Inst ToolsInst ToolsInst Tools
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Search
  • Books
  • Software
  • Projects
  • Process
  • Tools
  • Basics
  • Formula
  • Power Plant
  • Root Cause Analysis
  • Electrical Basics
  • Animation
  • Standards
  • 4-20 mA Course
  • Siemens PLC Course
Reading: Capacitance Level Sensor Principle, Limitations, Installation & Calibration
Share
Font ResizerAa
Inst ToolsInst Tools
Font ResizerAa
  • Courses
  • Design
  • PLC
  • Interview
  • Control System
Search
  • Courses
  • Automation
    • PLC
    • Control System
    • Safety System
    • Communication
    • Fire & Gas System
  • Instrumentation
    • Design
    • Pressure
    • Temperature
    • Flow
    • Level
    • Vibration
    • Analyzer
    • Control Valve
    • Switch
    • Calibration
    • Erection & Commissioning
  • Interview
    • Instrumentation
    • Electrical
    • Electronics
    • Practical
  • Q&A
    • Instrumentation
    • Control System
    • Electrical
    • Electronics
    • Analog Electronics
    • Digital Electronics
    • Power Electronics
    • Microprocessor
  • Request
Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Inst Tools > Blog > Calibration > Capacitance Level Sensor Principle, Limitations, Installation & Calibration

Capacitance Level Sensor Principle, Limitations, Installation & Calibration

Last updated: December 22, 2018 12:15 am
Editorial Staff
Calibration Level Measurement
No Comments
Share
6 Min Read
SHARE

Measurement principle

The capacitive measuring principle is based on the method of the operation of a capacitor.

A capacitor is formed by two differently charged electrodes isolated from each other. Applying an alternating current between the electrodes will create an electric field. This electrical field depends on the distance between the electrodes, the size of electrodes surface, and the isolating medium between the electrodes.

If the distance between electrodes and size of surface of the electrodes are kept constant, only the medium would have an effect on the electrical capacitance. When the medium change the electrical field changes also consequently the capacitance evolves as follows:

  • Capacitance (C) = Dielectric constant (Ɛ0) × Relative Dielectric constant (DC) × Electrode Surface Area Where the dielectric constant (Ɛ0) is the electric field constant (Ɛ0 = 8.8 × 10‐12 C/(Vm).

Capacitance Level measurement principle

Figure – Capacitance measurement principle

Media with a low dielectric constant (DC value) cause very small changes of the capacitance value in level measurement while media with a high DC value produce respectively large capacitance changes. In many interface applications, the medium with the lower DC value is on top, e. g. hydrocarbon (DC = 2) on water (DC = 80).

The upper medium provides only a minimum contribution to the overall capacitance value – only the water level (the interface layer) is thus indicated as level.

In order to make use of this effect, the DC value of the two media should be sufficiently different from each other.

Usually a medium with a low DC value is non‐conductive while a medium with a high DC value is conductive. Therefore interface measurement with a non‐conductive and a conductive medium is always possible.

Limitations

Capacitance sensor Operating Range

Figure – Capacitance operating range

If a process coats or fouls a capacitance probe, a compensation option may be required to prevent false highlevel readings.

Continuous level capacitance transmitters require that the liquid being measured remains at a constant dielectric value. If this is not the case, the transmitter should have the capability to compensate for the liquid dielectric variation.

Probes mounted directly in the vessel typically cannot be replaced with the process in service unless they are mounted in a sensor cage with isolation valves.

The rod probes require sufficient height clearance, depending on the length of the probe.

It cannot measure liquids which have a viscosity above 2000 cst.

Selection

The capacitive level measurement can be used in aggressive media when a fully coated probe (e.g. PTFE) is used.

Capacitive measurement has a very fast response time which makes it ideal for processes with fast level changes and small containers.

The measurement principle is not affected by the density variation of the media.

For interface measurements a conductive and non‐conductive media is required.

At this interface the difference between the conductivity of the conductive media should be greater than 100 μS/cm and the conductivity of the non‐conductive media should be lower than 1 μS/cm.

An oil‐water emulsion has all the conductivity range between 1 and 100 μS/cm depending on the oil‐water bubble repartition. This means that a capacitance probe will detect the media above 100 μS/cm (i.e. conductive media) and will not detect the emulsion layer (between 1 and 100 μS/cm) as well as the non-conductive media layer (i.e. <1 μS/cm).

Non‐conductive build‐up on the probe affects the measurement.

Design

The probes should be made of metallic, conductive electrode with full plastic insulation regardless of the conductivity of the medium.

