Reading: AND Logic in Bently Nevada Vibration System
Inst Tools > Blog > Vibration Measurement > AND Logic in Bently Nevada Vibration System
Last updated: May 3, 2023 9:54 am
vicky
One of the most important and confusing concepts in Bently Nevada is Normal AND vs True AND.
Bently Nevada Vibration SystemNormal AND LogicTrue AND LogicNormal AND Truth tableTrue AND Truth table
This is used in logic building.
Suppose there is one heavy rating machine in your plant and obviously it is expensive. We use special safety systems for these machines like vibration and temperature monitoring and protection systems so whenever there is an abnormality in vibration/temperature observed, then the machine should trip accordingly.
Now assume the following logic:
High vibration in two vibration probes is used for machine trips. (The two probes must detect High vibration then only the machine will be tripped)
In the above case, what if 1 vibration probe goes to NOT OK? (NOT OK means the sensor probe failed or it is damaged). In this case, say only 1 probe detected it and as per logic, the machine should trip on high vibration of both probes, but the machine won’t trip because only 1 probe detected and the other probe is in a faulty state.
Now again think of another example where the process is more important and machines should not trip on spurious vibrations. Now here what if one vibration probe goes to NOT OK and the other detects high vibration?
Yes, it’s confusing!
Now here we have to understand the role of Normal AND and True AND.
Normal AND Logic
In Normal AND whenever a probe goes into the NOT OK state, it is taken out of logic, and logic is degraded.
Consider 2 out of 2 logic.
In the 2oo2 logic, if the Probe 1 detects high vibration and Probe 2 is NOT OK
Then logic becomes 1 out of 1 considering Probe 1 as input.
This type of configuration is used when the machine is more important than the process.
True AND Logic
In True AND whenever a probe goes into the NOT OK state, the logic remains the same.
Consider 2oo2 logic again.
In two-out-two logic, if Probe 1 detects high vibration and Probe 2 is NOT OK.
Then machine won’t trip even if Probe 1 detects high vibration.
This type of configuration is used when the process is more important than the machine.
This logic is driven through a relay which is normally de-energized (can be changed to normally energized also).
The below table shows the different possible scenarios using Normal AND logic in the Bently Nevada condition monitoring system.
Vibration Probe 1Vibration Probe 2Relay Status
Normal VibrationNormal VibrationDe-energized
Normal VibrationNOT OKDe-energized
NOT OKNormal VibrationDe-energized
High VibrationNOT OKEnergized
NOT OKHigh VibrationEnergized
NOT OKNOT OKDe-energized
High VibrationHigh VibrationEnergized
The below table shows the different possible scenarios using True AND logic in the Bently Nevada condition monitoring system.
High VibrationNOT OKDe-energized
NOT OKHigh VibrationDe-energized
  • Proximity Sensor on Shaft
  • Turbine Protective Devices
  • Bently Nevada 3500 Modules
  • Seismic Transducers Questions
  • Vibration Verification Procedure
How Vibration sensors Work ?
Vibration Switch Working Principle
Mechanical Vibration Switch Principle
Speed Probe Working Principle
Non-contact Vibration Measurement
Types of Sensors used in Vibration Measurement
  • KISHOR says:
    April 21, 2022 at 7:48 pm
    Thanks for the wonderful topic.
    I just referred the documents of bently, i would like to give a correction that in the description above it is mentioned NOT OK means vibration is high; but as per bently documents, NOT OK means instrument failure. it may be Proximitor, Probe, Barrier if present, or The channel. please check once from your end and update.
    Link for the document below.,
    https://dam.bakerhughesds.com/m/113b4a288b90729d/original/GEA31971A-Centrifugal-Compress-App-Note_R4-pdf.pdf
Advantages & Disadvantages of Different Vibration Sensors
Importance of Vibration Measurement
Vibration Monitoring System Step by Step Troubleshooting Guide
How to do calibration checks of vibration Probe, extension cable and vibration monitor
Bently Nevada 3500 Machinery Protection Systems Hardware Modules
Gap Voltage of Bently Nevada Vibration Probe
Why we use Negative Voltage in Vibration Measurement ?
Basics of Vibration Measurement
LVDT Principle
Contact Vibration Measurement
Turbine Supervisory Instrumentation
What is Turbine Supervisory Instrumentation (TSI)?
Vibration Probe Commissioning Checklist
Keyphasor Principle
What is Keyphasor ? How does Keyphasor works ?
Proximity Transducer Operation
Proximity Transducer System Operation
tk3 calibration instrument
What is TK-3 Calibrator ?
Fire and Gas System Interview Questions & Answers
Spring Loaded Variable Area Flowmeter Working Principle
Spring Loaded Variable Area Flow Meter Working Principle