Reading: Rotork Motor Operated Valve Basic Configuration
Inst Tools > Blog > Control Valves > Rotork Motor Operated Valve Basic Configuration
In this article, you will learn about the rotork motor operated valve basic configuration, settings, and commissioning procedure.
Last updated: May 3, 2023 9:54 am
vicky
Control Valves
Motor Operated Valves (MOV) are generally used in large pipes where the torque required is high and only ON/OFF is used. MOV is not preferred for control applications.
Rotork Motor Operated ValveInfrared Setting ToolMOV ConfigurationCommissioning of Motor Operated Valve (MOV)
Today we will discuss about Rotork Make electrical motor actuator.
The supply voltage is a 3-phase supply
We can control the motor-operated valve through FF, Profibus, Modbus, DeviceNet, or Packscan system (it is a network loop controlled by a Rotork Master Station device available in a single, dual, or hot standby configuration. A single network can control up to 240 actuators. Cable length can be 20 km), through setting tool pro or through local switches.
Analog, as well as digital feedback (4 switches are available), can be configured as per our needs.
Let’s discuss some basic things about Rotork MOV (IQ series)
Parts of Motor Operated Valves
  • Hand Operation
Hand wheel operation can be done during any emergency situation. A clutch engages MOV for hand operation while power operation unlatches the clutch
  • Thrust base
To connect the body to MOV, an easily removable drive bushing is provided.
  • Local Control
Local switches provided for local control
  • Position Control
The hall effect magnetic pulse system is used to monitor the movement of the actuator
  • Terminal Compartment
Separate sealed compartment for 3-phase supply as well as control and feedback cables
  • Motor and Drive
The low inertia and high torque motor provided for easy operation. For protection, torque trip and high winding temperature trip are provided.
The motor-operated valve settings and configuration can be done through a Setting Tool Pro (Infrared setting tool).
This tool has different buttons available on it as shown below figure.
Motor Operated Valve Infra-Red setting tool
The button functions/names are listed below
  1. Down Function
  2. Up Function
  3. Next function across
  4. Previous function across
  5. Decrease/change value
  6. Increase/change value
  7. Download/upload mode
  8. Enter
  9. Stop actuator
  10. Open actuator
  11. Close actuator
MOV Configuration
MOV has a local display, an open/close button, and a local/remote/stop button
In local mode, MOV can be operated locally through the open/close button
MOV can be operated remotely from control system
In remote mode, MOV can be operated remotely from the control system
MOV Valve Images
In stop mode, MOV won’t operate electrically.
Motor Valve in Stop Mode
Let’s see how to set open and close feedbacks and set torque values which are widely used configuration settings in the motor-operated valves.
For setting any of 4 parameters, i.e. close feedback, open feedback, close torque or open torque, we need to enter the password and then we can access the menu.
NOTE: If MOV is close then GREEN LED will be ON and if MOV is open then RED LED will be ON as shown below
MOV valve close and open feedback
Below mentioned steps are common:
Step 1: Put MOV in stop mode using a local switch.
Step 2: Press down the function key, and you will be the Torque value as shown below
Step 3: Again press down the function key and you will be asked password as shown below
Valve Password Protection
Step 4: Press enter and you will see the password correct (If any other password is set then use the +/- key)
Electric Motor Password
Step 5: Now press down the function key again and you will see the basic/config option
Basic Configuration of Motor Operated Valve
Step 6: Go on pressing down the function key until you see MOV asking to set close feedback, move the valve to close position, and press enter.
Set close feedback in MOV Valve
Step 7: To set open feedback, press the Next function across key
Configure open feedback  in MOV Valve
Now MOV will ask to set open feedback
Then move MOV to open condition and press enter to set open feedback
Step 8: Again press down the function key and go on pressing until you see MOV asking to set Close torque and press ENTER.
Torque Setting in Valve
Use +/- to increase or decrease torque value after selecting it.
Step 9: To set open torque, press the NEXT function across key
Now MOV will ask to set open torque. Use +/- to increase or decrease torque value after selecting it.
Torque Switches in MOV
Basics of Ball Valves
Electronic Valve positioners
How to Solve On-Off Valve Problems?
Solenoid Valve Troubleshooting Practices
Over Pressure cases for Pressure Relief Valve Sizing
Reversing Control Valve Actuator Fail Safe Mode
Relative Flow Capacity of a Valve
What is Control Valve Flashing ?
How is Pressure Drop Calculated through a Valve ?
How Valve Positioners act as Cascade Control Systems in a Loop?
Control Valve Tips and Tricks
Valve Characteristics – Quick Opening, Linear & Equal Percentage
Difference Between the Control Valve and Shut-off Valve
What are Isolation valves? – Purpose, Types, Configurations
Online Testing of Solenoid Valve
Design and Accessories Required for Online Testing of Solenoid Valve
pneumatic piston actuator
Working Principle of Pneumatic Actuators
How to Do Maintenance of Control Valve Which is Stuck in Field?
Types of Control Valves Noise
What is Swing Check Valve ?
Summary of Valve Types Characteristics
What is Travel Stop in Control Valve
What is Travel Stop in Control Valve?
Air Cylinder Consumption Calculation for Control Valves
Wrong Orifice Installation
How Not to Install an Instrument and Wrong Practices
History of Measurement
Fuel Boiler
Boilers
Auto-negotiation in Network
What is Auto-negotiation in Network?
Automated Test Bench - Complex PLC Programming Examples
Automated Test Bench – Complex PLC Programming Examples
Pneumatic Actuators
Self-Actuated Valves, Pneumatic & Hydraulic Actuators
Alarm and Trip Documentation
Benefits of IoT in the Manufacturing Industry