Our scope will be for the common VarPlus-Logic device that is represented by Schneider.
These types of devices are used to monitor the power consumption of your plant and by its role, it will regulate the steps of your capacitors (automatically) in order to enhance and improve the power factor in your plant.
With the efficient use of this device, the industry can improve the efficiency of the system by reducing losses and reduced apparent power demand charges.
The idea behind the power factor correction by the use of the Capacitors. The capacitors are connected in parallel with the Power-incoming network as shown in the next Figure.
power factor correction equipment
Capacitors contained in most power factor correction equipment draw a current that leads the voltage, thus producing a leading power factor.
If capacitors are connected to a circuit that operates at a nominally lagging power factor, the extent that the circuit lags is reduced proportionately.
The VarPlus controllers are able to control six stages (6L) or twelve stages (12L), which depends on your needs and your device version, the device can be connected to either 220V/400V AC that depends on your selection.
For the next figure, we can see it is a phase to phase connection (480 VAC) the two phases are connected to (U1 . U2).
power factor correction using capacitors
Note
In case of disconnecting the current transformer (CT) because of rewiring or panel maintenance, you have to ensure that the CT terminals are shorted, because an open circuited CT makes a huge amount of volt across the secondary winding, and that could make a series danger for the Technician that is dealing with.
This device has two modes for commissioning:
  • Quickstart menu (commonly used).
  • Advanced menu setup for this mode you have to enter each parameter of your device by yourself, which makes it a kind of complex in most situations.
You can enter the quick start menu by selecting the 100 sub-menu from the PARAMETER menu.
  1. At first you need to enter the Ph-Ph voltage, the default value is 400V but you have to define the exact value of your station.
  2. Then the device asking for (CT) the current transformer factor that is written on the CT itself.
  3. If you are adjusting your device with the power network for the first time, you have to turn on the AUTO initializing that switches all outputs, during the test the controller determines the outputs that are working. It can also correct the voltage and current connections when the phases are swapped.
  4. Then you have to adjust the PFC power factor control parameter as following:
ON control is in Automatic mode.
OFF control stops and active steps will be disconnected.
Hold control stops and active steps remains in.
  • Here you can set the desired value of the power factor by adjusting CP1, the default value is 0.95 but you have the option to change it.
  • Finally, you have to set the time for the Switch Interval that is the time delay between switching steps in regulation.
Note
You will not find the setting of the cooling fan at the Quick start menu so, if you are using a cooling fan, you have to enter the desired temperature set point on parameter 511.
When the temperature drops under the set point the contact of the fan will be energized to turn the fan ON until it can achieve the set point again.
  • Identify PLC Critical Alerts
  • Monitor PLC Memory Usage
  • Instrument for Plausibility Checks
  • PLC Hard Stop Events from Faults
  • Assign Register Blocks by Function
Advantages and Disadvantages of Industrial Automation
What are the Interlocks for Steam Turbine?
Loop Calibrator to Simulate a 4-20 mA Signal
How to Solve Electrical Ground Loop Problems?
Instrumentation and Control (I&C) Design
Hot Well Level Control System in Condensing Turbine
What is Process Control?
List of 100 Distributed Control Systems Questions (DCS)
Installing and Using Modern Industrial Joystick Controls
Types of Noise in Electronics
Why Offset in Proportional Controller ?
Why 24 Volts DC Power Supply is used? – Industrial Automation Systems
Industry 4.0 Explained – Industrial Internet of Things
Standard Colors in PLC Automation Systems
Understanding-a-Process-Control-Loop
Understanding a Process Control Loop
4-20mA Loop Power Supply Questions
Does Really a Safety Barrier is Important
Does Really a Safety Barrier is Important? – PLC DCS Systems
Difference between Feedback, Feedforward, and Cascade Control
Difference between Feedback, Feedforward, and Cascade Control?
DeltaV System to Excel
How to Export Data from DeltaV System to Excel
Augmented Reality and Virtual Reality in Industrial Automation
Readings Mismatch between Field & Control Room
Zigbee Projects
Zigbee Based Project Ideas and List
Instrumentation Cables Testing Standards
Thermocouple Extension Lead Minimizer Circuit
Thermocouple Wires and Extension Lead Issues
Parallel Operation of Alternators
ICS System Design
Essential Dorm Room Items Every Student Should Get
The Dorm Room Essentials And Why You Need Them
Optical Pyrometer
Optical Pyrometer Working Principle
Point Gas Detectors Principle
Point IR Detectors Vs Open Path IR Detectors