the use of mechanical contacts, they have a higher load current carrying capacity than the other two types.
But they also have a shorter life span as compared to the other two and are prone to more damage if switched at a very high frequency constantly.
Triac
In triac type, you can connect only AC voltage to the common terminal. They are faster in operation and have a longer life span compared to relay outputs.
Even they can handle a larger amount of load current.
Transistor
In transistor type, you can connect only DC voltage to the common terminal. They are faster in operation and have a longer life span compared to relay outputs.
But they cannot handle a larger amount of load current.
These are the three types of digital outputs used in a PLC.
  • History of OPC Protocol
  • Top PLC Manufacturers
  • PLC, MCC, LCP & Pump Video
  • Comparison Instructions in PLC
  • How to Test TRIAC with Multimeter
Real-time PLC Projects – Industrial Automation
Architecture of Allen Bradley PLC
PLC Based Product Sorting Machine System – Lift Control
How to Select a SCADA for New PLC Project?
Drive Multiple Speeds with Different Reference using PLC
What is Fail-safe in Siemens PLC?
History of Programmable Logic Controllers (PLC)
Why is 24 Volts Commonly used in PLC Systems?
PLC Program Example on Multiple LEDs using Set Coil
PID with Practical Example
Cybersecurity in PLC
PLC Software Redundancy
Software Redundancy in Siemens PLC – Hardware versus Software
Programming with Schneider PLC
Mail Box Automation: Programming with Schneider PLC
EasyBuilder Pro Weintek HMI Software
EasyBuilder Pro Online Simulation of Mitsubishi FX3U PLC
PID Simulator
PID Simulator Download
Why Are Charcoal and Salt Added to an Earthing Pit
Why Are Charcoal and Salt Added to an Earthing Pit?
Database for each safety module
Global Acknowledgment Instruction in Safety PLC
Allen-Bradley PLC
Example of PLC Programming based on Logic Circuit
Stability in Frequency Domain
Tuning of PID Controllers
Mass Spectrometer Questions & Answers
Classification of Fuses
Step-by-Step Guide to Choose Right Fuse for a Panel
Advanced Ladder Logic PLC Example
Automatic Sanitizer – Complex Ladder Logic PLC Examples
Ladder Logic Counters Instruction
Up Counter PLC Program
Cybersecurity Projects for Engineering Students
Level-Measuring-Instruments-Velocities-of-Propagation
Level Measuring Instruments Velocities of Propagation
Disadvantages of Resistance Temperature Detectors (RTD)