Instruments TroubleshootingThermocouple / RTD / Temperature TransmittersPressure, Level, Temperature & Proximity SwitchesVibration / Speed SensorsFlame SensorsIgnitersControl Valves & On/Off Valves & AccessoriesI to P Converter / Valve PositionerPosition Feedback TransmitterHydraulic Servo ValvesSolenoid ValvesHazardous Gas / Chlorine Gas / Smoke / Building & Process Fire Detection InstrumentsPressure Relief / Regulating ValvesManual Call Points (MCP)AnalysersCustody Transfer / Check Metering System & Gas ChromatographPressure / DP / Temperature / Level GaugesAir Filter Regulator (AFR)Pressure, Flow & Level TransmittersInstrument Junction BoxesDistributed Control System (DCS)Programmable Logic Controllers (PLC)Weigh BridgeCorrective Actions
Different instruments are listed below.
  • Pressure / DP / Temperature / Level Gauges
  • Air Filter Regulators
  • Pressure, Flow & Level Transmitters
  • Thermocouple / RTD / Temperature Transmitters
  • Pressure, Level, Temperature & Proximity Switches
  • Vibration / Speed Sensor
  • Flame Sensors
  • Igniter
  • Control valves, On/Off Valves & Accessories
  • I to P Converter / Valve Positioner
  • Position Feedback Transmitter
  • Hydraulic Servo Valves
  • Solenoid Valves
  • Pressure Relief / Regulating Valves
  • Building & Process Fire Detection Instruments
  • Manual Call Points (MCPs)
  • Analyzers
  • Custody Transfer metering system & Gas Chromatograph
  • Instrument Junction Boxes
  • Weigh Bridge
  • Distributed Control System
  • Programmable Logic Control System
ProblemsCauses
Showing wrong / error / high / lowLoose connection at transmitter / junction box
No power / display / outputSensor failure / Cable open
Not workingFuse failure / Cable damaged
MalfunctioningElement damaged
Wrong extension cableIncorrect cable type
Sensor not respondingSensor disconnection
Intermittent signalPoor contact
Temperature reading fluctuatingEnvironmental changes
Sensor burnoutExcessive heat
Calibration errorIncorrect calibration procedure
ProblemsCauses
Not workingManifold leak / Choke
MalfunctioningLoose connection at switch / junction box
No power / Indication / OutputChannel fault at DCS / PLC
Incorrect switchingFaulty switch
Delayed responseSensor lag
False triggeringElectrical noise
Noisy operationMechanical wear
Switch stuckInternal blockage
Poor repeatabilitySensor aging
Mechanical damagePhysical impact
ProblemsCauses
Not workingMicro switch failure
Showing wrong / MalfunctioningSensor failed
No power / Indication / OutputExternal cable damaged
Intermittent signalPoor connection
Sensor overheatingEnvironmental conditions
Signal driftCalibration issues
High noise levelsElectrical interference
Sensor not alignedImproper installation
Mechanical wearProlonged usage
Sensor contaminationDust and debris
Flame Sensors
ProblemsCauses
No flame / No powerSensor faulty / Defective MCB
Showing fewer countsCalibration drift
Not indicating flameLoose connection
Sensor overheatingExcessive ambient temperature
Intermittent flame detectionUnstable flame
Sensor foulingDust and soot buildup
Electrical noise interferencePoor grounding
Sensor alignment issueMisaligned sensor
Faulty signal processingElectronics failure
Sensor agingDegraded sensor sensitivity
Igniters
ProblemsCauses
Not workingDefective ignitor
Not retractingMechanical blockage
No powerCable damaged
Weak sparkIgnitor wear
Intermittent operationLoose connections
Ignitor overheatingExcessive usage
Ignitor misalignmentIncorrect installation
Poor ignition timingControl circuit issues
Ignitor contaminationDirt and debris
Ignitor coil failureElectrical failure
ProblemsCauses
Not workingDefective actuator
Air leakSeal damage
Not opening/closingLoose connection
