Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: Liquid Level Switch Control Pump and Lamp
Share
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Control Systems > Liquid Level Switch Control Pump and Lamp

Liquid Level Switch Control Pump and Lamp

Last updated: February 2, 2020 10:41 pm
Editorial Staff
Control Systems
No Comments
Share
4 Min Read
SHARE

This pictorial diagram shows how a liquid level switch (with two separate SPDT switch units actuated by a common float mechanism) is wired to control both an electric pump and a lamp:

Liquid Level Switch

Liquid Level Switch Control Pump and Lamp

Under what liquid level condition will the lamp energize?

Under what liquid level condition will the pump motor energize?

Determine what an AC voltmeter would register under the following conditions:

→ Connected between terminals 1 and 2; high liquid level

→ Connected between terminals 2 and 6; low liquid level

→ Connected between terminals 4 and 7; low liquid level

→ Connected between terminals 1 and 6; high liquid level

Supposing the pump motor refused to energize but the lamp still functioned properly (turning on and off when it should), devise a series of diagnostic tests you could implement with an AC voltmeter to locate the fault. For each test, explain what the result of that test means for your diagnosis of the problem.

Solution:

The lamp receives power through an NC (normally-closed) switch contact, which means it will be energized when the level switch is in the resting (low level) state.

The pump motor receives power through a NO (normally-open) switch contact, which means it will be energized when the level switch is in the actuated (high level) state.

Determine what an AC voltmeter would register under the following conditions:

→ Connected between terminals 1 and 2; high liquid level – 120 VAC regardless of the level

→ Connected between terminals 2 and 6; low liquid level – 0 VAC

→ Connected between terminals 4 and 7; low liquid level – 120 VAC

→ Connected between terminals 1 and 6; high liquid level – 0 VAC

The symptoms tell us the problem must be limited to the pump circuit, and cannot be related to anything common with both the pump and lamp because the lamp still works as it should.

Taking a voltage measurement between terminals 6 and 7 while the liquid is at a high level is a good first step: the presence of 120 VAC between those points would indicate the switch is closing at it should, and that there must be an open fault between those terminals and the motor (including possibly within the motor itself ).

The lack of voltage between those points during a high liquid level would indicate an open fault between those terminals the source.

Here are some indeterminate tests. For each one, challenge engineers to explain why the specified test would not give good diagnostic information:

Measuring voltage between terminals 1 and 2 (We already know there is the supply voltage, since the lamp works)

Measuring voltage between terminals 6 and 7 while the liquid level is low (it is impossible for any fault prohibiting motor function to yield anything but zero volts in a condition of low level, and therefore this test tells us nothing about the problem).

Credits: Tony R. Kuphaldt

Read Next:

  • Level Switch Control Logic
  • Need for Automatic Controls
  • Level Measurement Basics
  • What is Reflex Level Gauge?
  • Displacer Level Sensor Principle
Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

ESD System Insights: Signals for Emergency Valve Shutdown Explained
2-wire Transmitters Current Loops
Recognizing an Over-Tuned PID Controller by Phase Shift
Add On Instructions Programming – Analog Input Devices in Studio 5000
Explaining Various Types of Analog Instruments
How Engineers Effectively do Problem-solve and Troubleshoot?
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
Leave a Comment

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

Difference Between Batch Process and Continuous Process
How Important is VPN for Control Engineers?
How to Solve Electrical Ground Loop Problems?
Design and Implement Motor Control – Electrical Engineering
I&C Engineer Roles & Responsibilities – Instrumentation Design
Difference between Process shutdown and Emergency Shutdown
Yokogawa DCS and SIS System Architecture
Node-RED in PLC Industrial Automation

Keep Learning

Modbus Function code 02 – Read Contact(s)

Modbus Function Command Formats

Identify Process Variables in P&ID

Identify Process Variables in P&ID

How is Data Stored in Standard Modbus Protocol?

How is Data Stored in Standard Modbus Protocol?

Identify Instruments in Piping and instrumentation Diagram

Identify Instruments in Piping and instrumentation Diagram

DCS Vs PLC

Difference between DCS & PLC Systems

Direct digital control principle

Direct Digital Control (DDC) Systems

compressor emergency shutdown system

Compressor Emergency Shutdown Root Cause Analysis

What is FAT and SAT?

What is FAT and SAT? Difference between them

Learn More

Electric Circuits Objective Questions

Electric Circuits Objective Questions – Set 6

Thermocouple Material Characteristics

Thermocouple Construction

LC Tuned circuit Working Animation

LC Tuned circuit Working Animation

Difference Between Modbus TCP IP and Profinet

Difference Between Modbus TCP IP and Profinet

Mechanical Torsion Meter Principle

Mechanical Torsion Meter Principle

Pressure and Level Control Loop

Problem on Pressure and Level Control Loops

Analog Electronics Objective Questions

Analog Electronics Objective Questions – Set 7

Electrical Machines Questions and Answers

Synchronous Machine Stability Questions

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?