When mounted, a good electrically conductive connection between the process connection and the tank should be ensured. An electrically conductive sealing band can be used.

Rod probes with a ground tube should be used in the event of severe lateral loads.

The length of the probe should be designed in accordance with level measurement range.

Installation

Capacitance Level Sensor installation

Figure – Capacitance Level Sensor installation

The vessel earthing (grounding) method, which can be critical to the operation of the device, should be assessed.

Calibration and configuration

Capacitance probes are calibrated at the factory for media with a conductivity ≥100 μS/cm (e.g. for all waterbased liquids, acids, alkalis…).

A site calibration is only necessary if the 0%‐value or the 100%‐value should be adjusted to suit specific measurement requirements (e.g. tank/capacitance distance <250 mm, conductivity <100 μS/cm or specific range).

A distinction is generally made between two types of calibration:

  • Wet calibration: The probe can be calibrated for its full range i.e. lower level (0% level calibration) and high level (100% level). Other intermediate values can also be performed.
  • Dry calibration: The level capacitance can be simulated by entering the low and high level values. Capacitance units will calculate automatically the capacitance variation image based in the factory calibration for a conductivity ≥100 μS/cm.

Capacitance Level Sensor calibration

Figure – Capacitance Level Sensor calibration

Source : International Association of Oil & Gas Producers

Acknowledgements : IOGP Instrumentation and Automaton Standards Subcommittee (IASSC), BG Group, BP, Endress + Hauser, Emerson, Honeywell, Krohne, Petrobras, PETRONAS Carigali Sdn Bhd, Repsol, Siemens, Statoil, Total, Vega, Yokogawa.

Don't Miss Our Updates
Be the first to get exclusive content straight to your email.
We promise not to spam you. You can unsubscribe at any time.
Invalid email address
You've successfully subscribed !

Continue Reading

Different Types of Temperature Calibrators
Hydrostatic Tank Gauging (HTG)
Capacitance Level Measurement Working Principle
Displacer Level Transmitter Calibration using Water & Process Liquid
Level Troll working principle
Error sources creating uncertainty in Calibration
Share This Article
Facebook Whatsapp Whatsapp LinkedIn Copy Link
Share
Leave a Comment

Leave a Reply Cancel reply

Your email address will not be published. Required fields are marked *

Stay Connected

128.3kFollowersLike
69.1kFollowersFollow
210kSubscribersSubscribe
38kFollowersFollow

Categories

Explore More

How a Level Switch Works
Hydrogen Sulfide Gas Detector Calibration Procedure
Pig Signalling Switches Functional Testing
Magnetic Float Level Transmitter Working Principle
Cat and Mouse type Level Indicator
Pressure Switch Calibration Procedure
Stroke Checking Procedure for GCV, SRV, IGV, and LFBV
Importance of Unit Measurement

Keep Learning

Ultrasonic Level Switch Principle

Ultrasonic Level Switch Principle

DeadWeight Tester

DeadWeight Tester Questions

calibration potentiometer for simulating the millivoltage output

Temperature Standards

what is calibration

Important Terms in Calibration

Multiphase Flow Meter Calibration Procedure

Multiphase Flow Meter Calibration Procedure

Level Gauges Questions and Answers

Level Gauges Objective Questions and Answers – Instrumentation

Density Calculation​ Using DP Transmitter

How to Measure Density using DP Transmitter?

Radiation based Level Sensor Principle

Radiation based Level Sensor Principle

Learn More

Ultrapure Water in the Semiconductor Industry

Ultrapure Water in the Semiconductor Industry

Difference Between PLC and SCADA

Difference Between PLC and SCADA

Fieldbus Flow Transmitter Calibration

Foundation Fieldbus Transmitter Calibration

11 kV, 3.3 kV, and 400 V systems insulation resistance (IR) Problems

11 kV, 3.3 kV, and 400 V systems insulation resistance (IR) Problems

NAMUR OPEN ARCHITECTURE

What is NAMUR OPEN ARCHITECTURE?

Classification of Transmission Lines

Classification of Transmission Lines

Incident Investigation: Motor Operated Valve Lesson

Incident Investigation: Motor Operated Valve Lesson

Relief Valve

Pressure Relief Valve Principle

Menu

  • About
  • Privacy Policy
  • Copyright

Quick Links

  • Learn PLC
  • Helping Hand
  • Part Time Job

YouTube Subscribe

Follow US
All rights reserved. Reproduction in whole or in part without written permission is prohibited.
Welcome Back!

Sign in to your account

Username or Email Address
Password

Lost your password?