Not opening / closing fullyPosition feedback failure
Valve huntingVolume booster failure
Valve passingSeat damage
Gland leakPlug / Seat / Spring damage
No feedbackChannel/card fault
No flow/outputTubing damage
Valve stuckDebris blockage
ProblemsCauses
Not workingLoose connection
Not opening/closingNot indicated in DCS
No outputInstrument card failure
Valve not operatingAir leak / Internal choke
Positioner driftCalibration issues
Feedback signal errorElectrical noise
Positioner overheatingEnvironmental conditions
Signal interferenceElectrical interference
Positioner alignment issueIncorrect installation
ProblemsCauses
Not workingChannel fault
Not indicatingAlignment problem
Coil not energizingCable damaged
Feedback driftSensor aging
Electrical noisePoor grounding
Feedback signal lossCable disconnection
ProblemsCauses
Not workingCoil failure
No outputNo power
Valve stuckSeal damage
Sealkits damagedInternal filter choke
Not operatingChannel fault
Intermittent operationElectrical noise
Valve overheatingEnvironmental conditions
Feedback signal errorCalibration issues
Valve misalignmentIncorrect installation
Solenoid Valves
ProblemsCauses
MalfunctioningValve passing
Leak/chokeCoil not energizing
Valve stuckInternal blockage
Noisy operationAirflow obstructions
Valve overheatingExcessive usage
ProblemsCauses
No powerPower supply failure
Air leakSeal kit / Diaphragm damage
Sensor not respondingSensor failure
False alarmsElectrical noise
Detector malfunctioningCalibration drift
No alarmBattery discharged
Intermittent signalLoose connection
Detector misalignmentIncorrect installation
ProblemsCauses
Not workingDiaphragm / Seat damaged
Air/gas leakSpring / Parts damaged
No flow/outputInternal blockage
Incorrect pressure readingPressure gauge damaged
Valve passingSeal damage
Pressure fluctuationCalibration issues
ProblemsCauses
No alarmNo communication with repeater panel
Glass brokenPhysical impact
Faulty signal transmissionCable damage
False alarmsSensor aging
MisalignmentIncorrect installation
Analysers
ProblemsCauses
Not workingAnalyser failure
MalfunctioningLoop cable damaged
Not matching with lab readingsCalibration drift
No local displaySensor not clean
No indication in DCS / PLCChannel fault
Sensor driftSensor aging
Signal lossCable disconnection
ProblemsCauses
Not workingSample line choke
No flow/outputFuse / Power supply card failure
Calibration gas leakIsolation valve problem
Carrier gas leakRotameter stuck
No sample gasValve passing problem
No carrier gasSeal kit damaged
Red LEDs glowingInternal filter choke
Readings not matchingCalibration disturbed
No powerSensor not clean / failed
Showing errorSampling probe issue
ProblemsCauses
Not workingBourdon tube damaged
Glass brokenImpact damage
Showing zero / span / errorInternal parts dislocated/damaged
Needle fallenPoor assembly
Gauge leakingThermowell damaged
Needle huntingOvertightening / Lack of cleaning
Inconsistent readingsTemperature fluctuations
Gauge vibrationNo anti-vibration liquid
View glass not visibleLack of guard for LG glass
Orientation not properImproper installation
ProblemsCauses
Not working / No air outputDiaphragm damaged
Sheath / Capillary puncturedPhysical damage
Air leakLoose fittings
Drain valve not workingInternal parts damaged/dislocated
Adjustment knob not workingInternal blockage
Pressure gauge fluctuatingFaulty gauge
Low output pressureRegulator set too low
High output pressureRegulator set too high
Gauge not respondingGauge failure
ProblemsCauses
Knob / Drain valve stuckDebris in valve
Impulse tubing leakTubing damaged
Fitting chokeBlockage in fitting
Diaphragm puncturedPhysical damage
No power / Indication / OutputAI channel fault at DCS / PLC
Incorrect calibrationCalibration drift
Signal interferenceElectrical noise
Moisture ingressPoor sealing
ProblemsCauses
Instruments not workingLoose connection
Not indicating / Showing errorTerminal blocks / Screws damaged
Display coming & goingWater entry
Intermittent power lossFaulty wiring
Noisy operationElectrical noise
OverheatingPoor ventilation
Signal interferencePoor grounding
Loose terminalsVibration
ProblemsCauses
Battery dischargedIO cards / CPUs failure
Red LEDs glowingChannel fault
Reading showing stars/zerosLoose connection
Not rebootingMomentary malfunction
Display hangedDefective power supply
Display coming & goingHMI / OT / SMPS fault
No displayEarthing / Grounding problem
Reading showing “—“Communication cable problem
Parameters not updatingSoftware bug / Hardware problem
Time mismatchGPS problem or time sync issue
ProblemsCauses
Showing wrong / error / high/lowIO card / CPU failure
Not rebootingBattery discharged
Display coming & goingHMI / OT / SMPS failure
Weigh Bridge
ProblemsCauses
Not workingFuse / Power card failure
Not showing readingLoad cell / Electronic card failure
Showing wrong / error / high / lowServicing / Cleaning required
Mismatch with flow meterCalibration setting disturbed
Intermittent readingsLoose connection
Overload indicationLoad cell damaged
Signal driftSensor aging
Corrective Actions
Some of the correction actions to be carried out during instrument troubleshooting are shown below.
  • Loop tightening
  • Cleaning
  • Lubrication
  • Servicing
  • Adjustment
  • Alignment
  • Configuration
  • Rebooting
  • Defective parts replacement
  • cables check
  • Instruments Replacement etc.
  • Instrumentation and Control Quiz
  • Troubleshooting PLC Automation Systems
  • Troubleshooting Flow Meter Common Problems
  • Control Valve Hunting Troubleshooting Tips
  • Motor Operated Valve Problems and Troubleshooting
Meters used in Troubleshooting Electrical Equipment
What is a Fotonic Sensor? – Working Principle, Advantages, Disadvantages
Discrete Manufacturing Automation
Heat Recovery in HVAC System
Piezo-electric Acceleration Measuring Device
Proximity Sensor
Information Technology and Operation Technology in Industrial Automation
What is an IP address? How to Set IP Address of the Computer?
HVAC Water Chillers Principle
Types of Air Conditioning Systems
What is Fuzzy Logic? Advantages, Disadvantages, Applications
What is Transparent Solar Panel? – Working Principle and Theory
How is Electricity Generated From Wind Energy?
Top 100 Microcontrollers Project Ideas
Bracelet Scanner
How to Use Bracelet Scanner? – Ultrasonic Thickness Gauge
International Standards - Types and their Details
International Standards – Types and Their Details
Hydrogen Sulfide Accident
The Aghorn Hydrogen Sulfide Accident – H2S Gas
How to Train Your Maintenance Team for Industrial Automation Systems
CNC Programming - Definition, Types, and Tips
CNC Programming – Definition, Types, and Tips
Career Scope in Electronics Engineering
What is Cloud Computing
What is Cloud Computing? Types of Cloud Services, Components
Radiation Exposure Converter
Free Online Radiation Exposure Calculating Platform
Relay Permissive and interlock circuits
Transformers Coolers Weld Joints Oil
Transformers Coolers Weld Joints Oil Oozes Were Eye Sores
Imbibition Water Flow Control System
Imbibition Water Flow Control System – Sugar Factory
Oil Burners
What are Oil Burners? Types, Advantages, Applications
LVR Motor Controller Operation
Low Voltage Protection (LVP) and Low Voltage Release (LVR)
Master Control Reset (MCR) ladder logic
How to use Master Control Reset (MCR) Instruction in PLC
Ladder Logic Example of Two Motors
Ladder Logic Example of Two Motors Interlinked with another Motor
phototransistor-circuit
Phototransistor Circuit Example